Equalize charge - SW4024 [RE-wrenches]
Kurt Nelson, SunWise
sunwise at win.bright.net
Tue Oct 17 11:38:25 EDT 2000
allan wrote:
>
> John,
> RE the EQ: It's [another] design/software weakness in the SW.
Hey Allan,
Yup on the EQ, One can also up the bulk voltage (and possibly
absorption time) to something that will approximate an EQ. Too bad it
doesn't just work the way it should.
> On the pumps: When you say DC250, do you mean T240? By all means, control
> the T240 on the primary side to avoid phantom loads. We have done a 3/4hp
> 240 well pump with a standard open-coil relay with 24VDC coil voltage
> (Grainger 3X749), letting the control circuit (float switch or pressure
> switch) operate the DC coil.
I have done a number of 3/4 horse 240 volt pumps with the Trace T-240
and have had good success switching the T-240's primary hot lead
directly from a Square D pressure switch, paralleling both sets of
contacts on the pressure switch.
On Grid-tied systems, I add a double throw 30 amp power relay with 240
volt coil and leave the pump on the utility unless they go down. That
relay switches the pump (and it's regular pressure switch) between the
utility and the output end of the T-240 based on the presence of 240vac
utility at the coil. In this case, I still use the other pressure
switch to supply power from the inverter to the primary of the T-240,
and set this pressure switch to come on and shut off at a slightly lower
pressure settings than the main pump pressure switch. Actually, Bob-O
may have originally come up with this arrangement.
Kurt Nelson
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list