S-
What E-mail(i.e. comments starting with ">") are you referencing in the below reply?
Nothing I recall reading.
Kirk
"R. Sparks Scott" wrote:
> >coil voltage to crash on the internal contactor when at the same moment.
>
> The internal transfer relay is NOT directly connected to the AC input, it
> is controlled by a DC logic, not powered by the AC itself. As a result,
> killing the generator will probably result in some out-of-spec voltage or
> freq, causing the logic to do the disconnect. This may happen before of
> after the equipment being powered is affected by the dying voltage/freq.
> Tightening the AC2 freq and voltage range in setup might go a long way
> towards clearing this up.
> Either way, seems like the logic should unload the generator *before* it
> is shut down, assuming a controlled stop, and not a generator failure. I
> can tell you for sure that killing *any* gasoline-powered internal
> combustion engine while it is running at speed and with a load is a sure
> way to shorten it's life. Consider all of the fuel that is sucked into the
> cylinders and left unburned. Tends to wash down the cylinder walls and
> makes the piston lubrication during the next start sequence virtually nil.
> This applies to your vehicles as well, don't rev the motor just before
> cutting the ignition.
> Shutting off the ignition on *any* engine with a turbo should only be done
> after the engine has idled for a moment or two. Turbos can reach 100,000
> RPM internally, and it sometimes takes a while for them to spin down from
> high speed/heavy load. Shutting off the engine while they are hauling ass
> will burn out their bearings pronto. (Probably not a lot of turbocharged
> generators in service on this list, eh?)
>
> >If I told you what I actually knew, I'd have to kill you. They are way
> ahead of you.
>
> This is very cryptic. What does it mean?
>
> -S
>
> - - - - - - -
> To send a message:
> RE-wrenches at topica.com
>
> The archive of previous messages:
> http://www.topica.com/lists/RE-wrenches/
>
> To unsubscribe send a message to:
> RE-wrenches-unsubscribe at topica.com
>
> To check out the other RE-Wrench participants:
> www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine:
> www.homepower.com
>
> For info contact list moderator by email:
> michael.welch at homepower.com
>
> ____________________________________________________________
> T O P I C A -- Learn More. Surf Less.
> Newsletters, Tips and Discussions on Topics You Choose.
> http://www.topica.com/partner/tag01
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
More information about the RE-Wrenches
mailing list