Inverter/genset problem [RE-wrenches]

Bob-O Schultze, Electron Connection econnect at snowcrest.net
Fri Dec 22 22:24:03 EST 2000


<x-flowed>Frank,
Unless you are running that China diesel through a step down 
transformer you've got a 5000W generator. When you severely load just 
one leg of a 120/240 genny, all kinds of things can happen to voltage 
regulation and frequency. Assuming you have checked the voltage and 
cycles and found them reasonably OK, try putting a 1500W heater on 
the other leg. If everything works fine, then that's possibly the 
problem.
Bob-O


>Hello fellow wrenches,
>Got a problem that I hope I can get some feedback on. I have a customer that
>uses a DR-3624 off of 12 L-16HC batteries. He supplies power to his shop that
>includes lathe, drill press, table saw, etc. While running directly from
>inverter power everything runs just fine. While charging battery bank his
>microwave in the house and 40 watt fluorescent light in power shed will not
>operate. Everything else runs just fine including power tools. His genset is
>a 10,000 watt China Diesel that is almost brand new. I'm at a loss. Anyone
>want to tackle this one?  

Bob-O Schultze, Electron Connection
PO Box 203, Hornbrook, CA 96044
800.945.7587 fax 530-475-3401
www.electronconnection.com

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

___________________________________________________________
T O P I C A  http://www.topica.com/t/17
Newsletters, Tips and Discussions on Your Favorite Topics

</x-flowed>


More information about the RE-Wrenches mailing list