<div dir="auto">John:</div><div dir="auto"><br></div><div dir="auto">Sorry, my previous post went out prematurely. </div><div dir="auto"><br></div><div dir="auto">The question is: how bad is the noise? I\u2019ve heard buzzing to some degree or another from most transformers. Is the noise level the same without any covers in place?</div><div dir="auto"><br></div><div dir="auto">Pumps lose efficiency over time. Could the pump be drawing more power? If there has been regularly service pump efficiency should have been logged. <br clear="all"><br clear="all"><div dir="auto"><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><br>William Miller<br>Miller Solar.com<br>805-438-5600<br><a href="http://www.millersolar.com">www.millersolar.com</a><br></div></div></div><div><br></div><div><br><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Thu, Jan 23, 2025 at 7:44\u202fPM John Blittersdorf via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr">The only thing I could find in the whole system that was not up to snuff was incomplete separation of neutrals and grounds in the sub-panel. In other words more than one ground to neutral bond. But the fact remains that this<div>system worked flawlessly for 26 years! I also removed the ground wire from the transformer but still no difference. What am I missing?</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Thu, Jan 23, 2025 at 10:35\u202fPM John Blittersdorf <<a href="mailto:john.blittersdorf@gmail.com" target="_blank">john.blittersdorf@gmail.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="ltr">Steve, I took my scope meter today and checked wave forms at all points. All were clean sine waves. I checked the breaker connections and all connections back to the inverter and all were tight. <div>Voltage drop when pump kicked on was small and only about 1 volt when running. Amp were 12 on both legs.</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Thu, Jan 23, 2025 at 9:48\u202fAM Jay via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="auto"><div dir="ltr"></div><div dir="ltr">Are the amps leg the same?</div><div dir="ltr">Jay</div><div dir="ltr"><br><blockquote type="cite">On Jan 22, 2025, at 9:29\u202fPM, Steve Higgins via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff<div dir="ltr"><div>How do their clocks run? Is the Xfmer quiet down when the generator runs? <br><br>If you have an O-scope, check the output waveform off the inverter. My guess is that the output waveform will be deformed, causing extra noise for the Xfmer. You might be able to see this on the frequency as well. It should be solid at 60Hz, but if it's drifting or way off the high side, FETS have probably failed. <br><br>If you pull the top cover off the inverter the and you look at the FET board, it'll be the fets closest to the Fan on the AC board. <br><br><br><div><image.png></div></div><div><br></div><div>Steve Higgins<br><br></div><div><br></div><br></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Jan 22, 2025 at 7:32\u202fPM John Blittersdorf via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="ltr">Christopher, <div>Update on the Transformer Humming. Installed a new PSX-240 from Kirk and it is LOUDER than the T-240 that I took out. <div>I have a call into the well driller to see if they have a record of the pump size or other details. When connected </div><div>directly to the grid via transfer switch, still loud noise... same with battery only. I did not check the 120VAC 30 amp break</div><div>in the backed up loads sub panel. All other wiring was redone as I switched the pump directly to the grid until I received the</div><div>new transformer and back to the inverter again. so all the connections were redone except the 120 breaker. </div><div><br></div><div>John</div><div><br></div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Jan 22, 2025 at 10:30\u202fAM Howie Michaelson via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="auto"><div>John, <div dir="auto">If you need a T240 (internal or external), I have a few used ones (and maybe a new one) in storage. </div><div dir="auto">Howie</div><br><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Jan 22, 2025, 10:14\u202fAM Christopher Warfel via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">I could be a loose electrical or mechanical connection. It's been <br>
installed for a while and connections could have loosened up from <br>
expansion and contraction.<br>
<br>
On 1/18/2025 9:06 AM, John Blittersdorf via RE-wrenches wrote:<br>
> Hi Wrenches,<br>
> I have a customer with an SW4024 installed in 2003 with the Trace <br>
> T220 transformer for<br>
> her well pump. Recently it has started making a lot of noise when the <br>
> well pump comes on.<br>
> I checked the current on the well pump and it seems to be in the <br>
> normal range. I have never had a transformer failure. Could this be a <br>
> failing transformer?<br>
><br>
> Also, I have not been able to source a new one (Outback T240). Are <br>
> there other brands<br>
> some of you may have used for a step up transformer?<br>
><br>
> John Blittersdorf<br>
><br>
> _______________________________________________<br>
> List sponsored by Redwood Alliance<br>
><br>
> Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
><br>
> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
><br>
> Change listserver email address & settings:<br>
> <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
><br>
> There are two list archives for searching. When one doesn't work, try the other:<br>
> <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
> <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
><br>
> List rules & etiquette:<br>
> <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
><br>
> Check out or update participant bios:<br>
> <a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
><br>
-- <br>
Christopher Warfel, PE<br>
ENTECH Engineering, Inc.<br>
PO Box 871, Block Island, RI 02807<br>
(401) 447-5773<br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div></div></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
<span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a></span><br><span></span><br><span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a></span><br><span></span><br><span>Change listserver email address & settings:</span><br><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a></span><br><span><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List rules & etiquette:</span><br><span><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a></span><br><span></span><br><span>Check out or update participant bios:</span><br><span><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a></span><br><span></span><br></div></blockquote></div>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
</blockquote></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div></div>