<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div dir="ltr"></div><div dir="ltr">You guys are making my point.&nbsp;</div><div dir="ltr">Melting the cases is not a fire. And every melted agm case is due to incorrect charging mechanisms.&nbsp;</div><div dir="ltr"><br></div><div dir="ltr">But there have been some cases on this site of catastrophic lithium failures.&nbsp;</div><div dir="ltr"><br></div><div dir="ltr">I am starting to see people asking about fires and lithium.&nbsp;</div><div dir="ltr"><br></div><div dir="ltr">These batteries are in the house. Not my design and not an easy fix to move them.&nbsp;</div><div dir="ltr"><br></div><div dir="ltr">Thanks again</div><div dir="ltr"><br></div><div dir="ltr">Jay&nbsp;</div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br><blockquote type="cite">On Jan 12, 2025, at 10:52\u202fAM, Tyrone Houck via RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt; wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff<div dir="auto"><div>I had the exact same thing happen(even down to the crowbar) with the only set of full river 400 6's I've ever installed. I personally lean away from agm though we've had pretty good luck with the Outback and Northstar PLR platform over the&nbsp;year..</div><div><br></div><div data-smartmail="gmail_signature"><br>&nbsp;&nbsp;&nbsp; </div></div><br><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Sun, Jan 12, 2025, 9:39\u202fAM Ray Walters via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><u></u>

  
    
  
  <div>
    <p>The only thermal runaway event I've ever seen, was with AGM in an
      over insulated battery box.&nbsp; Got so hot that the cases fused to
      each other, and we had to pry the batteries apart with a crow
      bar.&nbsp; She wants ZERO risk of fire?&nbsp; She needs to live in a
      concrete bunker with no electricity at all.&nbsp; Every electrical
      connection, every outlet, every appliance has a risk of fire.&nbsp;
      Period.</p>
    <p>Ray Walters<br>
      Remote Solar<br>
    </p>
    <div>On 1/12/2025 9:39 AM, Tyrone Houck via
      RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="auto">
        <div>I hate to be the one to say it but LFP has arguably less
          fire risk than agm. A short circuit in an agm could be
          disastrous and AGM is not necessarily any safer or less prone
          to thermal runaway events than modern LFP. I'd recommend a
          cobalt free LFP like homegrid, simpliphi, or midnite if it
          were me..</div>
        <div><br>
        </div>
        <div data-smartmail="gmail_signature"><br>
          &nbsp;&nbsp;&nbsp; </div>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Sat, Jan 11, 2025, 3:38\u202fPM
          jay via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">re-wrenches@lists.re-wrenches.org</a>&gt;
          wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
          <div style="line-break:after-white-space">I was going to try
            and steer her towards lithium but she wants zero, absolutely
            zero chance of fire, so no lithium.
            <div><br>
            </div>
            <div>great batteries though</div>
            <div><br>
            </div>
            <div>jay<br>
              <div><br>
              </div>
              <div><br id="m_-6779490390839839746m_5650226487739232990lineBreakAtBeginningOfMessage">
                <div><br>
                  <blockquote type="cite">
                    <div>On Jan 11, 2025, at 4:35\u202fPM, MD Electric &amp;
                      Solar via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;
                      wrote:</div>
                    <br>
                    <div>
                      <div dir="ltr">
                        <div class="gmail_default" style="font-size:small">30KWH of LFP from
                          discover energy, fits in one enclosure, around
                          $14000.00</div>
                        <div class="gmail_default" style="font-size:small">Enclosure is
                          indoor/outdoor rated.</div>
                        <div class="gmail_default" style="font-size:small"><br>
                        </div>
                        <div class="gmail_default" style="font-size:small"><a href="https://discoverenergysys.com/products/lithium-batteries/aes-rackmount" rel="noreferrer noreferrer" target="_blank">https://discoverenergysys.com/products/lithium-batteries/aes-rackmount</a></div>
                        <div class="gmail_default" style="font-size:small"><a href="https://discoverenergysys.com/products/accessories/slimline-enclosure" rel="noreferrer noreferrer" target="_blank">https://discoverenergysys.com/products/accessories/slimline-enclosure</a></div>
                      </div>
                      <br>
                      <div class="gmail_quote">
                        <div dir="ltr" class="gmail_attr">On Sat, Jan
                          11, 2025 at 3:31\u202fPM jay via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;
                          wrote:<br>
                        </div>
                        <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">HI
                          Willam <br>
                          <br>
                          Thanks for the input.<br>
                          I didn\u2019t know that trojan was sold, and from
                          what you say, yeah scratch them off.&nbsp; <br>
                          <br>
                          It\u2019s currently at 30kwh.&nbsp; And thats probably a
                          good size.&nbsp; <br>
                          As always, cost and time is a factor.&nbsp; <br>
                          <br>
                          I\u2019ll check the others out.<br>
                          <br>
                          jay<br>
                          <br>
                          <br>
                          <br>
                          <br>
                          <br>
                          &gt; On Jan 11, 2025, at 4:17\u202fPM, William
                          Miller &lt;<a href="mailto:william@millersolar.com" rel="noreferrer noreferrer" target="_blank">william@millersolar.com</a>&gt;
                          wrote:<br>
                          &gt; <br>
                          &gt; Jay:<br>
                          &gt; <br>
                          &gt; What AH or Kwh level are you looking for?<br>
                          &gt; <br>
                          &gt; Trojan was acquired by another company a
                          few years ago and quality had gone<br>
                          &gt; downhill.<br>
                          &gt; <br>
                          &gt; Rolls is very sensitive to high
                          temperatures.&nbsp; They will deny a warranty<br>
                          &gt; claim if all of your parameters are not
                          exactly right.<br>
                          &gt; <br>
                          &gt; For larger AH systems:<br>
                          &gt; <br>
                          &gt; I like the Full River DC-400-2.&nbsp; You
                          might be able to do a one string<br>
                          &gt; installation.<br>
                          &gt; <br>
                          &gt; Unigy II is a great system.&nbsp; Very
                          robust.&nbsp; Hard to deliver but I can offer<br>
                          &gt; tips.&nbsp; Lots of AH size options.<br>
                          &gt; <br>
                          &gt; William<br>
                          &gt; <br>
                          &gt; Miller Solar<br>
                          &gt; 17395 Oak Road, Atascadero, CA 93422<br>
                          &gt; 805-438-5600<br>
                          &gt; <a href="http://www.millersolar.com/" rel="noreferrer noreferrer noreferrer" target="_blank">www.millersolar.com</a><br>
                          &gt; CA Lic. 773985<br>
                          &gt; <br>
                          &gt; <br>
                          &gt; <br>
                          &gt; -----Original Message-----<br>
                          &gt; From: RE-wrenches [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>]
                          On<br>
                          &gt; Behalf Of jay via RE-wrenches<br>
                          &gt; Sent: Saturday, January 11, 2025 2:48 PM<br>
                          &gt; To: RE-wrenches<br>
                          &gt; Cc: jay<br>
                          &gt; Subject: [RE-wrenches] AGM battery
                          recommendations<br>
                          &gt; <br>
                          &gt; Hi All<br>
                          &gt; <br>
                          &gt; I have a customer what is set on AGM.<br>
                          &gt; <br>
                          &gt; It been so long since I\u2019ve bought any,
                          wondering if there are any<br>
                          &gt; recommendations?<br>
                          &gt; <br>
                          &gt; The ones I\u2019m looking at:<br>
                          &gt; <br>
                          &gt; Rolls&nbsp; S6-460AGM-RE<br>
                          &gt; <br>
                          &gt; Full river DC-400-6<br>
                          &gt; <br>
                          &gt; Trojan SAES 06 375 6V<br>
                          &gt; <br>
                          &gt; sun Xtender&nbsp; brand.<br>
                          &gt; <br>
                          &gt; What\u2019s interesting is the trojan has
                          about 3000 cycles vs the others at<br>
                          &gt; around 1250 cycles to 50%.<br>
                          &gt; Im wondering if that is a marketing idea
                          or if its real.<br>
                          &gt; <br>
                          &gt; thanks in advance<br>
                          &gt; <br>
                          &gt; jay<br>
                          &gt;
                          _______________________________________________<br>
                          &gt; List sponsored by Redwood Alliance<br>
                          &gt; <br>
                          &gt; Pay optional member dues here: <a href="http://re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
                          &gt; <br>
                          &gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                          &gt; <br>
                          &gt; Change listserver email address &amp;
                          settings:<br>
                          &gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                          &gt; <br>
                          &gt; There are two list archives for
                          searching. When one doesn't work, try the<br>
                          &gt; other:<br>
                          &gt; <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                          &gt; <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                          &gt; <br>
                          &gt; List rules &amp; etiquette:<br>
                          &gt; <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
                          &gt; <br>
                          &gt; Check out or update participant bios:<br>
                          &gt; <a href="http://www.members.re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
                          <br>
_______________________________________________<br>
                          List sponsored by Redwood Alliance<br>
                          <br>
                          Pay optional member dues here: <a href="http://re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
                          <br>
                          List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                          <br>
                          Change listserver email address &amp;
                          settings:<br>
                          <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                          <br>
                          There are two list archives for searching.
                          When one doesn't work, try the other:<br>
                          <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                          <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                          <br>
                          List rules &amp; etiquette:<br>
                          <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
                          <br>
                          Check out or update participant bios:<br>
                          <a href="http://www.members.re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
                          <br>
                        </blockquote>
                      </div>
                      <div><br clear="all">
                      </div>
                      <div><br>
                      </div>
                      <span class="gmail_signature_prefix">-- </span><br>
                      <div dir="ltr" class="gmail_signature">
                        <div dir="ltr">
                          <div>
                            <div dir="ltr">
                              <div>
                                <div dir="ltr">
                                  <div>
                                    <div dir="ltr">
                                      <div dir="ltr">
                                        <div dir="ltr">
                                          <div dir="ltr">
                                            <div dir="ltr">
                                              <div><span style="font-size:12.8px">Michael D Nelson</span><br>
                                              </div>
                                              <div>
                                                <div><span style="background-color:rgb(255,255,255)">MD Electric &amp; Solar Inc.</span></div>
                                                <div><span style="background-color:rgb(255,255,255)">Office: 707-412-3181</span></div>
                                                <div><span style="background-color:rgb(255,255,255)">Cell: 707-684-0064</span></div>
                                              </div>
                                              <div><a href="http://www.mdelectricsolar.com/" style="font-size:12.8px" rel="noreferrer noreferrer" target="_blank">www.mdelectricsolar.com</a><span style="background-color:rgb(255,255,255)"><br>
                                                </span></div>
                                              <div><span style="background-color:rgb(255,255,255)"><a href="http://www.facebook.com/mdelectricandsolar" rel="noreferrer noreferrer" target="_blank">www.facebook.com/mdelectricandsolar</a></span></div>
                                              <div><br>
                                              </div>
                                              <div><br>
                                              </div>
                                            </div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                      _______________________________________________<br>
                      List sponsored by Redwood Alliance<br>
                      <br>
                      Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
                      <br>
                      List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                      <br>
                      Change listserver email address &amp; settings:<br>
                      <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      There are two list archives for searching. When
                      one doesn't work, try the other:<br>
                      <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                      <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      List rules &amp; etiquette:<br>
                      <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
                      <br>
                      Check out or update participant bios:<br>
                      <a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
                      <br>
                    </div>
                  </blockquote>
                </div>
                <br>
              </div>
            </div>
          </div>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
          <br>
          List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address &amp; settings:<br>
          <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          There are two list archives for searching. When one doesn't
          work, try the other:<br>
          <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
          <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
          <br>
          List rules &amp; etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <fieldset></fieldset>
      <pre>_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank" rel="noreferrer">http://re-wrenches.org</a>

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
<span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: http://re-wrenches.org</span><br><span></span><br><span>List Address: RE-wrenches@lists.re-wrenches.org</span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span>https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</span><br><span>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span>http://www.re-wrenches.org/etiquette.htm</span><br><span></span><br><span>Check out or update participant bios:</span><br><span>http://www.members.re-wrenches.org</span><br><span></span><br></div></blockquote></body></html>