<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div dir="ltr"></div><div dir="ltr">Thx Chris for the info.&nbsp;</div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr">A person I did a grid tie design help with decided to get one.&nbsp;</div><div dir="ltr"><br></div><div dir="ltr">Short comings that I see so far ( info is pretty weak) is no AC coupling as best I can tell?</div><div dir="ltr">Which of course makes integration with existing solar all but impossible.&nbsp;</div><div dir="ltr">This guy has a ground mount so it\u2019ll be relatively easy.&nbsp;</div><div dir="ltr"><br></div><div dir="ltr">It\u2019s costing them close to 20,000$ for parts and install.&nbsp;</div><div dir="ltr"><br></div><div dir="ltr">I\u2019ll see it when it gets installed might be a few months with permitting etc. I\u2019ll give a report&nbsp;</div><div dir="ltr"><br></div><div dir="ltr">Jay</div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br><blockquote type="cite">On Apr 6, 2026, at 7:58\u202fPM, Chris Sparadeo &lt;sparadeo.chris@gmail.com&gt; wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff<div dir="ltr"><p>Jay,<br><br>Let me attempt to give you a quick(ish) overview of this system.&nbsp;</p>
<p>The \u201cGM Energy Storage Bundle\u201d is a V2H / ESS setup made up of a salad of white-labeled components and GM-native equipment. It can be configured as V2H only, or paired with 10\u201335 kWh of stationary storage for added redundancy.&nbsp;</p>
<p>At the heart of the system is the Home Hub (MID). It has an integrated 10 circuit busbar rated at 164A (randomly), with a max subfeed of 125A. No smart load functionality. It can be set up as either a 100A-200A main lug only OR with a 100- 200A Eaton CSR main breaker. A little odd on paper since it\u2019s 200A in but only 125A out. If you\u2019re integrating AC-coupled solar, you\u2019ll need to add a GM Acrel meter inside the Home Hub. There\u2019s also an optional 100A non-backed-up loads panel, which can only be used&nbsp; for the EVSE circuit.</p>
<p>The PowerShift charger is the bidirectional EVSE. It\u2019s rated at max 80A continuous charge (100A circuit), and it can be derated down to around 16A without affecting backup performance. The AC circuit must originate from the non-backed-up section of the system. The PowerShift also includes a 50A DC connection that feeds the GM Energy Inverter. One thing to note is that when the charger is in discharge mode, the vehicle can\u2019t recharge from either AC or DC-coupled solar.</p>
<p>The Energy Inverter is a 9.6 kW multimode inverter with four MPPT inputs if you\u2019re DC coupling. If there\u2019s no PowerBank installed, you need a Dark Start Battery. That comes with a prefab whip and connects straight into the inverter to provide 12V control power so the system can start up during an outage. No direct generator integration. Select 3 phase configuration, but really a split phase offering.&nbsp;</p>
<p>System Advantages:</p>
<p>GM has made bidirectional capability standard across all new GMC, Chevy and Cadillac models, which is a big plus with compatibility&nbsp;hunting. Everything runs through the same GM app as the vehicles, so it\u2019s a pretty clean user experience. The PowerShift setup also gives you some flexibility since it uses both AC and DC paths. That makes it easier to derate the&nbsp;charger or install it on a load management device to get that load calc to pass.&nbsp;&nbsp;</p>
<p>System Disadvantages</p>
<p>The product is still pretty new, and it shows. Commissioning can take a while, usually around two hours but sometimes much longer. I've heard horror&nbsp;stories of 6+ hrs when things go wrong.&nbsp; The 125A subfeed limit in the Home Hub can be a constraint depending on the job. No one wants to derate their&nbsp;brand new 200A MSP to 125A. Also, the PowerBank is only IP55 rated, and the install manual suggests avoiding moist locations, even indoors, which can be limiting, especially in jurisdictions where indoor ESS installs are highly&nbsp;regulated (thinking of San Jose and LA County). There have also been some reliability concerns with components like the Home Hub, inverter, and PowerShift. If something fails, it can essentially brick and need full replacement.<br><br>Overall, it's the one of the few bidirectional systems on the market that is currently functional and confirmed compatible with multiple vehicles. If you are up for enduring the growing pains of a large automotive company testing out our market.... give it a try! A solid B-&nbsp;</p></div><br><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Sat, Apr 4, 2026 at 6:57\u202fPM Jay via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">Hi all<br>
<br>
Does anyone know anything about the new to me Chevy V2H inverter, and other equipment?<br>
Thanks<br>
<br>
Jay<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
</div></blockquote></body></html>