<p>If you look at the graphics on the website, they're really
showing temporary mounted PV. This is not designed to be
hardwired for an NEC approved installation. It's like a portable
generator. I'd get the guy a couple of modules on folding racks,
and make up a 50 ft portable cable so he can set the modules in
the sun to charge if its a long outage. I've done a few of these
for folks, using like the little Jackery systems. Ryobi,
Milwaukee, etc make "battery generators"; same concept: you're
not going to hardwire them in to anything. Its got to be portable
to stay compliant. </p>
<p>If he wants the PV mounted to the roof, you're either throwing
code out the door, or he needs a different inverter setup. </p>
<p>Ray Walters<br>
Remote Solar</p>
<div class="moz-cite-prefix">On 4/27/2026 3:36 PM, MDElectricSolar
via RE-wrenches wrote:<br>
</div>
<blockquote type="cite"
cite="mid:588D216E-52CF-4C01-BD91-75E2F7E69DB0@gmail.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
What is the input voltage requirement for this PV module to Eco
flow unit? It may be a low-voltage input which may not require any
metal conduit at all?
<div><br id="lineBreakAtBeginningOfSignature">
<div dir="ltr">
<div>Michael D Nelson</div>
<div>MD Electric & Solar, Inc.</div>
<div>707-684-0064 mobile</div>
<div>707-884-1862 office</div>
<div><a class="moz-txt-link-abbreviated" href="http://www.mdelectricsolar.com">www.mdelectricsolar.com</a></div>
<div><a class="moz-txt-link-abbreviated" href="http://www.facebook.com/mdelectricandsolar">www.facebook.com/mdelectricandsolar</a></div>
<br>
</div>
<div dir="ltr"><br>
<blockquote type="cite">On Apr 27, 2026, at 2:23\u202fPM, Zeke
Yewdall via RE-wrenches
<a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></a> wrote:<br>
<br>
</blockquote>
</div>
<blockquote type="cite">
<div dir="ltr">\ufeff
<div dir="ltr">
<div>I can't see any way to do this. Some sort of metal
conduit or metal clad cable (not EMT specifically) is
required by 690.31(D)(1) and I dont think the PVHCS
exception would apply to this. This is an issue with
european style inverters with direct MC4 connectors for
the PV input.</div>
<div><br>
</div>
<div>Short of putting the entire inverter inside another
box, or bolting a box onto the outside of the inverter
that enclosed the MC4 connectors....</div>
<div><br>
</div>
<div>Zeke</div>
<div dir="ltr"><br>
</div>
<div dir="ltr">Date: Mon, 27 Apr 2026 13:46:25 -0400<br>
From: Howie Michaelson <<a
href="mailto:Howie.Michaelson@gmail.com"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">Howie.Michaelson@gmail.com</a>><br>
To: RE-wrenches <<a
href="mailto:re-wrenches@lists.re-wrenches.org"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>><br>
Subject: [RE-wrenches] Code compliant PV wire to an
EcoFlow DELTA Pro<br>
Ultra Inverter/Charger<br>
Message-ID:<br>
<CAHMeMski8wRM=<a
href="mailto:LnqdqOoPd2AY4oq5w6EddcYpGDvcq_NkJjcDA@mail.gmail.com"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">LnqdqOoPd2AY4oq5w6EddcYpGDvcq_NkJjcDA@mail.gmail.com</a>><br>
Content-Type: text/plain; charset="utf-8"<br>
<br>
Hi All,<br>
I have a potential client who currently has an EcoFlow
DELTA Pro Ultra<br>
<<a href="https://www.ecoflow.com/us/delta-pro-ultra"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">https://www.ecoflow.com/us/delta-pro-ultra</a>>
inverter installed in his<br>
house for battery backup. He wants to install
roof-mounted PV. I don't see<br>
how to connect PV into the Inverter/Charger using EMT
for code compliance.<br>
Has anyone done something similar? Can anyone think of
a code-compliant<br>
method to bring PV into this setup?<br>
<br>
Howie Michaelson</div>
<br>
<div class="gmail_quote gmail_quote_container">
<div dir="ltr" class="gmail_attr">On Mon, Apr 27, 2026
at 1:18\u202fPM <<a
href="mailto:re-wrenches-request@lists.re-wrenches.org"
moz-do-not-send="true" class="moz-txt-link-freetext">re-wrenches-request@lists.re-wrenches.org</a>>
wrote:<br>
</div>
<blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">Send
RE-wrenches mailing list submissions to<br>
<a
href="mailto:re-wrenches@lists.re-wrenches.org"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web,
visit<br>
<a
href="http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org</a><br>
or, via email, send a message with subject or body
'help' to<br>
<a
href="mailto:re-wrenches-request@lists.re-wrenches.org" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">re-wrenches-request@lists.re-wrenches.org</a><br>
<br>
You can reach the person managing the list at<br>
<a
href="mailto:re-wrenches-owner@lists.re-wrenches.org" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">re-wrenches-owner@lists.re-wrenches.org</a><br>
<br>
When replying, please edit your Subject line so it is
more specific<br>
than "Re: Contents of RE-wrenches digest..."<br>
<br>
<br>
When responding to posts within the Digest, be sure to
restore the Subject: line to the exact original, and
please edit out any extraneous lines from the quoted
message.<br>
<br>
<br>
<br>
Today's Topics:<br>
<br>
1. Peerless Gas Range Question (<a
href="mailto:drake.chamberlin@redwoodalliance.org"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">drake.chamberlin@redwoodalliance.org</a>)<br>
2. Code compliant PV wire to an EcoFlow DELTA Pro
Ultra<br>
Inverter/Charger (Howie Michaelson)<br>
3. Re: Code compliant PV wire to an EcoFlow DELTA
Pro Ultra<br>
Inverter/Charger (Glenn)<br>
<br>
<br>
----------------------------------------------------------------------<br>
<br>
Message: 1<br>
Date: Mon, 27 Apr 2026 10:09:42 -0400<br>
From: <a
href="mailto:drake.chamberlin@redwoodalliance.org"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">drake.chamberlin@redwoodalliance.org</a><br>
To: RE-wrenches <<a
href="mailto:re-wrenches@lists.re-wrenches.org"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>><br>
Subject: [RE-wrenches] Peerless Gas Range Question<br>
Message-ID: <<a
href="mailto:b2d629c301707ce64dbd99a52e3911da@redwoodalliance.org"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">b2d629c301707ce64dbd99a52e3911da@redwoodalliance.org</a>><br>
Content-Type: text/plain; charset="us-ascii";
Format="flowed"<br>
<br>
<br>
Does anyone know where the spark generator is on a
Peerless gas range? <br>
Tech support can sell us a new one, but can't tell me
where the unit may <br>
be found on the stove.<br>
<br>
It may not need a new one. The symptoms are a bit
confusing. The <br>
sparkers work well on all burners until the oven is
used. After that <br>
they won't work for about 2 days. Then they start
working again until <br>
the oven is used again.<br>
<br>
The situation warrants investigation before investing
in a new spark <br>
generator.<br>
<br>
Thank you,<br>
<br>
Drake<br>
<br>
_Drake Chamberlin_<br>
<br>
_Athens Electric LLC_<br>
<br>
_Ohio Electrical Contractor's License 44810_<br>
<br>
_NABCEP Certified PV Installation Professional_<br>
<br>
--<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/c9192082/attachment-0001.htm"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/c9192082/attachment-0001.htm</a>><br>
<br>
------------------------------<br>
<br>
Message: 2<br>
Date: Mon, 27 Apr 2026 13:46:25 -0400<br>
From: Howie Michaelson <<a
href="mailto:Howie.Michaelson@gmail.com"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">Howie.Michaelson@gmail.com</a>><br>
To: RE-wrenches <<a
href="mailto:re-wrenches@lists.re-wrenches.org"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>><br>
Subject: [RE-wrenches] Code compliant PV wire to an
EcoFlow DELTA Pro<br>
Ultra Inverter/Charger<br>
Message-ID:<br>
<CAHMeMski8wRM=<a
href="mailto:LnqdqOoPd2AY4oq5w6EddcYpGDvcq_NkJjcDA@mail.gmail.com"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">LnqdqOoPd2AY4oq5w6EddcYpGDvcq_NkJjcDA@mail.gmail.com</a>><br>
Content-Type: text/plain; charset="utf-8"<br>
<br>
Hi All,<br>
I have a potential client who currently has an EcoFlow
DELTA Pro Ultra<br>
<<a
href="https://www.ecoflow.com/us/delta-pro-ultra"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">https://www.ecoflow.com/us/delta-pro-ultra</a>>
inverter installed in his<br>
house for battery backup. He wants to install
roof-mounted PV. I don't see<br>
how to connect PV into the Inverter/Charger using EMT
for code compliance.<br>
Has anyone done something similar? Can anyone think
of a code-compliant<br>
method to bring PV into this setup?<br>
<br>
Howie Michaelson<br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL: <<a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/871cc0e9/attachment-0001.htm"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/871cc0e9/attachment-0001.htm</a>><br>
<br>
------------------------------<br>
<br>
Message: 3<br>
Date: Mon, 27 Apr 2026 14:19:55 -0400<br>
From: Glenn <<a href="mailto:glenn.burt@glbcc.com"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">glenn.burt@glbcc.com</a>><br>
To: RE-wrenches <<a
href="mailto:re-wrenches@lists.re-wrenches.org"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>><br>
Subject: Re: [RE-wrenches] Code compliant PV wire to
an EcoFlow DELTA<br>
Pro Ultra Inverter/Charger<br>
Message-ID: <<a
href="mailto:040db52a-d4c0-46aa-a28d-90a5ce8fb2e3@email.android.com"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">040db52a-d4c0-46aa-a28d-90a5ce8fb2e3@email.android.com</a>><br>
Content-Type: text/plain; charset="us-ascii"<br>
<br>
An HTML attachment was scrubbed...<br>
URL: <<a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/ae1e7f2a/attachment-0001.htm"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260427/ae1e7f2a/attachment-0001.htm</a>><br>
<br>
------------------------------<br>
<br>
Subject: Digest Footer<br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a
href="http://re-wrenches.org" rel="noreferrer"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
<br>
List Address: <a
href="mailto:RE-wrenches@lists.re-wrenches.org"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one
doesn't work, try the other:<br>
<a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org"
rel="noreferrer" target="_blank"
moz-do-not-send="true" class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
<br>
<br>
<br>
------------------------------<br>
<br>
End of RE-wrenches Digest, Vol 19, Issue 128<br>
********************************************<br>
</blockquote>
</div>
<div><br clear="all">
</div>
<br>
<span class="gmail_signature_prefix">-- </span><br>
<div dir="ltr" class="gmail_signature">
<div dir="ltr">
<div>
<div dir="ltr">Zeke Yewdall
<div>PV Engineer</div>
<div>NABCEP #031508-89</div>
<div><a href="mailto:zeke@darkforestsolar.com"
target="_blank" moz-do-not-send="true"
class="moz-txt-link-freetext">zeke@darkforestsolar.com</a></div>
<div>303-523-3592</div>
</div>
</div>
</div>
</div>
</div>
<span>_______________________________________________</span><br>
<span>List sponsored by Redwood Alliance</span><br>
<span></span><br>
<span>Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a></span><br>
<span></span><br>
<span>List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
<span></span><br>
<span>Change listserver email address & settings:</span><br>
<span><a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
<span></span><br>
<span>There are two list archives for searching. When one
doesn't work, try the other:</span><br>
<span><a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a></span><br>
<span><a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br>
<span></span><br>
<span>List rules & etiquette:</span><br>
<span><a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a></span><br>
<span></span><br>
<span>Check out or update participant bios:</span><br>
<span><a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a></span><br>
<span></span><br>
</div>
</blockquote>
</div>
<br>
<fieldset class="moz-mime-attachment-header"></fieldset>
<pre wrap="" class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>
</pre>
</blockquote>
</body>
</html>