Friends:

Here is some new info I am not sure I shared with this group.  My apologies
if this particular point is a repeat.

A rep. from Square D told me they tested and will certify QO breakers in an
NQOD panel to 125 volts DC.  If you purchase an NQOD panel with QO
breakers, they will send a certificate stating that these breakers are OK
to use up to 125 VDC.  I have the persons name and the date we spoke in my
notes, if anyone needs this data.

William




At 07:58 AM 3/6/01 -0800, you wrote:
>Hi Travis,
>
>Square-D QO breakers....up to the 70 amp size are rated for use up to 50
>volts DC. That's why they're quite iffy for use in 48 volt
>systems.....you'll wind up over the 50 volts frequently if you're doing it
>right! As for the breaker's DC approval...it's got to do with the AIR
>rating of the QOs. To the best of my knowledge, the HOM type breakers do
>not have the DC rating.
>
>Look on page 57 of Wiles' Sandia Handbook, under Distribution
>Systems....that discusses the QO breaker rating. And I've had several
>systems with the QO DC load center pass inspection with flying colors....no
>problemo!
>
>Hope this helps a bit.
>
>Roy Butler
>Four Winds RE
>
>- - - - - - -
>To send a message:
> RE-wrenches at topica.com
>
>The archive of previous messages: 
> http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette:
> http://www.mrsharkey.com/wrenches/etiquete.htm
>
>To unsubscribe send a message to: 
> RE-wrenches-unsubscribe at topica.com
>
>To check out the other RE-Wrench participants:
> www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine: 
> www.homepower.com
>
>For info contact list moderator by email:
> michael.welch at homepower.com
>
>____________________________________________________________
>T O P I C A  -- Learn More. Surf Less. 
>Newsletters, Tips and Discussions on Topics You Choose.
>http://www.topica.com/partner/tag01
>
>
>

__________________________________________________________________
William Miller
SLO Communications: Communications and Power Systems Consulting
PO Box 50, Santa Margarita, CA 93453
Voice :805-438-5600		Fax: 805-438-4607	VMail: 805-546-4875
email: wrmiller at slonet.org
License No. C-10-773985
_____________________________________________________________
Compatibility:
Word processor: WP7
Spreadsheet: Quatro Pro 7
CAD: Microstation 95, DXF, Visio 4.1T
_____________________________________________________________
"I stand by all the misstatements that I've made." Dan Quayle
__________________________________________________________________

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01



More information about the RE-Wrenches mailing list