4024... [RE-wrenches]

allan allan at positivenergy.com
Mon Dec 18 12:50:30 EST 2000


Todd,
    Your problem is unusual, but here's part of it.  I think you're causing
an intermittent overload of the gennie.  At 3800' you need to derate more
for altitude.  Try 14A on AC2 in (that's a SWAG number, not a calculated
one).
    Also try matching setting max charge current to the same as AC2 amps,
then set them widely apart.  Let your observations of the results in each
case help you deduce the cause.
Allan @ Positive E
>Todd Cory, Bald Mt. Solar wrote:
>>
>> Hi Wrenches,
>>
>> I am wondering if anyone has experienced what is going on with my 4024
>> (software rev 3.0). I recently bought a 2500 watt Honda genny and for
>> the first time added an input to the AC2 terminals.
>>
>> I set the AC2 input at 18 amps so it has a bit of head room (it's rates
>> at 19.2A continuous). I set the max charge current to 17 amps. Here is
>> what happens... When there is a load from the house on the system,
>> everything works fine... but when the load on the genny drops to about
>> an input amps on the Trace metering of 01, the inverter starts
>> cycling... connecting to the generator and then disconnecting to it
>> every 30 seconds or so. If I add a load (say 2, 250 watt heat lamps or
>> setting the battery float or bulk settings higher) the inverter stays
>> connected to the genny.
>>
>> Genny voltage and frequency are within acceptable windows... and as I
>> said if loaded everything is fine. I would think even without a load,
>> the inverter would stay synched to the genny. It isn't too big of a deal
>> as I would only use this for battery charging when the grid is down and
>> batteries needing it so there would be plenty of load.
>>
>> Thanks,
>>
>> Todd


- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

___________________________________________________________
T O P I C A  http://www.topica.com/t/17
Newsletters, Tips and Discussions on Your Favorite Topics



More information about the RE-Wrenches mailing list