I belive the theory here is that your generator is running too fast unless
it has a load to slow it down. the converse could be that if you slow it
down to so as to fit within the inverter frequency window unloaded, when
you load it, it may drop below the frequency window.
I understand that generators need to be de rated by 50% in UPS systems.
This may be true for smaller generators in inverter systems. If the
continuous amp rating of your generator is 19 or so, you may want to set
the inverter to take 10 or 12. This way the load range is not so wide and
you may be able to regulate the generator frequency to stay within the
acceptance window.
The only way to know what frequency your generator is making during the
cycling is to connect a frequency counter to the generator itself. The
trace only reads the frequency of the accepted source. If your generator
is currently rejected, the Trace won't be reading it.
William Miller
At 05:57 PM 12/16/00 -0800, you wrote:
>I thought it could also be the gen freq., but if it was so out of whack so as
>to cause the inverter to disconnect from the generator, why would it
reconnect
>again with no load? If the theory of less load = worse frequency is
carried to
>this condition as well, with NO load it would be even more out of acceptable
>range, and the Trace should not even synch with it to begin with.
>
>Todd
>--
>Todd Cory
>KE6SXS
>toddcory at jps.net
>Bald Mountain Solar
>P.O. Box 689
>Mt. Shasta, Ca. 96067
>(530) 926-1079
>
>"Let us declare nature to be legitimate. All plants should
>be declared legal, and all animals for that matter. The notion
>of illegal plants and animals is obnoxious and ridiculous."
> --Terence McKenna--
>
>
>
>- - - - - - -
>To send a message:
> RE-wrenches at topica.com
>
>The archive of previous messages:
> http://www.topica.com/lists/RE-wrenches/
>
>To unsubscribe send a message to:
> RE-wrenches-unsubscribe at topica.com
>
>To check out the other RE-Wrench participants:
> www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine:
> www.homepower.com
>
>For info contact list moderator by email:
> michael.welch at homepower.com
>
>___________________________________________________________
>T O P I C A http://www.topica.com/t/17
>Newsletters, Tips and Discussions on Your Favorite Topics
>
>
>
__________________________________________________________________
William Miller
SLO Communications: Communications and Power Systems Consulting
Chief Engineer, KCBX: NPR and PRI for San Luis Obispo and Santa Barbara
PO Box 50, Santa Margarita, CA 93453
Voice :805-438-5600 Fax: 805-438-4607 VMail: 805-546-4875
email: wrmiller at slonet.org
License No. C-10-773985
_____________________________________________________________
Compatibility:
Word processor: WP7, Word 7
Spreadsheet: Quatro Pro 7, Excel 5
CAD: Microstation 95, DXF, Autocad V12 DWG, Visio 4.1T
_____________________________________________________________
"I stand by all the misstatements that I've made." Dan Quayle
__________________________________________________________________
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A http://www.topica.com/t/17
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list