<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto">Dana<div><br></div><div>I have always wired the PV negative all the way to the charge controller. That way, the battery negative of the charge controller that happens to go to a shunt has a proper representation of the current flow. &nbsp;I guess you could put that PV negative at the same side of the shunt as the battery negative since internally the negatives are tied together on the charge controller.</div><div><br></div><div>Did the charge controller come</div><div>AFCI? If so, you likely have to bring both PV cables through the current sense of the AFCI.&nbsp;</div><div><br></div><div>Also check to see if you have global charge control coordination turned on, if so, turn it off &nbsp;and also check restart mode to set to two which means restart after 90 minutes no matter what.&nbsp;</div><div><br></div><div><br id="lineBreakAtBeginningOfSignature"><div dir="ltr">Thank you,<div><br></div><div>Maverick</div><div><div id="AppleMailSignature" style="caret-color: rgb(0, 0, 0); color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px;"><div class="ApplePlainTextBody"><br></div><div class="ApplePlainTextBody">Maverick Brown<br>Off-Grid Solar Commander since 2006<br>Maverick Solar Enterprises, Inc.<br>&nbsp;\u2022 Solar Commander Remote Power<br>&nbsp;\u2022 SunFlow Systems Cathodic&nbsp;Protection&nbsp;<br>maverick@mavericksolar.com<br>512-460-9825</div><div><br></div></div></div><div><br></div></div><div dir="ltr"><br><blockquote type="cite">On Sep 7, 2024, at 5:50\u202fPM, Dana Orzel via RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt; wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff<span>OK, you wise guys.</span><br><span>I am upgrading my home off grid system from two FM 80s to two FM 100s.</span><br><span>The FM 80s were able to share the negative wire so you didn\u2019t have to pull a second negative wire.</span><br><span>I wired the FM 100 typical of how my FM 80s were wired with a number four battery negative assuming and yes, I know what happens when I assume, that the PV negative on the battery negative are common and I could just pull one number four since going through those double 1\u201d - 90° is a bitch. Currently I have two # fours for output to battery, the number eight ground and 1 # six PV input.</span><br><span>I got this all together and it\u2019s charging just fine but once the battery got full charge controllers continued to produce full output. The battery dropped to a float and I had 2800W on each charge controller continuing to be produced at which was turning into heat so the FM 100s were getting very warm. The fans had not turned on, but the heat sinks were definitely very very warm to the touch. The battery voltage is fine.</span><br><span>I Read the manual it doesn\u2019t talk about being able to use one negative so I am assuming that my problem is that the PV needs a negative and they do not share the negative.</span><br><span>Has anybody else seen this or done the same wiring maneuver.</span><br><span> thanks in advance</span><br><span></span><br><span>Dana Orzel - dana@solarwork.com - 208.721.7003</span><br><span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: http://re-wrenches.org</span><br><span></span><br><span>List Address: RE-wrenches@lists.re-wrenches.org</span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span>https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</span><br><span>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span>http://www.re-wrenches.org/etiquette.htm</span><br><span></span><br><span>Check out or update participant bios:</span><br><span>http://www.members.re-wrenches.org</span><br><span></span><br></div></blockquote></div></body></html>