approved disconnects [RE-wrenches]
William Miller
wrmiller at slonet.org
Wed Apr 4 00:34:21 EDT 2001
At 06:19 PM 4/3/01 -0700, you wrote:
>Concerning the disconnect that PG&E requires; does anyone know if it
>would be acceptable to use the disconnect that is the main service
>entrance, which is a lockable and located at the pole and disconnects
My experience has been that PG&E requires a disconnect with an external
handle so it is visible without opening the cover, and it must be adjacent
to the meter. I did talk PG&E into approving a disconnect about 8 feet
away from a meter on condition there be a plaque adjacent to the meter
indicating the location of the disconnect.
I have asked linemen on the street and they know of no requirement or
database of locking disconnects or customers with generating equipment,
inverter or generator based, on premise. I argued with our local PG&E
representative about this but for them this is a safety issue, and they
will not budge.
I do have several jobs going with a unique condition: We desire to use an
existing feed to a greenhouse, garage or well pump for the originally
intended use as a feeder AND as the path for the line-tie system to connect
back to the utility. I have two verbal OKs from PG&E as long as the
feeder/line-tie return be routed through locking disconnect at the meter.
This is a BIG convenience and I am grateful to PG&E for allowing this.
William Miller
__________________________________________________________________
William Miller
SLO Communications: Communications and Power Systems Consulting
PO Box 50, Santa Margarita, CA 93453
Voice :805-438-5600 Fax: 805-438-4607 VMail: 805-546-4875
email: wrmiller at slonet.org
License No. C-10-773985
_____________________________________________________________
Compatibility:
Word processor: WP7
Spreadsheet: Quatro Pro 7
CAD: Microstation 95, DXF, Visio 4.1T
_____________________________________________________________
"I stand by all the misstatements that I've made." Dan Quayle
__________________________________________________________________
- - -
To send a message:
RE-wrenches at topica.com
Archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator:
michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================
More information about the RE-Wrenches
mailing list