<!DOCTYPE html>
<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  </head>
  <body>
    <p>That's strike one, I get two more.<br>
    </p>
    <div class="moz-cite-prefix">On 1/22/2025 10:31 PM, John
      Blittersdorf via RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CALp43SS9em1VTG4H5o+csoEzn+H06EBwnj6+fbomQ=zFfX-Uxw@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Christopher, 
        <div>Update on the Transformer Humming.  Installed a new PSX-240
          from Kirk and it is LOUDER than the T-240 that I took out. 
          <div>I have a call into the well driller to see if they have a
            record of the pump size or other details. When connected </div>
          <div>directly to the grid via transfer switch, still loud
            noise... same with battery only.  I did not check the 120VAC
            30 amp break</div>
          <div>in the backed up loads sub panel. All other wiring was
            redone as I switched the pump directly to the grid until I
            received the</div>
          <div>new transformer and back to the inverter again. so all
            the connections were redone except the 120 breaker. </div>
          <div><br>
          </div>
          <div>John</div>
          <div><br>
          </div>
        </div>
      </div>
      <br>
      <div class="gmail_quote gmail_quote_container">
        <div dir="ltr" class="gmail_attr">On Wed, Jan 22, 2025 at
          10:30\u202fAM Howie Michaelson via RE-wrenches &lt;<a
            href="mailto:re-wrenches@lists.re-wrenches.org"
            moz-do-not-send="true" class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>&gt;
          wrote:<br>
        </div>
        <blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div dir="auto">
            <div>John, 
              <div dir="auto">If you need a T240 (internal or external),
                I have a few used ones (and maybe a new one) in
                storage. </div>
              <div dir="auto">Howie</div>
              <br>
              <br>
              <div class="gmail_quote">
                <div dir="ltr" class="gmail_attr">On Wed, Jan 22, 2025,
                  10:14\u202fAM Christopher Warfel via RE-wrenches &lt;<a
                    href="mailto:re-wrenches@lists.re-wrenches.org"
                    target="_blank" moz-do-not-send="true"
                    class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>&gt;
                  wrote:<br>
                </div>
                <blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">I
                  could be a loose electrical or mechanical connection.
                  It's been <br>
                  installed for a while and connections could have
                  loosened up from <br>
                  expansion and contraction.<br>
                  <br>
                  On 1/18/2025 9:06 AM, John Blittersdorf via
                  RE-wrenches wrote:<br>
                  &gt; Hi Wrenches,<br>
                  &gt;   I have a customer with an SW4024 installed in
                  2003 with the Trace <br>
                  &gt; T220 transformer for<br>
                  &gt; her well pump.  Recently it has started making a
                  lot of noise when the <br>
                  &gt; well pump comes on.<br>
                  &gt; I checked the current on the well pump and it
                  seems to be in the <br>
                  &gt; normal range.  I have never had a transformer
                  failure. Could this be a <br>
                  &gt; failing transformer?<br>
                  &gt;<br>
                  &gt; Also, I have not been able to source a new one
                  (Outback T240).  Are <br>
                  &gt; there other brands<br>
                  &gt; some of you may have used for a step up
                  transformer?<br>
                  &gt;<br>
                  &gt; John Blittersdorf<br>
                  &gt;<br>
                  &gt; _______________________________________________<br>
                  &gt; List sponsored by Redwood Alliance<br>
                  &gt;<br>
                  &gt; Pay optional member dues here: <a
                    href="http://re-wrenches.org"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
                  &gt;<br>
                  &gt; List Address: <a
                    href="mailto:RE-wrenches@lists.re-wrenches.org"
                    rel="noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
                  &gt;<br>
                  &gt; Change listserver email address &amp; settings:<br>
                  &gt; <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                  &gt;<br>
                  &gt; There are two list archives for searching. When
                  one doesn't work, try the other:<br>
                  &gt; <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                  &gt; <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                  &gt;<br>
                  &gt; List rules &amp; etiquette:<br>
                  &gt; <a
                    href="http://www.re-wrenches.org/etiquette.htm"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
                  &gt;<br>
                  &gt; Check out or update participant bios:<br>
                  &gt; <a href="http://www.members.re-wrenches.org"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
                  &gt;<br>
                  -- <br>
                  Christopher Warfel, PE<br>
                  ENTECH Engineering, Inc.<br>
                  PO Box 871, Block Island, RI 02807<br>
                  (401) 447-5773<br>
                  <br>
                  _______________________________________________<br>
                  List sponsored by Redwood Alliance<br>
                  <br>
                  Pay optional member dues here: <a
                    href="http://re-wrenches.org"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
                  <br>
                  List Address: <a
                    href="mailto:RE-wrenches@lists.re-wrenches.org"
                    rel="noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
                  <br>
                  Change listserver email address &amp; settings:<br>
                  <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                  <br>
                  There are two list archives for searching. When one
                  doesn't work, try the other:<br>
                  <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                  <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                  <br>
                  List rules &amp; etiquette:<br>
                  <a href="http://www.re-wrenches.org/etiquette.htm"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
                  <br>
                  Check out or update participant bios:<br>
                  <a href="http://www.members.re-wrenches.org"
                    rel="noreferrer noreferrer" target="_blank"
                    moz-do-not-send="true" class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
                  <br>
                </blockquote>
              </div>
            </div>
          </div>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          Pay optional member dues here: <a
            href="http://re-wrenches.org" rel="noreferrer"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
          <br>
          List Address: <a
            href="mailto:RE-wrenches@lists.re-wrenches.org"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address &amp; settings:<br>
          <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          There are two list archives for searching. When one doesn't
          work, try the other:<br>
          <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
          <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
          <br>
          List rules &amp; etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org" rel="noreferrer"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre wrap="" class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401) 447-5773</pre>
  </body>
</html>