Travis Creswell, Ozark Solar wrote:
> 
> I have a customer who already had a 22 kW kohler controlled by a
> automatic transfer switch.  We added solar and a dual SW inverter
> system to the house.  Due to the size of the existing generator and
> existing house wiring configuration I can't run the generator into AC2
> on the SW's.  There are loads on the main panel that he would like to
> run still that shoudn't be ran of the inverters.

Hey Travis,

Having a hard time following this, maybe if you spoke more about what
these loads and such consist of.  That said, I don't see why you can't
bring the gen-set into AC2.  Just don't have all the home loads on the
AC outputs of the Trace(s).  Also, if you want to do some type of
transferring, consider using the AUX relays in the Trace rather than an
Emeter set-up.  If you'd care to give more info on what is running where
in this home (maybe off list), it may help me to follow the logic and I
may be able to offer some other thoughts -- Kurt Nelson

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

____________________________________________________________
T O P I C A  -- Learn More. Surf Less. 
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01



More information about the RE-Wrenches mailing list