SW4048 giving me grief [RE-wrenches]

Kurt Nelson, SunWise sunwise at win.bright.net
Mon Jul 3 20:52:36 EDT 2000


Back on the SW inverter problem from Donna and responded to by Steve.  I
really like Steve's caution about cordless tool battery chargers.  Never
thought of it that way, but with inverter cyclying in and out of sleep (I
have seen this happen on may small induction loads), the tool battery
regulator may not operate correctly.  I have a client who has adjusted his
DR's sleep setting to where his cordless shaver won't wake the inverter, but
receives power when another device wakes the Trace.  It has worked well for
him but I could see the possible problem, espically if the inverter is
cycyling as frequently as I have seen some do when connected to small
cordelss chargers. 

On the battery bubbling, I am perhaps confused.  I thought Donna might be
adjusting the HVD of the Trace itself, not the setting that is actually
designed to regulate charging.  I don't have my manual in from of me, but
there is a HVD setting that is set to shut off the Trace if the battery
voltage should exceed design limits for the inverter.  If Donna was changing
this setting while float or bulk settings were left high??  Maybe it would
be good to reset the inverter to factory spec's and reprogram to new, well
thought-out settings.

Kurt Nelson

At 08:52 PM 7/1/00 -0700, you wrote:
>You set the HVD to 57 volts and its still bubbling the batteries.  You did
>not say if the battery voltage was at 57 or had exceeded it?  If not
>exceeded, its a function of the batteries, set it lower. If it has gone 1 or
>2 or so volts over 57, it can be a function of the temp compensation in the
>inverter, and you can set the voltage etc to account for that. Are you using
>the temp sensor and is it attached to the battery?
>
>The drill chargers should not be having trouble on a sine wave in my
>experience.  I have not heard of any interference by the Trace waveform of
>SW to these but there are two other things that can do it that should be
>easy to check.
>1.  Did you check the actual AC voltage input to them? It happened with the
>generator running so that could be a voltage factor. I did have one melt
>down but the cause turned out to be that rain had flooded the Makita charger
>overnight.
>2. This may be the real answer:  If the inverter goes into search mode and
>back out, cycling with a partial load from just the charger on overnight,
>each time it starts up and shuts down it can reset the cordless tool
>automatic charger to full bulk mode for a few seconds, so constant cycling
>like that is a hazard to the chargers. And it will do that if the charger is
>the only load.
>
>Steve Willey   www.backwoodssolar.com
>Backwoods Solar Electric Systems
>
>----- Original Message -----
>From: Donna Fischer, Amazon Power <amazonpower at hotmail.com>
>To: <RE-wrenches at topica.com>
>Sent: Saturday, July 01, 2000 7:20 PM
>Subject: SW4048 giving me grief [RE-wrenches]
>
>
>> Hi folks - I could really use some help.  I've now installed three SW4048
>> inverters, two in one system, and in both cases they're overcharging the
>> batteries.  On the first set I set the HVD to 57 volts and, after reading
>> some of the comments here I set them on sell.  They're still bubbling the
>> batteries!  The second set (both systems have 1165 ah Hup batteries) have
>> been at 62 volts for a  few days.  It's a construction site and they're
>> running a generator through the inverter.  Today two cordless drill
>> batteries got fried while charging and the general contractor is upset,
>and
>> I don't have any real answers for him.  He wants me to go fix everything
>and
>> explain what's going on and I don't really know.  Help!
>> ________________________________________________________________________
>> Get Your Private, Free E-mail from MSN Hotmail at http://www.hotmail.com
>>
>> - - - - - - -
>> To send a message to the list use: <RE-wrenches at topica.com>
>>
>> To view an archive of previous messages go to:
><http://www.topica.com/lists/RE-wrenches/
>>
>> To unsubscribe send an email message to:
><RE-wrenches-unsubscribe at topica.com>
>>
>> To check out who the other RE-Wrench participants are, go to
><http://www.mrsharkey.com/wrenches/>
>>
>> Hosted by Home Power magazine: <http://www.homepower.com>
>>
>> for info contact: <michael.welch at homepower.com>
>> ___________________________________________________________
>> T O P I C A  The Email You Want. http://www.topica.com/t/16
>> Newsletters, Tips and Discussions on Your Favorite Topics
>>
>
>- - - - - - -
>To send a message to the list use: <RE-wrenches at topica.com>
>
>To view an archive of previous messages go to:
<http://www.topica.com/lists/RE-wrenches/
>
>To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>
>
>To check out who the other RE-Wrench participants are, go to
<http://www.mrsharkey.com/wrenches/>
>
>Hosted by Home Power magazine: <http://www.homepower.com>
>
>for info contact: <michael.welch at homepower.com>
>___________________________________________________________
>T O P I C A  The Email You Want. http://www.topica.com/t/16
>Newsletters, Tips and Discussions on Your Favorite Topics
>
>

- - - - - - -
To send a message to the list use: <RE-wrenches at topica.com>

To view an archive of previous messages go to: <http://www.topica.com/lists/RE-wrenches/

To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>

To check out who the other RE-Wrench participants are, go to <http://www.mrsharkey.com/wrenches/>

Hosted by Home Power magazine: <http://www.homepower.com>

for info contact: <michael.welch at homepower.com>
___________________________________________________________
T O P I C A  The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics


More information about the RE-Wrenches mailing list