<div dir="ltr"><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">We have been talking a lot recently about all-in-ones. I just had a massive fail during Hurricane Milton with a quad Sol-Ark 15K off-grid system that deserves some discussion about whether AIO is a good idea if it can&#39;t build in some resilience to errors. I&#39;m not sure if the new Midnite unit is better in this respect, but this is what happened to the Sol-Ark system...</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Four inverters, each with 4 strings of PV paralleled to 2 MPPT per inverter. One of the slave units developed some sort of PV DC fault during the storm. This caused the slave inverter to shut down and throw an error, which in turn caused a parallel fault across all four inverters. Power output ceases at that point. Apparently the system keeps resetting because I have a cell modem that uploads data to Sol-Ark, but that cell modem is powered by the inverter outputs, so it must be getting power at least intermittently. The rest of the loads are basically flatlined according to the Sol-Ark data. It&#39;s mostly air conditioners, so they probably can&#39;t turn on fast enough before the PV fault causes another shutdown.</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">So, in essence, one of 16 strings of PV develops a fault, and that causes all four inverters to malfunction? What is the point of redundancy if a fault of one results in a fault of all?! If there is a true PV input fault, shouldn&#39;t that just shut down that MPPT, or perhaps all of the PV DC input to that inverter? And why can&#39;t this inverter continue to invert power from the batteries and charge from a generator when there is a DC input fault that could be programmatically isolated and ignored?</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">This is a bad design in my opinion, and something I hadn&#39;t considered. If the faulted inverter can&#39;t function with a DC input fault, it should just take itself out of the game. (This is 120/240 split phase, BTW). Is this how all AIO inverters work? One inverter fault on the DC side kills all paralleled units&#39; AC output? Not good.</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">This is a completely off-grid system on a remote island with no vehicle access, so it&#39;s not exactly easy to do a &quot;truck roll&quot; on this one, especially post-hurricane. To make matters worse, the generator was running at the time of the fault, as it was being signaled to run because the battery had reached the assigned charge voltage. The fault also killed the 2-wire start signal from the master, so the system also stopped passing through generator power to the loads. The house is dark.</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Jason Szumlanski</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Florida Solar Design Group</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><b></b></div></div></div></div></div></div></div></div></div>