Mon Aug 28 19:04:39 EDT 2000
Kohler 10RY and the discontinued 6.5ROY air cooled 1800 RPM can all be
rewired for full power 120 volt single circuit, or for split 120/240 with
half power on each of two 120 legs. It simply requires switching the wires
in behind the circuit breaker panel to put the two coils in series with
opposite phases or in parallel with same phase. The diagrams in the
OPERATION (not the installation) manual, page 5-1 and 5-2, figure 5-2 for
120 volt full power and figure 5-3 for 120/240 volt. Output power wires are
numbered 1, 2, 3, 4. #3 is AL:WAYS grounded to stud on the chassis. Also on
that stud bolt is EITHER gen output #1 for full power 120 volt, or Generator
output #2 for 120/240 set-up. The remaining two gen wires are connected to
the output breakers as shown in the two drawings. In reversing these two
wires you will find the small tip on the wire originally on the breaker will
not fit the stud and needs to be changed to a larger tip. Also there are 4
voltage regulator small white wires on these same output terminals. Labeled
V1, V2, V3, V4. Do not move these from where they originally are.
Steve Willey www.backwoodssolar.com
Backwoods Solar Electric Systems
A catalog business on a mountain
2 miles from utility lines,
powered entirely by our catalog products.
IF UTILITY POWER IS 1/2 MILE OR MORE FROM YOUR SITE,
get our free 160 page solar-electric Planning Guide/Catalog.
(Your postal address required - Our list is never given or sold).
Phone(208)263-4290 Fax (208) 265-4788 in Idaho, USA
----- Original Message -----
From: Gary Higbee, Solutions from the Land <ghigbee at efn.org>
To: <RE-wrenches at topica.com>
Sent: Monday, August 28, 2000 2:18 PM
Subject: Kohler full-output at 120 volts? [RE-wrenches]
> Hi Wrenches,
>
> Allan at Positive E wrote "All Kohlers thru 12 or 20kW or so can be wired
> 120 VAC output, so you don't have to match a pair of inverter/charger
loads
> on each leg of 240 VAC output..."
>
> How this is done?
>
> I do mostly stand-alone systems, and haven't messed with generators much.
> I'm working with a client now, though, who's going to be using his Kohler
> propane generator (around 7kW) with a SW5548, 16 L-16's, running a
Grundfos
> Model 10 SQ sub pump (9-10gpm measured at 425', "efficient," soft-start)
and
> general household loads. He'll be generator-charging until we add a couple
> KW of solar in the future (when the $ tree grows up!).
>
> If there's a way to get (balanced) full-output from the Kohler without a
> T/240 I'd love to know how ASAP. Thank You!
>
>
> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
> Gary Higbee (ghigbee at efn.org)
> (541)607-1818
> Solutions from the Land--solar,
> wind, and hydro site analysis, design,
> and installation assistance
> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
>
>
> - - - - - - -
> To send a message:
> RE-wrenches at topica.com
>
> The archive of previous messages:
> http://www.topica.com/lists/RE-wrenches/
>
> To unsubscribe send a message to:
> RE-wrenches-unsubscribe at topica.com
>
> To check out the other RE-Wrench participants:
> www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine:
> www.homepower.com
>
> For info contact list moderator by email:
> michael.welch at homepower.com
> ___________________________________________________________
> T O P I C A The Email You Want. http://www.topica.com/t/16
> Newsletters, Tips and Discussions on Your Favorite Topics
>
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list