<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto">We have been using the Solark inverter for GTBB and off grid clients. In the case of low battery cut out the solar does stay alive in the background and will recharge the batteries when the sun comes out the next day and turn itself back on and provide AC power output.<div><br id="lineBreakAtBeginningOfSignature"><div dir="ltr"><div>Michael D Nelson</div><div>MD Electric &amp; Solar, Inc.</div><div>707-684-0064 mobile</div><div>707-884-1862 office</div><div>www.mdelectricsolar.com</div><div>www.facebook.com/mdelectricandsolar</div><br></div><div dir="ltr"><br><blockquote type="cite">On May 12, 2025, at 10:13\u202fAM, Ray Walters via RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt; wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff

  
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  
  
    <p>So the bypass switch gets the house power on, and I too always
      recommend a hard bypass switch. However, you still need a 48 v
      power supply to get the battery system back up, and that's
      becoming a serious pain in my aging backside.&nbsp; Until AIOs with Li+
      batteries, lead acid would have enough voltage to get the charge
      controller to come back on, and eventually the customer could get
      the inverter back on too.&nbsp; No special trip out.&nbsp;</p>
    <p>We need an independent circuit that would sense array voltage,
      and wake up the battery, so it could take a charge: a backup
      battery for the offgrid battery.&nbsp; Without that, AIOs and Li+
      batteries are not self healing like Lead Acid.&nbsp; We are going
      backwards fast, but with an amazing amount of new Chinese
      technology driving the jalopy in reverse.&nbsp; (Danger Will Robinson)<br>
    </p>
    <p>Ray Walters<br>
      Remote Solar<br>
    </p>
    <div class="moz-cite-prefix">On 5/12/2025 10:54 AM, Jason Szumlanski
      via RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite" cite="mid:CAE438R_X4H8U=i2oEo7poPPNO4PF5LuB_yLREmJcXrbsQ9w9uQ@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div dir="ltr">
          <div>
            <div class="gmail_default" style="font-family:arial,helvetica,sans-serif">We always
              recommend a transfer switch to bypass the inverter and
              send generator power to the loads. Most clients take us up
              on it. For retrofits, sometimes there can be space
              limitations, however.&nbsp;</div>
            <div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br>
            </div>
            <div class="gmail_default" style="font-family:arial,helvetica,sans-serif">As for the
              function of the AIO, there is no integrated mechanical
              bypass, and since there is an internal relay controlling
              the generator&nbsp;input (or smart load output on that
              breaker), I think the default function is for the relay to
              open when the inverter turns off. AC voltage on the load
              side of the breaker does not close the relay and turn the
              inverter back on automatically.</div>
            <br clear="all">
          </div>
          <div>
            <div dir="ltr" class="gmail_signature">
              <div dir="ltr"><br>
                Jason Szumlanski
                <div><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Principal
                    Solar Designer | Florida Solar Design Group</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">
                  <span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">NABCEP
                    Certified Solar Professional (PVIP)</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">
                  <span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Florida
                    State Certified Solar Contractor CVC56956</span></div>
                <div><font color="#333333" face="Roboto, RobotoDraft, Helvetica, Arial, sans-serif">Florida
                    Certified Electrical Contractor EC13013208</font></div>
              </div>
            </div>
          </div>
          <br>
        </div>
        <br>
        <div class="gmail_quote gmail_quote_container">
          <div dir="ltr" class="gmail_attr">On Mon, May 12, 2025 at
            9:49\u202fAM Dave Angelini Offgrid Solar via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" moz-do-not-send="true" class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>&gt;
            wrote:<br>
          </div>
          <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
            <div style="font-size:12pt;font-family:Verdana,Geneva,sans-serif">
              <div id="m_-2585636671733455182signature">
                <div id="m_-2585636671733455182v1signature" style="color:rgb(51,51,51);background-color:rgb(255,255,255)">All sounds
                  wrong to me. Call Midnite.&nbsp;&nbsp;</div>
                <div style="color:rgb(51,51,51);background-color:rgb(255,255,255)">&nbsp;</div>
                <div style="color:rgb(51,51,51);background-color:rgb(255,255,255)">Typically
                  there is a AC bypass mechanical switch that allows the
                  gen to bypass the inverter and power loads.</div>
                <br>
                <pre>&nbsp;</pre>
                <pre><strong><span style="font-size:small">Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" rel="noopener" target="_blank" moz-do-not-send="true">  </a><a style="color:blue;font-size:11px;font-family:&quot;Lucida Grande&quot;,Verdana,Arial,Helvetica,sans-serif;font-weight:400;background-color:rgb(255,255,255)" href="https://offgridsolar1.com/" rel="noopener noreferrer" target="_blank" moz-do-not-send="true"><span style="font-size:12pt">https://offgridsolar1.com/</span></a><a href="http://members.sti.net/offgridsolar/" rel="noopener" target="_blank" moz-do-not-send="true"> </a>
e-mail  <a href="mailto:offgridsolar@sti.net" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
              </div>
              <p><br>
              </p>
              <p id="m_-2585636671733455182reply-intro">On 2025-05-12
                9:29 am, Jason Szumlanski via RE-wrenches wrote:</p>
              <blockquote type="cite" style="padding:0px 0.4em;border-left:2px solid rgb(16,16,255);margin:0px">
                <div id="m_-2585636671733455182replybody1">
                  <div dir="ltr">
                    <div>
                      <div style="font-family:arial,helvetica,sans-serif">Maybe
                        I'm missing something, but it seems like there
                        is a flaw in the logic for how generator
                        integration works with this product.&nbsp;Unlike some
                        of the other AIOs, you can't put the generator
                        on the Grid input in an off-grid scenario. You
                        have to use the Generator smart load breaker,
                        which isn't a dedicated generator input, but a
                        programmable circuit. This is problematic
                        because it seemingly has a normally open
                        internal relay that closes only when the
                        inverter is ON. At least, that's how it seems to
                        work in my limited experience.</div>
                      <div style="font-family:arial,helvetica,sans-serif">&nbsp;</div>
                      <div style="font-family:arial,helvetica,sans-serif">Why
                        is this a problem? If the battery capacity drops
                        below the low voltage cutoff, the inverter turns
                        off. You have to turn the inverter ON for the
                        generator relay to close so you can charge the
                        battery, but since the battery is too low, the
                        inverter won't turn on. You would have to
                        reprogram the inverter to drop the cutoff
                        voltage/SOC below the current battery state. For
                        people who do not want to use AGS, or if AGS
                        fails to start the generator for any reason,
                        getting the generator&nbsp;to charge the battery
                        manually is no easy&nbsp;task.</div>
                      <div style="font-family:arial,helvetica,sans-serif">&nbsp;</div>
                      <div style="font-family:arial,helvetica,sans-serif">Moreover,
                        turning the generator on manually when the
                        inverter is in an OFF state will not pass power
                        to the loads, and will not turn the&nbsp;inverter ON
                        automatically. You have to get the inverter
                        turned ON somehow so that the generator power
                        can&nbsp;pass through to the loads. And since the
                        startup sequence for this inverter is very
                        quirky, non-intuitive, and unreliable, that
                        makes the problem even worse. I'm not sure if
                        you can even turn the inverter ON when there is
                        generator input and the battery is too low. I
                        don't think you can because the relay is open
                        and the inverter doesn't even see
                        generator&nbsp;voltage when it is in an OFF state.</div>
                    </div>
                    <div>
                      <div style="font-family:arial,helvetica,sans-serif">This
                        seems like a serious oversight and a reason to
                        go with one of the other AIOs on the market. I
                        believe the Sol-Ark 15K and EG4 18kPV will both
                        immediately power loads and start charging when
                        the generator is on, regardless of whether the
                        generator is connected to the Grid or Generator
                        input. Any AC input immediately passes through
                        to the loads. This is because those inverters
                        stay "on" when a low battery condition is met,
                        and they simply stop using the battery to invert
                        power if the battery conditions do not allow it,
                        based on the settings.&nbsp;</div>
                    </div>
                    <div>&nbsp;</div>
                    <div>
                      <div style="font-family:arial,helvetica,sans-serif">The
                        logic of the Midnite AIOs turning "off" when
                        battery&nbsp;cutoff is met and opening the generator
                        relay doesn't make sense to me. Am I wrong about
                        how this works?</div>
                    </div>
                    <div>
                      <div dir="ltr">
                        <div dir="ltr">
                          <div>&nbsp;</div>
                          Jason Szumlanski
                          <div>Principal Solar Designer</div>
                          <div>Florida Solar Design Group</div>
                        </div>
                      </div>
                    </div>
                    <div dir="ltr">
                      <div>&nbsp;</div>
                      <div>
                        <div dir="ltr">&nbsp;</div>
                      </div>
                    </div>
                  </div>
                </div>
                <br>
                <div style="margin:0px;padding:0px;font-family:monospace">_______________________________________________<br>
                  List sponsored by Redwood Alliance<br>
                  <br>
                  Pay optional member dues here: <a href="http://re-wrenches.org" rel="noopener noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
                  <br>
                  List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
                  <br>
                  Change listserver email address &amp; settings:<br>
                  <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noopener noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                  <br>
                  There are two list archives for searching. When one
                  doesn't work, try the other:<br>
                  <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noopener noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                  <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noopener noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                  <br>
                  List rules &amp; etiquette:<br>
                  <a href="http://www.re-wrenches.org/etiquette.htm" rel="noopener noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
                  <br>
                  Check out or update participant bios:<br>
                  <a href="http://www.members.re-wrenches.org" rel="noopener noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
                  <br>
                </div>
              </blockquote>
            </div>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
            <br>
            List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address &amp; settings:<br>
            <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            There are two list archives for searching. When one doesn't
            work, try the other:<br>
            <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
            <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre wrap="" class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  

<span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: http://re-wrenches.org</span><br><span></span><br><span>List Address: RE-wrenches@lists.re-wrenches.org</span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span>https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</span><br><span>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span>http://www.re-wrenches.org/etiquette.htm</span><br><span></span><br><span>Check out or update participant bios:</span><br><span>http://www.members.re-wrenches.org</span><br><span></span><br></div></blockquote></div></body></html>