    <p>Of course not all clients are monetarily capable or willing to
      oversize a Lithium based battery but many can. In my mind this is
      a simpler solution. Its a strategy we're using more to avoid that
      voltage cliff and reduce the likelihood of even nearing the BMS
      shutting down with all of its hassle factor.  This higher battery
      capacity allows a little higher LBCO voltage again to keep the
      system away from the dreaded BMS cutting out.  With the
      availability of Midnite's PowerFlo batteries at a much more
      reasonable price, the added cost for an increase in off-grid
      reliability may not be out of budget for many systems. </p>
    <p>        Gotta love the conversation about parasitic loads also, I
      hope manufacturers are looking at that. <br>
    </p>
    <p>My $.02<br>
    </p>
    <p>Bill<br>
    </p>
    <pre class="moz-signature" cols="72">Feather River Solar Electric
Bill Battagin, owner
4291 Nelson St. (Shipping)
5575 Genesee Rd. (USPS, UPS)
Taylorsville, CA  95983
530-284-7849, 258-1641(cell)
CA. C10 Lic # 874049
Solar Powered since 1982
Home of the Sunny Side Up</pre>
    <div class="moz-cite-prefix">On 2/22/2025 1:06 PM, William Bryce via
      RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAEQmjP4c8bqDeF3zcyTMXU53KWSK4Fn-3=tgjpuRgWTjRVOa=g@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Everyone wants to compare the AIO inverters to the
        older low frequency inverters when it comes to the idle power
        draw. But everyone now wants all the bells and whistles.
        <div><br>
        </div>
        <div>Nothing is free, and if you take an older system then add
          up the charge controllers draw, SCP monitoring system, Gateway
          device, and then add a battery monitor to the mix you will
          find the Idle draw is much higher than what the MFG says for
          the inverter alone.</div>
        <div><br>
        </div>
        <div>Feel free to check the math with a Schneider XW with 3 VH
          MPPT controllers, a gateway, a SCP, and lithium batteries
          running closed loop. Oh, the Schinder does not have any smart
          loads like most AIO do.</div>
        <div><br>
        </div>
        <div>My 2 cents.</div>
        <div><br>
        </div>
        <div>Logan</div>
        <div><br>
        </div>
        <div><br>
        </div>
      </div>
      <br>
      <div class="gmail_quote gmail_quote_container">
        <div dir="ltr" class="gmail_attr">On Sat, Feb 22, 2025 at
          12:03\u202fPM Jason Szumlanski via RE-wrenches &lt;<a
            href="mailto:re-wrenches@lists.re-wrenches.org"
            moz-do-not-send="true" class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>&gt;
          wrote:<br>
        </div>
        <blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div dir="ltr">
            <div dir="ltr">
              <div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif">The
                  voltage cliff is a real issue. Even though LFP
                  batteries can be pretty deeply discharged without
                  damage, for practical purposes we need to set the
                  LBCO on the inverter at a relatively high voltage (or
                  SOC) to avoid the steep part of the cliff altogether,
                  rendering a good part of the capacity essentially
                  useless. In situations where there is a readily
                  available charging source at all times (auto-start
                  generator or grid), there really should be a way to
                  overcome this game of chicken between the battery
                  protect mode and inverter LBCO. In the off-grid world,
                  I don't consider that a bell &amp; whistle, but more
                  of a required feature.</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif"><br>
                </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif">Maybe
                  it's not so much an inverter issue as much as it is a
                  needed battery feature. Imagine if there were a dry
                  contact on a battery BMS that told it to stay on
                  regardless of how it was feeling that day (subject to
                  safety shutdowns, of course). Then you could force the
                  battery to be alive with 48V DC connected when there
                  is generator output voltage present, for example. Of
                  course, there are risks with this simplistic example,
                  like if the inverter/charger is faulted and cannot
                  charge the battery. </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif"><br>
                </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif">I think
                  the right answer is closed-loop communications that
                  can tell a BMS in protect mode to wake up because
                  there is a charging source ready to go. If Midnite
                  could implement this with AIO/Powerflo, it could be a
                  very powerful selling point. On the other hand, maybe
                  it's not that important as long as the inverter
                  reliably reaches LBCO well before the battery goes
                  into protect mode. That answer could be in closed loop
                  communication logic where the BMS sends a warning to
                  the inverter that it is about to shut down, so the
                  inverter can stop inverting on the command of the
                  battery, but keep the battery connected so a charging
                  source will charge it. </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif"><br>
                </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif">In
                  other words, maybe it would be better for the battery
                  to be in command of the inverter's LBCO rather than
                  the inverter's own fuzzy logic.</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif"><br>
                </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif">The
                  parasitic draw issue does need to be addressed. I went
                  through some calculations on some typical systems I
                  have in the field. For example, one system has a
                  120kWh battery with four Sol-Ark 15Ks. I think the
                  inverter manufacturers prefer "idle consumption" to
                  the derogatory parasite comparison, but whatever you
                  call it, let's assume 360W for four inverters. If
                  the inverter LBCO is set at 12% and the protect mode
                  is triggered at 2%, that gives us 33 hours until the
                  battery reaches protect mode in theory. That is a
                  substantial amount of time to get a charging source on
                  the battery. But in practice, I have seen many
                  batteries enter protect mode before a "properly"
                  programmed inverter LBCO engages itself.</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif"><br>
                </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif">That
                  brings up another feature request. How about dropping
                  the idle consumption of paralleled inverters and just
                  keeping the primary inverter at full idle?</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif"><br>
                </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif"><br>
                </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif">Side
                  note: I inherited a site where a Lithionics battery
                  BMS is in control of the 2-wire start for a generator.
                  In theory, this should work, but in practice, the
                  owner often finds the BMS in protect mode with the
                  generator not started. I haven't dug too deeply into
                  this issue yet, but direct BMS control of the
                  generator is another interesting option. But then you
                  would want to build in all of the quiet time, charge
                  percentage/voltage limits, exercise, and other logic
                  that typically an inverter handles. This is an example
                  of how a BMS is in control of the charging source, but
                  it would be better if the BMS was telling the inverter
                  what to do in terms of AGS and LBCO. </div>
              </div>
              <div>
                <div dir="ltr" class="gmail_signature">
                  <div dir="ltr"><br>
                    Jason Szumlanski
                    <div><span
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Principal
                        Solar Designer | Florida Solar Design Group</span><br
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">
                      <span
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">NABCEP
                        Certified Solar Professional (PVIP)</span><br
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">
                      <span
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Florida
                        State Certified Solar Contractor CVC56956</span></div>
                    <div><font color="#333333"
face="Roboto, RobotoDraft, Helvetica, Arial, sans-serif">Florida
                        Certified Electrical Contractor EC13013208</font></div>
                  </div>
                </div>
              </div>
              <br>
            </div>
            <br>
            <div class="gmail_quote">
              <div dir="ltr" class="gmail_attr">On Sat, Feb 22, 2025 at
                11:17\u202fAM Steve Higgins &lt;<a
                  href="mailto:steve@surrette.com" target="_blank"
                  moz-do-not-send="true" class="moz-txt-link-freetext">steve@surrette.com</a>&gt;
                wrote:<br>
              </div>
              <blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
                <div dir="ltr">
                  <div>Hello all... <br>
                    <br>
                    The first issue is that inverter/charger parasitic
                    loads have increased exponentially in the past 20+
                    years. When the LBCO cuts out, the inverter may shut
                    off, but it does not remove itself or any other
                    DC-connected device from the battery.   These
                    devices still draw a parasitic load. In the 1990s,
                    the Trace SW would pull about .3 to .4 amps of
                    current from the battery when connected to it.
                    Today, many manufacturers use cheaper transformers,
                    and the high-frequency inverters draw a much higher
                    current. Some of these all-in-one inverters draw 1-2
                    amps of current from battery banks, just connected
                    and not even turned on. <br>
                    <br>
                    What's important here is that the battery voltage is
                    already very low when you trigger an LBCO shutdown
                    (it's not a disconnect). For a 48-volt system, this
                    is 44 to 47 volts, depending on where you set the
                    LBCO. When a Lithium battery is this low, the
                    voltage dropoff is much higher. With a lead battery,
                    the voltage dropoff is much more linear, but with
                    Lithium chemistry, this voltage dropoff is more like
                    a cliff.    This is why it's important for many of
                    these Lithium systems to set the Battery cutouts a
                    bit higher so people have more time to fix the
                    situation before the BMS shuts down.   Ideally, the
                    customer should be educated not to over-discharge
                    the bank, which would help. Many of these customers
                    want turnkey systems that they don't want to think
                    about but don't want to pay for it or do the work
                    that is required to maintain it.  <br>
                    <br>
                    Now, if the battery had gone into "Protect" mode and
                    the BMS had shut down, the battery is outputting
                    very little votlage... the inverter/charger needs
                    voltage to run.  There used to be a line of
                    inverters in the marine and RV market that would do
                    what we called "Dead Battery Restart".   This meant
                    there was a parallel circuit in the power supply so
                    that when you supplied AC to the input, a secondary
                    power supply bypassed the regular battery power
                    supply and would power up the inverter and allow the
                    charger to run.   Most of the inverter manufacturers
                    got rid of this circuitry because it was not cheap,
                    took up space on the boards, and was just another
                    circuit that could get damaged with generator/shore
                    power surges.   I don't know of an inverter today
                    with this dead battery restarting circuit. </div>
                  <div><br>
                  </div>
                  <div>With this, you need to be very careful. If the
                    customer has cratered the battery voltage and drawn
                    down the voltage so low that they have damaged the
                    cells, jumpstarting the battery can create a
                    charging hazard, and that could cause the cells to
                    swell internally. If that happens, the battery will
                    get warmer and warmer under charge, and eventually,
                    you could have a cell rupture.  This can happen
                    quickly with Li-ion, but with LFP, it's much harder
                    to create this problem. Usually, in LFP, cells will
                    swell a bit, and the current interrupter on the
                    individual cell will open up and drop that string,
                    and you will lose capacity. </div>
                  <div><br>
                  </div>
                  <div>Like everything else, it's a race to the bottom
                    on cost; this affects quality and features...
                    Everyone wants the "Bells &amp; Whistles," but they
                    don't want to pay for it. </div>
                  <div><br>
                  </div>
                  <div>Steve Higgins <br>
                  </div>
                  <br>
                </div>
                <br>
                <div class="gmail_quote">
                  <div dir="ltr" class="gmail_attr">On Sat, Feb 22, 2025
                    at 5:08\u202fAM Jason Szumlanski via RE-wrenches &lt;<a
                      href="mailto:re-wrenches@lists.re-wrenches.org"
                      target="_blank" moz-do-not-send="true"
                      class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>&gt;
                    wrote:<br>
                  </div>
                  <blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
                    <div dir="auto">I have been thinking a lot recently
                      about the reasons off-grid systems can shut down,
                      and working on strategies to prevent these
                      nuisances that require manual intervention.
                      <div dir="auto"><br>
                      </div>
                      <div dir="auto">Ideally, a BMS should never shut
                        down due to low voltage/SOC because a properly
                        programmed inverter should reach it's cut off
                        well before the BMS decides it needs to protect
                        the battery, especially where there is closed
                        loop communication. But let's say that happens,
                        where the BMS does make the DC battery output go
                        to zero.</div>
                      <div dir="auto"><br>
                      </div>
                      <div dir="auto">It seems to me like the inverter
                        should be able to start a generator, and then
                        signal to the BMS that a charging source is
                        available. But I'm not aware of any system that
                        actually does this. The inverter should be able
                        to wake up the battery. I can see this being
                        particularly possible where one manufacturer is
                        writing the code (I'm thinking Midnite
                        AIO/Powerflo).</div>
                      <div dir="auto"><br>
                      </div>
                      <div dir="auto">Of course, the inverter would have
                        to have power in order to do that, so if it's
                        nighttime and there is no PV, the inverter power
                        would need to come from somewhere. I have two
                        thoughts. First, someone could manually start
                        the generator, waking up the inverter, but they
                        would not have to reset the BMS if the inverter
                        told it to wake up. The second way would be for
                        the inverter to somehow close the 2-wire start
                        circuit upon inverter shutdown, restoring power
                        to the inverter automatically. </div>
                      <div dir="auto"><br>
                      </div>
                      <div dir="auto">If those are not options, an
                        external NO relay powered by the inverter output
                        could be added to the 2-wire start circuit,
                        perhaps with a time delay to return to the NO
                        position to allow the generator to remain
                        powered until the inverter does it's thing and
                        starts charging the batteries.</div>
                      <div dir="auto"><br>
                      </div>
                      <div dir="auto">Anyway, my question is whether any
                        inverter/battery combination out there works in
                        a way that the inverter tells the battery there
                        is a charging source available to wake up the
                        BMS and reconnect DC power. And if not, why?</div>
                      <div dir="auto"><br>
                      </div>
                      <div dir="auto">Jason Szumlanski </div>
                      <div dir="auto">Florida Solar Design Group </div>
                    </div>
                    <br>
                    <br>
                  </blockquote>
                </div>
              </blockquote>
            </div>
          </div>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          Pay optional member dues here: <a
            href="http://re-wrenches.org" rel="noreferrer"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
          <br>
          List Address: <a
            href="mailto:RE-wrenches@lists.re-wrenches.org"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address &amp; settings:<br>
          <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          There are two list archives for searching. When one doesn't
          work, try the other:<br>
          <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
          <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
          <br>
          List rules &amp; etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org" rel="noreferrer"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre wrap="" class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  <div id="DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2"><br /><table style="border-top: 1px solid #D3D4DE;"><tr><td style="width: 55px; padding-top: 13px;"><a href="https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient" target="_blank"><img src="https://s-install.avcdn.net/ipm/preview/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif" alt="" width="46" height="29" style="width: 46px; height: 29px;"/></a></td><td style="width: 470px; padding-top: 12px; color: #41424e; font-size: 13px; font-family: Arial, Helvetica, sans-serif; line-height: 18px;">Virus-free.<a href="https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient" target="_blank" style="color: #4453ea;">www.avast.com</a></td></tr></table><a href="#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2" width="1" height="1"> </a></div></body>
</html>