Heat redistribution/timer [RE-wrenches]

Allan Sindelar, Positive Energy, Inc. allan at positivenergy.com
Wed Feb 21 17:36:18 EST 2001


Gary,
The problem I see is 24 cycles/day on a DC-powered timer; it's probably a
custom unit.  I did a similar approach recently with an AC well pump, but I
only needed 2 cycles/day.  AEE sells a 12V/24V DC analog timer, part
#52-520-016 ($90 retail) to control the relay.  Their catalog suggest a
minimal on or off cycle of 15 minutes, using trippers to activate a switch.
As extra trippers can be added, in theory you could do 48 cycles/day...but
the switch might wear out in a few years, and it's pretty spendy...
If you use a T240, make sure that the relay controls the input side, to
avoid phantom loads.  Also use a DC coil relay, for same reason.  But
hey--if the motor is only 1/3 hP, it's probably reconnectable as 120VAC.
Have you checked that out?

Allan at Pos E

----- Original Message -----
From: "Gary Higbee, Solutions from the Land" <ghigbee at efn.org>
Subject: Heat redistribution/timer [RE-wrenches]


> I'm working with a client who would like to be able to run his 1/3hp
> 240-volt circulating fan.

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

List rules & etiquette:
 http://www.mrsharkey.com/wrenches/etiquete.htm

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01



More information about the RE-Wrenches mailing list