Sewer Pump 1/2HP 120vac / DR2424 [RE-wrenches]
i2p at aol.com
i2p at aol.com
Thu Apr 27 12:25:35 EDT 2000
In a message dated 04/27/2000 8:40:09 AM Pacific Daylight Time,
cvsolar at aol.com writes:
<< Has anyone had experience using a DR2424 to run a 1/2 hp 120vac sewer
pump.
All my pump experience is either DC pumps or ac pumps using the SW4024 or
4048. I have only installed one DR2424 so far and it is only running a
freezer and furnace. This pump will be pumping up to a mound system. The
inverter will be dedicated to this one purpose so their are no other load
issues.
>>
Hi John, A DR 2424 would run it, but the question in my mind is what is the
duty cycle. A few minutes a day no problem. For long runs any ac induction
motor is going to be more effiecient on sinewave and run cooler.