Gray Flex [RE-wrenches]

Bill Brooks billbrooks7 at earthlink.net
Sun Apr 22 00:43:07 EDT 2001


Joel and others,

The point is not that air conditioners don't get got and wet, they just
don't get nearly as hot as the back side of a PV module. For roof mounted
arrays in warm climates (Los Angeles), it is best to use 75C as the hottest
ambient temperature (on the back of the module). This means that the conduit
must be rated for at least 80C (wet since it is outdoors). The conductors we
use to connect to the module must be at least 90C rated to allow current
flow (a 75C wire at 75C has zero ampacity by definition). Non-Metallic
Flexible Conduit is normally 60C wet rated but can be purchased in 80C,
which is fine to use.

If you are mounting the modules in an open rack like most of our off-grid,
ground-mount and pole mount systems, the hottest temperature never go above
about 65C, so 75C wire is okay, but the 0.33 multiplier must be applied to
the ampacity calculation (e.g. 10 ga. wire has a 16 amp ampacity at these
temps).

Bill.

-----Original Message-----
From: Joel Davidson [mailto:joeldavidson at earthlink.net]
Sent: Saturday, April 21, 2001 10:05 AM
To: RE-wrenches at topica.com
Subject: Re: Gray Flex [RE-wrenches]


Gray flex on air conditioner installations gets hot and wet. For many years,
manufacturers, distributors, installers and inspectors have accepted gray
flex.
What should be used on air conditioner installations that would be better,
cheaper and faster than current practices?

Bill Brooks wrote:

> Answer,
>
> USE-2 cable or Tray Cable without conduit using cable glands to connect to
> the junction boxes is cheaper than conduit and more appropriate in many
> cases. Many modules are not "conduit ready". Just because it has a 3/4"
> knockout, does not mean you can put a piece of conduit on it. We have many
> examples of conduit causing junction boxes to pop off the backside of the
> module. If the installation directions don't mention conduit you CANNOT
put
> conduit on them.
>
> If you put conduit on a module it must be a minimum of 80C wet-rated. The
> stuff you buy at HOME DESPOT is 60C rated and can weaken and fall apart at
> the temperatures we work with. I'm not making this stuff up or just
> regurgitating John Wiles stuff, I've seen it on several occasions in the
> field. The crap they often put on A/C units rated for lower temperatures
> should NEVER be used on PV system.
>
> Now that oughta get some reaction--anyone care to take me to task on this
> one? (in good fun of course)
>
> Bill.
>
> -----Original Message-----
> From: Joel Davidson [mailto:joeldavidson at earthlink.net]
> Sent: Saturday, April 21, 2001 9:17 AM
> To: RE-wrenches at topica.com
> Subject: Gray Flex [RE-wrenches]
>
> Flexible conduit is used almost always to wire outdoor air conditioners
> and passes inspection. Yet some designers say do not use gray flex for
> PV module interconnects and short sub-panel whips. What is better,
> faster, cheaper than gray flex?
>
> - - -
> To send a message:
>  RE-wrenches at topica.com
>
> Archive of previous messages:
>  http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette:
>  http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios:
>  www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator:
>  michael.welch at homepower.com
>
> - - -
> To send a message:
>  RE-wrenches at topica.com
>
> Archive of previous messages:
>  http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette:
>  http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios:
>  www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator:
>  michael.welch at homepower.com
>

- - -
To send a message:
 RE-wrenches at topica.com

Archive of previous messages:
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator:
 michael.welch at homepower.com


- - -
To send a message:
 RE-wrenches at topica.com

Archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator:
 michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A  -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================



More information about the RE-Wrenches mailing list