<div dir="ltr"><div>Hi, Mechanics ~ </div><div><br></div><div>The general contractor put in a 2&quot; PVC pipe before pouring the slab. The pipe has a 90 degree sweep so there&#39;s a vertical pipe stub.  </div><div>He thought there would be no code inspections for this remote property... oops. </div><div><br></div><div>I now must use this plastic pipe for incoming PV wires. These wires will terminate on a MidNite Power MN15\u201112KW\u2011AIO, so question one:</div><div>Without embarrassing myself, can I argue that this qualifies for the exemption as a PV ICS (Photovoltaic Integrated Control System)?  </div><div>The PV arrays will be on top of an open horse shed, so I don&#39;t plan on any form of &quot;rapid shutdown&quot;. </div><div><br></div><div>Assuming that the above exemption won&#39;t get me off the hook, what are your suggestions for retrofit? My five wires could comfortably fit 1&quot; trade size EMT</div><div>conduit. If I cut the PVC stub then glue on a male adapter (so I could mount a metal box low to the floor), there&#39;s still some unprotected plastic</div><div>due to the hub of the male adapter. </div><div><br></div><div>Also: what would have been better initial tradecraft in a non-retrofit slab situation, assuming that one wants to use PVC for most of the pipe run while still satisfying</div><div>NEC 690.31(D) (1)?  </div><div><br></div><div>Thanks in advance, Mechanix. &quot;The Wrench List is the Bomb!&quot;</div><div><br></div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div>Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com" target="_blank">www.abrahamsolar.com</a><br><br></div><div>Cell phone or for text messaging: 970-946-6584</div></div></div></div></div>