<div dir="ltr"><div>The default settings on the PS2512 don&#39;t look too bad for LFP -- 14.4 absorb and 13.4 float.  The 2 hour default absorb could be the issue, if you didn&#39;t turn the generator off or unplug from shore power after it reached absorb voltage.  And it would depend on the BMS for the battery that you use... the rackmount EG4&#39;s that I&#39;ve used don&#39;t really like more than 14.1 or 14.2 for very long, even though you could custom set your own BMS for 14.4 without problems with a 4 cell LFP.  Most rackmount batteries are not rated for mobile use with vibration and such anyway though... I think I&#39;ve seen some of the cheap Li-time batteries that spec 14.6 volts, so might work with that -- though I&#39;ve also found that a lot of them give you the spec for the emergency shutoff voltage, not the recommended absorb voltage.   Also, a lot of the cheaper BMS&#39;s can&#39;t handle the capacity surge from turning on a large inverter like this, so would need a precharge circuit too.    I think it&#39;s probably possible, but not a definite yes to switch it to LFP.</div><div><br></div><div>Zeke</div><div><br></div><div>&gt; On Wed, Apr 22, 2026 at 10:52?AM Chris Daum via RE-wrenches &lt;</div>
&gt; <a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br>
&gt;<br>
&gt;&gt; Hi folks:<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt;<br>
&gt;&gt; Some of these antiques just won?t die.  I have a fellow with a Trace<br>
&gt;&gt; PS2512 in his RV (lightly used).  He?s very interested in lithium batteries<br>
&gt;&gt; ? there is no PV in this system; his battery charging is done by shore<br>
&gt;&gt; power or generator.  Is there any sort of remote that will work with his<br>
&gt;&gt; old beast, so he can accommodate the LFP technology?  Or is he doomed to<br>
&gt;&gt; upgrade his inverter?   Any advice is very helpful.  Of course, the manual<br><div>
&gt;&gt; for the PS series doesn?t mention LFP technologies!</div><div><br></div><div><br></div><div><br clear="all"></div><br><span class="gmail_signature_prefix">-- </span><br><div dir="ltr" class="gmail_signature"><div dir="ltr"><div><div dir="ltr">Zeke Yewdall<div>PV Engineer</div><div>NABCEP #031508-89</div><div><a href="mailto:zeke@darkforestsolar.com" target="_blank">zeke@darkforestsolar.com</a></div><div>303-523-3592</div></div></div></div></div></div>