<div dir="ltr"><div dir="ltr"><div><br></div></div><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Thu, Sep 4, 2025 at 5:48\u202fPM Blair May via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div style="overflow-wrap: break-word;"><div style="overflow-wrap: break-word;"><div>I use Cobra X flex and the X Flex 150 wire and have found it to be great to work w/ and it offers larger ampacity ratings. XFlex150 #6AWH is ~150A</div><div><br></div></div></div></blockquote><div><br></div><div>Note that the ampacity of Cobra X flex for NEC applications would not be 150 amps or the 118 amps Cobra lists in the specifications. For NEC purposes it is a MTW or THW type. THW type would be rated for 65 amps at a 75 degree C termination temperature.</div><div><br></div><div>There are different sets of rules that wire ampacity has to play by. NEC is very conservative. When the same wire is used as appliance wiring material (AWM) is where you can sometimes get those really high ampacities.  But for hooking up batteries and inverters and building wiring and the like ... you only get 65 amps (more or less).</div><div><br></div><div>This is a pretty common sales tactic that you will see on a lot of wires. Ampacities advertised under AWM conditions and not NEC conditions. </div></div></div>