Breakers overheating [RE-wrenches]
Don Loweburg, Offline
i2p at aol.com
Mon Nov 13 14:04:51 EST 2000
In a message dated 11/13/2000 10:47:36 AM Pacific Standard Time,
wrmiller at slonet.org writes:
<< have a project I've sub-contracted and the sub-contractor is having a
problem I can't explain. The system is an off grid PV with 2 SW4024
inverters and a 16kVA Onan backup. The generator is new and is fed via a
load center into the inverters. Three circuit breakers in two load centers
have burned up in this generator circuit. The first was a 125 A GE load
center with a 60 amp feeder into the inverters. The second two breakers
were 60 A Square D QO breakers in a 70 amp QO load center. The inverters
were set for 50 A on Line in 2 and the charging circuit at 30 A.
I wasn't on site to witness this. My only guess is that the 60 A breakers
in a 70 A panel were too close to design limits to handle 50 A continuous?
This does not seem possible considering the following: Since the charger
is set for 30 A, the client would need to draw 20 A on either leg for the
inverter(s) to create a 50 A draw. The battery charging circuit may draw
30 amps at first, but this should taper off relatively soon. Therefore, it
seems unlikely the system is ever drawing 50 A, at least not for any period
of time. Why then are circuit breakers burning up?
>>
Bill I have several systems with 15 kw gensets with dual inverters. Have not
had this problem. Since you subed this out- there may be something you don't
know or your sub does not see. I would go on site and go over everthing. This
is not a general problem.
One thing just popped to mind. If for some reason there were a large power
factor this would result in large out of phase currents that might explain
the heating and failure of the breakers. Again I suggest this will require
your onsite attention.
Best, Don
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A http://www.topica.com/t/17
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list