<div dir="ltr"><div>I&#39;ve got a system that is throwing occasional battery voltage sensor errors and shutting down, then turning back on when the error clears a few seconds to a minute later. Stacked system, two VFX3524&#39;s, two FM60&#39;s, 600AH of LFP batteries (EG4 LL rackmounts) in open loop.  It tends to do this when the batteries are full with lots of sun out.</div><div><br></div><div>I am not 100% sure that the batteries are happy -- it&#39;s possible that the BMS&#39;s are shutting off charging, and that&#39;s causing a spike in the bus voltage the inverters are seeing. But if that&#39;s so, I don&#39;t see anything recording it.  Charge controllers both report 28.2 volts as highest voltage for the day.  I adjusted the absorb voltage and time down a little bit -- we had set it up a few months ago at 28.2 for 2 hours to try to get the batteries to balance better, but I took it down to 28.0 for 1 hour now.  Float was at 27.1, I reduced it to 27.0.</div><div><br></div><div>But, could this be an actual problem with the inverters?  Or likely still a programming issue?</div><div><br></div><div>Z</div><span class="gmail_signature_prefix">-- </span><br><div dir="ltr" class="gmail_signature"><div dir="ltr"><div><div dir="ltr">Zeke Yewdall<div>PV Engineer</div><div>NABCEP #031508-89</div><div><a href="mailto:zeke@darkforestsolar.com" target="_blank">zeke@darkforestsolar.com</a></div><div>303-523-3592</div></div></div></div></div></div>