<div dir="ltr"><div>In that case, we&#39;re getting way off track and way more complicated :P  </div><div><br></div><div>Just put a contactor between the PV array and the POI using the NC contacts, with the coil powered off the generator.  Then the PV array can never backfeed the generator because it&#39;ll be turned off anytime the generator is running.</div><div><br></div><div>Zeke</div><div><br></div><div>------------------</div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr">Thanks but I&#39;m just trying to grid-tie a small Enphase array without ESS
 where the point of interconnection is on the customer side of the 
generator/ATS.<br>
<br>
Trying to use existing wires in place to simplify and lower costs...but 
the generator is my constraint because I need the PoI to be on line side
 of the ATS.<br>