<div dir="ltr"><div class="gmail_default" style="font-size:small">Jason,</div><div class="gmail_default" style="font-size:small">There are 2 different methods typically utilized, one specified by Tesla for any UL2703 module/racking combination which is as you say and limits the MCI to 165V, which is the tested disconnect limit of the MCI-2.</div><div class="gmail_default" style="font-size:small"><br></div><div class="gmail_default" style="font-size:small">If you use the MCI-1 then you have an additional option of using the 3741 PVHCS listing of another manufacturer such as Ironridge. Since the MCI-1 has a 600V disconnect limit, you can safely use just (2) MCI-1 on a string, one at the beginning and end, as long as the array is physically contiguous with no gaps larger than 2&#39; between adjacent modules.</div><div class="gmail_default" style="font-size:small"><br></div><div class="gmail_default" style="font-size:small">The GW2/3 is irrelevant to the MCI question, as the Powerwall 3 inverter sends its keep alive signal with PLC over the DC wiring.</div><div class="gmail_default" style="font-size:small"><br></div><div class="gmail_default" style="font-size:small">I think you could make a temporary off grid system work well enough if you simply commissioned it with grid voltage, then removed the grid, but kept the islanding contactor intact. Either GW3/GW2 or the Backup Switch in a meter socket enclosure could serve as this contactor, to keep the PW3 happy and in communication with &quot;the grid.&quot;</div><div class="gmail_default" style="font-size:small"><br></div><div class="gmail_default" style="font-size:small">On a separate note, the details and testing of a 3741 PVHCS listing probably means that module level rapid shutdown never added much first responders safety compared with rooftop shutdown at within 1&#39; of the array group. I have seen others on this list agree to as much and the test labs basically validate this in my eyes.</div><div class="gmail_default" style="font-size:small"><br></div><div class="gmail_default" style="font-size:small">From: Jason Szumlanski &lt;<a href="mailto:jason@floridasolardesigngroup.com" target="_blank">jason@floridasolardesigngroup.com</a>&gt;<br>To: &quot;RE-wrenches&quot; &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;<br>Cc: Vincent Jolissaint &lt;<a href="mailto:vincentj@cobaltpower.com" target="_blank">vincentj@cobaltpower.com</a>&gt;<br>Subject: Re: [RE-wrenches] Powerwall 3 (contd)<br>Message-ID:<br>        &lt;<a href="mailto:70929283-0f8f-f810-c3c7-9716cfd0e77b@floridasolardesigngroup.com" target="_blank">70929283-0f8f-f810-c3c7-9716cfd0e77b@floridasolardesigngroup.com</a>&gt;<br>Content-Type: text/plain; charset=&quot;utf-8&quot;<br><br>Thanks,?Vincent. This is the information I needed.<br><br><br>I did read that at least 1 MCI is needed even if you do not require RSD. The MCI<br>instructions are a bit confusing. I know for RSD you need one at the start of a<br>string and at least one every three modules, but it&#39;s unclear if you need the<br>MCI-1 or MCI-2 when using the GW3.<br><br><br>The reason I was thinking about an off-grid application is I want to use one PW3<br>in a mobile application (for myself). I was thinking about tricking it into<br>working, but I think it would?take a?PW3, GW2 or GW3, and an AC source<br>to?commission it initially.<br><br>Jason Szumlanski<br>Principal Solar Designer | Florida Solar Design Group<br>NABCEP Certified Solar Professional (PVIP)<br>Florida State Certified Solar Contractor CVC56956<br>Florida Certified Electrical Contractor EC13013208<br><br><br>On Wed, Sep 11, 2024 at 4:18?PM Vincent Jolissaint via RE-wrenches<br>&lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br><br>&gt; (sorry sent the previous reply before it was complete)<br>&gt; Hi Jason,<br>&gt;<br>&gt;<br>&gt; Currently Tesla doesn&#39;t allow any totally off-grid installations with PW3 or<br>&gt; PW3, they used to support this through the Gateway but no longer do.<br>&gt;<br>&gt;<br>&gt; In addition, the Powerwall 3 will require at least a single MCI per string to<br>&gt; pass the self?test function. This also limits the total string loop length<br>&gt; from MPPT+ to MPPT-.<br>&gt;<br>&gt;<br>&gt; Powerwall 3 does contain the site controller, but it will require some<br>&gt; islanding contactor to function properly.<br>&gt;<br>&gt;<br>&gt;<br>&gt; Vince Jolissaint?|?Director of CAD Services<br>&gt;<br>&gt; 2557 Wyandotte Street | Mountain View, CA? 94043<br>&gt; Office:?650.938.9574 | Email:?<a href="mailto:vincentj@cobaltpower.com" target="_blank">vincentj@cobaltpower.com</a><br>&gt; [<a href="mailto:vincentj@cobaltpower.com" target="_blank">vincentj@cobaltpower.com</a>]<br>&gt;<br>&gt;<br>&gt;<br>&gt; &gt;From: Jason Szumlanski &lt;<a href="mailto:jason@floridasolardesigngroup.com" target="_blank">jason@floridasolardesigngroup.com</a><br>&gt; [<a href="mailto:jason@floridasolardesigngroup.com" target="_blank">jason@floridasolardesigngroup.com</a>]&gt;<br>&gt; &gt;To: RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a><br>&gt; [<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>]&gt;<br>&gt; &gt;Subject: [RE-wrenches] Powerwall 3<br>&gt; &gt;Message-ID:<br>&gt; ?&gt;? ? ? ?&lt;CAE438R9LWo_VNuTTkOzVbv62LST3_Bf4-x7VfLm=-<a href="mailto:Rkk6k%2BwJw@mail.gmail.com" target="_blank">Rkk6k+wJw@mail.gmail.com</a><br>&gt; [<a href="mailto:Rkk6k%252BwJw@mail.gmail.com" target="_blank">Rkk6k%2BwJw@mail.gmail.com</a>]&gt;<br>&gt; &gt;Content-Type: text/plain; charset=&quot;utf-8&quot;<br>&gt;<br>&gt; &gt;Certified Powerwall installers,<br>&gt;<br>&gt; &gt;Can the PW3 be commissioned for for a completely off-grid system with DC<br>&gt; &gt;coupled solar panels with no MCIs. If so, do you need a Gateway 2/3, or can<br>&gt; &gt;it operate autonomously in this scenario without a Gateway?<br>&gt; &gt;<br>&gt; &gt;Jason Szumlanski<br>&gt; &gt;Florida Solar Design Group<br></div><div class="gmail_default" style="font-size:small"><br></div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><p class="MsoNormal"><b><span style="font-size:10pt;font-family:Arial,sans-serif"><font color="#0000ff">Vince Jolissaint</font></span><span style="color:rgb(77,45,211);font-size:10pt;font-family:Arial,sans-serif"> </span><span style="font-size:10pt;font-family:Arial,sans-serif"><font color="#000000">|</font></span></b><font color="#000000"><span style="font-size:10pt;font-family:Arial,sans-serif"> </span><b><span style="font-size:10pt;font-family:Arial,sans-serif">Director of CAD Services</span></b></font><font color="#222222"><u></u><u></u></font></p><p class="MsoNormal"><font color="#444444"><span style="font-size:10pt;font-family:Arial,sans-serif">2557 Wyandotte Street | Mountain View, CA  94043</span><span style="font-family:Arial,sans-serif"><br></span><span style="font-size:10pt;font-family:Arial,sans-serif">Office: 650.938.9574 | Email:</span><span style="font-size:10pt;font-family:Arial,sans-serif"> </span><span style="font-size:10pt;font-family:Arial,sans-serif"><a href="mailto:vincentj@cobaltpower.com" target="_blank">vincentj@cobaltpower.com</a></span></font></p><p class="MsoNormal" style="color:rgb(34,34,34)"><br></p><p class="MsoNormal" style="color:rgb(34,34,34)"><img src="https://www.cobaltpower.com/images/logos/Transparent-Logo.png" width="200" height="55"><br></p></div></div></div></div>