Hi David,

I have had a lot of problems with the "new" todd 75's running in series. When I worked at AEE we
burned up 8 or 10 of them running in series, and this was on utility power.  I don't know the answer
to your question but I would caution you to use the 75's, the 45's and 30's seem to be fine however.

jay peltz

"David Palumbo, Independent Power & Light" wrote:

> Problem: Honda EU 3000 IS (inverter output) generator goes into protection
> mode (breaker like disconnection from load) when powering two Todd 75 amp
> (seriesed for 24v output) battery chargers.
>
> What we know: The Todd's use 1070 watts each under full load, they use 1475
> watts under maximum load and 80 amps inrush current for 5 milliseconds (Todd
> Engineering gave me the latter two numbers yesterday).
>         The Honda gen is rated for 3kw max and 2875w continuous power (120v only).
> It tests out on a resistive load bank with the protection feature opening at
> 30amps. With the 225 amp hour battery bank (small but ok for the application
> and pocketbook involved)at 85% state of charge, or more, the gen powers the
> chargers fine.
>
> I thought the generator would be able to handle this load ok. Wrong. So my
> question to the more electronically savvy wrenches out there is: Will wiring
> a capacitor across the Honda's output help the gen deal with the surge that
> is shutting it down? And what type of capacitor, motor start or motor run?
> And what Microfarad rating?
>
> Thanks for your time,
>
> David Palumbo
>
> - - - - - - -
> To send a message to the list use: <RE-wrenches at topica.com>
>
> To view an archive of previous messages go to: <http://www.topica.com/lists/RE-wrenches/
>
> To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>
>
> To check out who the other RE-Wrench participants are, go to <http://www.mrsharkey.com/wrenches/>
>
> Hosted by Home Power magazine: <http://www.homepower.com>
>
> for info contact: <michael.welch at homepower.com>
> ___________________________________________________________
> T O P I C A  The Email You Want. http://www.topica.com/t/16
> Newsletters, Tips and Discussions on Your Favorite Topics



- - - - - - -
To send a message to the list use: <RE-wrenches at topica.com>

To view an archive of previous messages go to: <http://www.topica.com/lists/RE-wrenches/

To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>

To check out who the other RE-Wrench participants are, go to <http://www.mrsharkey.com/wrenches/>

Hosted by Home Power magazine: <http://www.homepower.com>

for info contact: <michael.welch at homepower.com>
________________________________________________________________________
Start an Email List For Free at Topica.  http://www.topica.com/register


More information about the RE-Wrenches mailing list