Placement of lightning rods [RE-wrenches]
sunwise at cheqnet.net
sunwise at cheqnet.net
Tue Feb 27 09:59:39 EST 2001
Drake Chamberlin - Electrical Energy wrote:
>
> Could you say more about the problem with multiple ground paths? With
> wind systems I've been advised to connect a ground rod to each leg of the
> tower.
Yes, that's not a multiple ground path, thats just good grounding of the
tower. I believe these individual tower leg groundings are suposed to
all be bonded as well. An example of multiple ground path on a PV
system would be installing a ground rod at the (pole mounted) array and
bonding the negative leg of the PV to ground at the array, and then
installing a seperate ground rod on the home wiring. Now, you have the
possibility of a voltage potential developing (near-by lightning)
between the two grounds and it is carried through the conductors (and
charge controller, etc.) rather than through the ground wire. Kurt
Nelson
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
________________________________________________________________________
Start an Email List For Free at Topica. http://www.topica.com/register
More information about the RE-Wrenches
mailing list