    <p>Thanks, the problem is we need it to disconnect only upon loss of
      utility power, and it is on the battery loads panel. The panel for
      the HVAC is in another building that the HVAC serves.</p>
    <div class="moz-cite-prefix">On 8/22/2025 8:20 PM, Chris Sparadeo
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAAdbmLbWRZxUbQ6gCmmXWbkHTfu9XzULk2kqNT=-_=Rf4+w1VQ@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="auto">Hi Chris,</div>
      <div dir="auto"><br>
      </div>
      <div dir="auto">I\u2019m wondering if a load management device like
        this could be helpful? However, it does not discern between grid
        presence and island mode, so it might not fit the bill. </div>
      <div dir="auto"><br>
      </div>
      <div dir="auto">
        <div><a
href="https://www.getstepwise.com/product?gad_source=1&amp;gad_campaignid=22363404421&amp;gclid=Cj0KCQjwqqDFBhDhARIsAIHTlkub687mJZYb6g0nIR33X1eA2FVY3bMc_zBxMr44IEl5a7QenVljhUgaArKeEALw_wcB"
            moz-do-not-send="true">https://www.getstepwise.com/product?gad_source=1&amp;gad_campaignid=22363404421&amp;gclid=Cj0KCQjwqqDFBhDhARIsAIHTlkub687mJZYb6g0nIR33X1eA2FVY3bMc_zBxMr44IEl5a7QenVljhUgaArKeEALw_wcB</a></div>
        <br>
      </div>
      <div dir="auto">Quick caveat that shedding an HVAC unit
        potentially mid cycle is not ideal for the health of that
        unit\u2026but neither is an overload and subsequent power failure. </div>
      <div dir="auto"><br>
      </div>
      <div dir="auto">I do know that Lumin Smart sells remote CTs for
        grid detection. Might be worth a call to them to see if this
        fairly inexpensive product can pair with a remote contactor to
        open the HVAC circuit. </div>
      <div dir="auto"><br>
      </div>
      <div dir="auto">Best of luck! </div>
      <div dir="auto"><br>
      </div>
      <div dir="auto">-Chris </div>
      <div><br>
        <div class="gmail_quote gmail_quote_container">
          <div dir="ltr" class="gmail_attr">On Fri, Aug 22, 2025 at
            3:54\u202fPM Christopher Warfel via RE-wrenches &lt;<a
              href="mailto:re-wrenches@lists.re-wrenches.org"
              moz-do-not-send="true" class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>&gt;
            wrote:<br>
          </div>
          <blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-style:solid;padding-left:1ex;border-left-color:rgb(204,204,204)">We
            installed a 4kW Outback multimode system about 8 years ago. 
            An <br>
            electrician came in afterwards and installed 3 heat pumps on
            the battery <br>
            backed up power panels.  The Outback inverter disconnected
            on load every <br>
            time there was a power outage. The electrician really messed
            up and is <br>
            long gone. Also found out did not pull a permit. But I
            digress.  We <br>
            managed to move two of the heat pump circuit breakers to the
            utility <br>
            panel, so no longer on the battery backed up power panels. 
            The third <br>
            heat pump is the problem as it is located in an apartment
            building <br>
            remote from the main house. The whole apartment subpanel,
            including the <br>
            heat pump load  is interconnected to the "main" battery
            backed up power <br>
            panel in the home.<br>
            <br>
            A master electrician and I are considering how to shed the
            apartment <br>
            heat pump in a power outage.  We cannot easily run a
            separate circuit to <br>
            the apartment building to pick up this load.  We have
            considered a smart <br>
            panel, but the cost seems high for one circuit. Does anyone
            know of a <br>
            power line product of RF product or similar that could
            operate this <br>
            breaker when the main service panel loses power? I have been
            <br>
            unsuccessful over months of sporadic research.<br>
            <br>
            Thanks in advance.<br>
            <br>
            <br>
            Chris<br>
            <br>
            <br>
            <br>
            <br>
            <br>
            <br>
            <br>
            <br>
            -- Christopher Warfel, PE ENTECH Engineering, Inc. PO Box
            871, Block <br>
            Island, RI 02807 (401) 447-5773<br>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            Pay optional member dues here: <a
              href="http://re-wrenches.org" rel="noreferrer"
              target="_blank" moz-do-not-send="true"
              class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
            <br>
            List Address: <a
              href="mailto:RE-wrenches@lists.re-wrenches.org"
              target="_blank" moz-do-not-send="true"
              class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address &amp; settings:<br>
            <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              rel="noreferrer" target="_blank" moz-do-not-send="true"
              class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            There are two list archives for searching. When one doesn't
            work, try the other:<br>
            <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
              rel="noreferrer" target="_blank" moz-do-not-send="true"
              class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
            <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
              rel="noreferrer" target="_blank" moz-do-not-send="true"
              class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a href="http://www.re-wrenches.org/etiquette.htm"
              rel="noreferrer" target="_blank" moz-do-not-send="true"
              class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a href="http://www.members.re-wrenches.org"
              rel="noreferrer" target="_blank" moz-do-not-send="true"
              class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
      </div>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401) 447-5773</pre>