Trace ST problems [RE-wrenches]
Eric Smiley
Eric_Smiley at bcit.ca
Tue Mar 6 16:38:35 EST 2001
>Remember that EPV modules have a very poor fill factor and therefore
are not
>far off the max power point with a few volts. However, I have seen EPV
>modules operating at much lower than 39 Volts (try 34 Volts). A good
rule of
>thumb is to not believe manufacturers specifications--that goes for
modules
>and inverters.
I have witnessed the same thing with EPV modules. However, I spoke with
Tobin Booth at Trace and he confirmed my suspicion that the 42 - 85 V
MPPT window is conservative. (Also one would assume EPV would carefully
select modules for a demo system)
Personally, I still wouldn't spec EPV modules with a SunTie, but I'm no
longer so concerned about pairing other a-Si modules with the ST.
>The MPPT window of an inverter is based on the line voltage. The low
end of
>the voltage range is always suspect from the manufacturer. If the line
>voltage is 124Volts (3%high) the low end of the MPPT window just went
up 3%
>(that would be about 44 Volts on the Sun-Tie). Now we have a 10 Volt
>differential--Very significant power loss.
I think this would be true for a low frequency inverter. However, since
the ST has a high frequency topology, it probably isn't strictly a
linear relationship.
----------------------------------------------------------------------
Eric Smiley
Project Leader - BCIT Technology Centre
Photovoltaic Energy Applied Research Lab (PEARL) - BCIT
ph: (604)432-8657 www.bcit.ca/~tc/pearl/index.htm
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
More information about the RE-Wrenches
mailing list