QO Breakers and Panels [RE-wrenches]

Travis Creswell, Ozark Solar ozsolar at ipa.net
Tue Mar 6 12:56:42 EST 2001


Bob-0,

I agree. I have always thought that a little ridiculous but I doubt have a
good grasp of the big picture.  Yes, by the time you apply all the de-rate
factors you can get the OCV of a 24v array near 48 volts but there is no
current which = no energy. In my way of thinking.  If there is a fault then
the array is instantly pulled to near zero volts at short circuit current
which = just a little above no energy.

I wonder if a lot of the overkill on electrical code as it relates to solar
is thinking of the array as a infinite energy source just like you have to
consider the service coming into the house.  For example if there is a
problem with the grid wires in between your main breaker and the utility
transformer then the problem either burns the wire in two or trips the
transformer.

Travis
----------
>From: "Bob-O Schultze, Electron Connection" <econnect at snowcrest.net>
>To: RE-wrenches at topica.com
>Subject: Re: QO Breakers and Panels [RE-wrenches]
>Date: Tue, Mar 6, 2001, 11:38 AM
>

>
>No. They are rated for 48VDC which is below the normal operating 
>voltage in a 48V system. Wiles even has a problem with them in 24V PV 
>systems because the PV open circuit voltage X 1.56 exceeds 48V. THAT, 
>in my opinion, is just ridiculous. During normal operation they never 
>see more than 32VDC or so.

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01



More information about the RE-Wrenches mailing list