two Trace SW4048's in parallel [RE-wrenches]
Don Loweburg, Offline
i2p at aol.com
Sun Aug 20 13:53:15 EDT 2000
In a message dated 08/20/2000 9:39:07 AM Pacific Daylight Time,
joe.schwartz at homepower.com writes:
<< . You may need separate, isolated neutral busses for each inverter in the
>panel. May not. I've had some strange feedback into the Trace SW's from
>common neutrals, and think this may cause a problem. (Something like the
>inverter #2 thinking that it is getting its supply fed back into it's
>input.)
>
>Anyone else have an opinion on this?
We run four inverters up at Home Power. Neutral is common among them
via the neutral/ground bond. I was concerned that this would be
p >>
Not sure what the actual details are here (and this can be the most
important thing)
In general- each inverter should have it's own neutral wire run to a common
system neutral - this common neutral will also be bonded to the system ground
at a single point. This neutral is common to everything, generator, all
inverters, all loads.
Don Loweburg
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list