<<If all of your SW setup values are actually where they belong, and the
charge controller is operating properly (above the SW bulk voltage), then
you probably have MOSFET damage in the inverters. The inverters will
produce output that seems "normal", but they won't feed back the grid. Your
best bet here is to look at the wave form on an oscilloscope, if possible.
This was the situation with my SW 2512, it would connect to the grid and
*act* like it was feeding the utility, but the batteries would boil away at
15+ volts (there's no other charge controller in my system). The inverter
would power loads from the batteries in a seemingly normal manner. When I
took apart the cabinet, I found four fried MOSFET's, all connected to one
of the three transformers. The result of this failure was that the inverter
could meet the voltage of the grid, but not exceed it enough to cause
current to flow back unto the utility. No error indications were noted on
the front panel, or in the faults menu.
Time to exercise your (entended?) warranty.>>
Sharkey et all,
After I posted my original message the wrench on site got the system to
sell back several amps (late afternoon) on each inverter by adjusting the
charge controller float setting upwards. So it looks like the Pulse
controller was holding back on pv amps. Now I have to figure out why.
We would appreciate any other suggestions.
David Palumbo
IP&L
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
More information about the RE-Wrenches
mailing list