Colleagues:

I just finished a telephone call with Square D tech support.  They are
going to fax me critical information which I will share as soon as it
arrives and I have time to transcribe it.

I have a question about Drake's post, below:


At 10:03 AM 3/8/01 -0800, you wrote:
>Hi Bill,
>
>
>What ever the reason might be, it convinced me that fuses are superior 
>protection to breakers.  As you stated before, the QO breaker makes an 
>excellent switch for low voltage DC.  I think it is good for PV array 
>disconnects, as they are current limited.  On the battery side, I don't 
>trust the QO as the sole protection.
>
>Drake

Q: If we are using a DC rated circuit breaker to connect PV source circuits
to a battery charging system, then don't we have a battery connection at
the load side?  For example, in a TC60 with breaker option with the breaker
wired in the output circuit: the breaker will be connected to the battery
bank.  In this case then, one should always install a fuse between the
breaker and the batteries, correct?  Then why even have a breaker?  Why not
instead use a switch with adequate interrupting capacity?  See ASCII CAD
below:

Typical PV source and charging circuit:

PV array---DC breaker-----\
                                       ----Charge
control---Switch-------fuse--batteries
PV array---DC breaker-----/


Thanks again for the great dialog.  We need these answers so we can design
reliable and legal installations.


William

__________________________________________________________________
William Miller
SLO Communications: Communications and Power Systems Consulting
PO Box 50, Santa Margarita, CA 93453
Voice :805-438-5600		Fax: 805-438-4607	VMail: 805-546-4875
email: wrmiller at slonet.org
License No. C-10-773985
_____________________________________________________________
Compatibility:
Word processor: WP7
Spreadsheet: Quatro Pro 7
CAD: Microstation 95, DXF, Visio 4.1T
_____________________________________________________________
"I stand by all the misstatements that I've made." Dan Quayle
__________________________________________________________________

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01



More information about the RE-Wrenches mailing list