Fuses vs. Breakers (was QO Breakers and Panels)[RE-wrenches]
Jerry Caldwell
solarcowboy at yahoo.com
Sun Mar 11 16:30:50 EST 2001
And what is a good rule of thumb for deciding when the
battery is large enough to require fusing? Most of
the smaller grid tied systems I've installed have not
had fuses on the battery as have the systems with
larger battery banks.
Jerry Caldwell
--- "Travis Creswell, Ozark Solar" <ozsolar at ipa.net>
wrote:
> Fuses are for stopping faults before they do a lot
> of damage and breakers
> are for over current protection. Faults and over
> current are very different
> things. A fault on a system with more the just a
> few golf cart batteries
> will have catastrophic results.
>
> So what is the implication? It is a very good idea
> to have a fuse in
> between the batteries and the breaker.
>
> Travis Creswell
> Ozark Solar
__________________________________________________
Do You Yahoo!?
Yahoo! Auctions - Buy the things you want at great prices.
http://auctions.yahoo.com/
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
More information about the RE-Wrenches
mailing list