If you have 4 - L-16's on a SW4024 I don't think you have enough battery for
an inverter of that size (you know that), so I would expect it to drag the
voltage down in a hurry. 120 amps will charge the batteries too fast, so 60
is probably a happy medium, but you could bump it up to 80 to 90 amps to get
to the upper limit.
The Peukerts exponent is 1.28 if I remember correctly.
If you take 200 AH from the battery bank @ a 60 amp charge it will take
around 31/2 to 4 hours or probably longer to charge them I would expect. In
reality it will probably be longer.
Sometimes I think the e-meter does all it's calculating at the very end of
its charge cycle, I have seen it drop 200 AH in a few seconds (or so it
seems), reset to zero AH and start flashing as soon as I turn my back. (Is
this similar to a watched pot never boiling?)
Do you have the temp. compensated for? It is in centigrade if you don't have
the probe, so you have to think about it.
I have always found battery voltage to be tricky, the battery needs to sit
for several hours unused to be accurate, otherwise I have always found the
readings to be on the low side. I just quit worrying about it! The E-Meter
sure beats using a hydrometer every hour.....
Bob
-----Original Message-----
From: cvsolar at aol.com [mailto:cvsolar at aol.com]
Sent: Monday, May 01, 2000 10:55 PM
To: RE-wrenches at topica.com
Subject: E-meter [RE-wrenches]
Hi all,
I am doing another experiment at my house (along with the humming DC250)
to determine the negative aspects of an undersized battery bank. I have
gone
to manual generator start so I can play with the battery state of charge. I
have 4 Trojan L16G batteries in a 24v bank feeding the SW4024. Loads vary
from a base of 4 to 8 amps to a peak of 70 to 80 amps. Charge rate with my
Yamaha 4600 is set at 60 amps. Because I have been hitting the batteries
hard at both ends, I have noticed a deterioration in the batteries capacity
(in only 4 weeks of usage) . I will get down to 80% on the e-meter and
negative amp hours agree but my battery voltage is way down indicating less
than 50% left. I fiddled with the Peukerts exponent setting and set it to
1.5 (the maximum) and it didn't seem to make any difference. Does the
e-meter just lose its ability to properly track the battery at high loads?
Anyone had any experience with this. I saw a similar problem with one
installed system with big loads and small battery bank.
Unfortunately I did not have the e-meter on my old bank of 16 T105's that
were worn out so I don't know what the indications of a failed battery would
look like. These batteries charge to 28.8 without any trouble but they are
having a fast voltage drop similar to my worn out T105's (though not as bad)
The negative amp hours on my e-meter seem to be correct based on my loads.
Battery specific gravity reading indicates batteries are not really fully
charged after running the generator for two hours at 28.8v bulk absorption
charge. Current drops off normally. Does this have something to do with
the HUMMMMM? I'm confused!
John Blittersdorf
CVSolar
- - - - - - -
To send a message to the list use: <RE-wrenches at topica.com>
To view an archive of previous messages go to:
<http://www.topica.com/lists/RE-wrenches/
To unsubscribe send an email message to:
<RE-wrenches-unsubscribe at topica.com>
To check out who the other RE-Wrench participants are, go to
<http://www.mrsharkey.com/wrenches/>
Hosted by Home Power magazine: <http://www.homepower.com>
for info contact: <michael.welch at homepower.com>
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
- - - - - - -
To send a message to the list use: <RE-wrenches at topica.com>
To view an archive of previous messages go to: <http://www.topica.com/lists/RE-wrenches/
To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>
To check out who the other RE-Wrench participants are, go to <http://www.mrsharkey.com/wrenches/>
Hosted by Home Power magazine: <http://www.homepower.com>
for info contact: <michael.welch at homepower.com>
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list