<div dir="ltr">Greetings Allan,<br><div><br></div><div>Sorry for the lack of response to your inquiry a few weeks back. Starting in 2017 I too have had impressive success and support from the BPE folks. 88 cabinets installed over 53 sites. One BMU failure on my second install but it wasn&#39;t a true failure of the main hardware. Somehow too much current tried to find it&#39;s way through the momentary start button and burned up the small 18 gauge (or similar) conductors. A fix was shipped and power was immediately restored to the site. Never turned off actually, only downtime was for the swap. Only noticed because the client reported a strong burning smell so I returned to the site to find the surprise.</div><div><br></div><div>Another site&#39;s BMU failed on a newly installed system about 2 years ago. This one appeared to have occurred due to excessive current beyond what the BMU is rated for. Although it was a commonly successful inverter pairing with an 8 KW Radian, there was evidence that the  tenants were frequently not paying attention to consumption habits and there was datalogs (Egauge and Vue) of brief moments near 10 KW&#39;s of consumption. At first BPE hesitated a bit and noted that it would not automatically be covered until they could perform a failure analysis on the returned unit but ultimately they took care of me. Jody and the crew always supported me and always felt like an extended family. Some may or may not remember but there was even a brief period on their website that stated &quot;we don&#39;t believe in fine print&quot;.</div><div><br></div><div>I also had one Sony battery module fail about 5 years ago. Luckily it was on my own system otherwise I might not have believed it or found it so easily. Once again a replacement was sent out immediately and I never had any other failures with the batteries. Once I had a single battery LED status light go from green to blinking orange but upon their advice powered down the HI cabinet and the problem was never to be seen again.</div><div><br></div><div>Due to a few clients selling properties and others wanting to double capacity in their 8 KWH cabinets I have now found myself with two empty cabinets therefore I can rely on those as backups should a BMU failure occur. Additionally, with a Midnite Powerflo16 now being barely just 3x what a replacement BMU costs it seems there is plenty of strategy to just stock Powerflos and play the swap game with other clients as necessary. Part of me would like to have another BMU on my shelf and I can see the security of having one but too many times I&#39;ve spent thousands of dollars only to have unsellable inventory years later.</div><div><br></div><div>I hope Blue Planet comes back and they can offer a drop in replacement that would allow us to not have to alter the mechanical rooms but I imagine these batteries still have many useful years of service ahead of them. Obviously would be some implications of placing more than 20 KWH&#39;s in a single cabinet but sure would be nice to leave them in place once the batteries need to be replaced. Based on conclusions in the ITP test years ago the Forelion cells seemed quite promising. Sure seems like our Blue Ion sites are in a good position for continued success.</div><div><br></div><div>Nick</div></div><br><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Sat, Dec 20, 2025 at 11:13\u202fAM Sindelar Solar via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><u></u>

  
    
  
  <div bgcolor="#FFFFFF">
    Esteemed Wrenches,<br>
    Following up on this thread that I started in early December: I sent
    an email to my seven former Blue Planet customers, that included the
    texts of BPE&#39;s website homepage announcement of shutting down
    operations and the letter offering spare BMUs on closeout. I
    remained neutral, equating the offer to buying insurance that you
    hope never to need. Three customers responded, and I spoke with
    three more by phone, with one yet to reply. All six are fully
    satisfied with their BPE batteries, except for one client&#39;s
    expressed difficulty with the loss of the online portal interpreting
    the E-Gauge information. None has had any failures or issues since
    installation. <br>
    Three of the six chose to order a spare BMU, each of whom has the
    financial means to buy it. I&#39;ll act as a pass-through, with no
    markup.<br>
    <br>
    I expected more response on this list, given all of the discussions
    regarding LiFP suppliers and results with other brands. The dearth
    of discussion suggests to me that there have been very few issues
    with the products and with the support while BPE was still in
    operation.<br>
    <br>
    The only contact I have at what&#39;s left of BPE is my former Regional
    Sales Manager, Lori Ann Saunders, <a href="mailto:lori@blueplanetenergy.com" target="_blank">lori@blueplanetenergy.com</a>.<br>
    Allan<br>
    <br>
    <div>On 12/20/2025 8:01 AM, Jerry Shafer via
      RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="auto">To all the blue planet installers and to the
        wrenches too,
        <div dir="auto">Blue planet is not the first nor will it be the
          last to terminate a product line.</div>
        <div dir="auto">I personally have been installing blue planet
          from befor the 16 was released. I have only one issue with a
          system we had 6 16 k and one had a battery issue, quickly
          resolved and back up, no BMU issues so far ever so its a
          difficult call to drop the cash to sit on your shelf or not.
          It may be very valuable to have one down the road, look at
          Apple, Microsoft or maybe a Saab or Desoto. To invest or not
          to and that&#39;s the bottom line. For me as much as would like to
          have a spare l don&#39;t think l can right now.</div>
        <div dir="auto">Fun times</div>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Tue, Dec 9, 2025, 12:22 AM
          Mark Downing via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;
          wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div dir="ltr">
            <div style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:11pt;color:rgb(0,0,0)">
              All detailed in here</div>
            <hr style="display:inline-block;width:98%">
            <div id="m_-5539122034176705999m_8171757462207905075divRplyFwdMsg" dir="ltr"><font face="Calibri, sans-serif" style="font-size:11pt" color="#000000"><b>From:</b> RE-wrenches &lt;<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" rel="noreferrer" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>&gt;
                on behalf of Sam Haraldson via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
                <b>Sent:</b> Monday, December 8, 2025 10:33 AM</font>
              <div> </div>
            </div>
            <div>
              <div dir="ltr">
                <div>Good Morning, Allan,</div>
                <div>I&#39;ll share my limited insight in hopes it proves
                  valuable to you.  </div>
                <br>
                <div>
                  <blockquote style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
                    <div bgcolor="#FFFFFF">Have you had any Blue Ion
                      battery or BMU failures?  If so, how many systems
                      have you installed, and how many failures have you
                      had? What failed, and what did you do to resolve
                      the issue? If you replaced a BMU, was the process
                      straightforward, and were you given a complete set
                      of documentation with the unit? Was the factory
                      warranty process honored? </div>
                  </blockquote>
                  <div>We have nine sites with Blue Ion installed. 
                    These range in size from a single battery module up
                    to 48 modules.  They are mated to a range of
                    chargers and inverters from Outback, Magnum,
                    Midnite, Schneider, and Sol-Ark.  We have only
                    experienced an issue at a single site and that was a
                    battery module.  Blue Ion was extremely attentive
                    from a customer service perspective.  They mailed
                    problem-specific testing equipment along with
                    the RMA&#39;ed parts, provided live customer-support
                    during the testing, and provided return shipping. 
                    All was covered by warranty (I do not know if there
                    was a labor reimbursement).</div>
                  <div><br>
                  </div>
                  <blockquote style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
                    <div bgcolor="#FFFFFF">On a related track, how have
                      you responded to Blue Planet&#39;s offer? Does it come
                      across as a valid solution? Have you bought one or
                      more spare BMUs? How are you supporting your Blue
                      Ion customers going forward? Have you received
                      support of any kind from Blue Planet? <br>
                    </div>
                  </blockquote>
                  <div>Our company took the same approach you did,
                    sending an email to our customer base informing them
                    to consider purchasing a back up BMU.  To the best
                    of my knowledge only one of our customers has opted
                    to purchase a back-up and they are an energy utility
                    with two large, high-consequence systems that easily
                    warrants the ROI.  We as a company are leaning
                    toward not purchasing one to &quot;have in stock&quot;.</div>
                  <div>Sincerely,</div>
                  <div>Sam</div>
                  <div><br>
                  </div>
                </div>
                <div>
                  <div dir="ltr">
                    <div dir="ltr">
                      <table cellpadding="0" cellspacing="0" style="font-family:Carlito,Tahoma,sans-serif">
                        <tbody>
                          <tr>
                            <td style="padding:0px 10px 0px 0px;vertical-align:top"><a href="https://onsiteenergyinc.com/" style="border:none" rel="noreferrer" target="_blank"><img alt="OnSite Energy" align="top" width="95" height="95" style="display: block;" src="https://cdn.prod.website-files.com/675cb4f269e8da457106c938/67acde8cf274634235411bdd_email-sig-logo-onsite-energy.png"></a></td>
                            <td style="padding:0px;vertical-align:top">
                              <table cellpadding="0" cellspacing="0">
                                <tbody>
                                  <tr>
                                    <td style="padding:0px 10px 0px 0px;vertical-align:bottom">
                                      <div color="#514ca0" style="padding:0px;color:rgb(81,76,160);font-size:14pt;font-weight:600;text-transform:uppercase">
                                        Sam Haraldson</div>
                                      <div color="#f9a145" style="padding:0px;color:rgb(249,161,69);font-size:11pt">Operations
                                        Specialist</div>
                                      <div color="#514ca0" style="padding:0px;color:rgb(81,76,160);font-size:8pt">(406) 551-6135</div>
                                      <div color="#514ca0" style="padding:0px;color:rgb(81,76,160);font-size:8pt"><a href="https://www.google.com/maps/search/1515+N.+Rouse+Ave+Bozeman,+MT+59715?entry=gmail&amp;source=g" target="_blank">1515 N.
                                          Rouse Ave Bozeman, MT 59715</a></div>
                                      <div color="#f9a145" style="padding:0px;color:rgb(249,161,69);font-size:8pt">Locally owned
                                        and operated since 2012</div>
                                    </td>
                                    <td style="padding:0px;vertical-align:bottom"><a href="https://onsiteenergyinc.com/bcorp" style="border:none" rel="noreferrer" target="_blank"><img alt="B Corporation" width="22" height="33" align="bottom" hspace="2" vspace="2" style="display: block;" src="https://cdn.prod.website-files.com/675cb4f269e8da457106c938/67acde8cb918886086c8a0d5_email-sig-logo-bcorp.png"></a></td>
                                  </tr>
                                </tbody>
                              </table>
                            </td>
                          </tr>
                        </tbody>
                      </table>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
          List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
          Change listserver email address &amp; settings:<br>
          <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          There are two list archives for searching. When one doesn&#39;t
          work, try the other:<br>
          <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
          <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
          List rules &amp; etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
          Ceck out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
          <span style="white-space:pre-wrap">
</span></blockquote>
      </div>
    </blockquote>
    <br>
  </div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn&#39;t work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>