    <p>I have both controllers set to the Fortress recommended absorb
      settings of 54.4 vdc for 2 hrs.  Its always possible that there
      was voltage over swing or something.  I did check that the voltage
      on the controllers was within a0.1 vdc of the battery voltage at
      the Fortresses. I'm now using a pair of Midnite Hampton Bay
      Controllers.  They're rated to 90 amps, but I set them down to 85
      A output, just to provide some head room.  I don't mind the very
      occasional clipping.  The array is two strings of Jinko 425s, 10
      per series string, so 4250 w per controller. <br>
    </p>
    <p>I wonder if the voltage that causes trouble for Fortress might
      have changed due to the possible lightning surge?<br>
    </p>
    <p>Ray<br>
    </p>
    <div class="moz-cite-prefix">On 8/27/2024 3:46 PM, jay wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:8874459D-456F-4B57-AD14-281425B0530E@gmail.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      I have a buddy in tech support at Fortress.
      <div class=""><br class="">
      </div>
      <div class="">I asked him and he said that elevated absorb volts
        above 55.2 could cause this situation.  </div>
      <div class="">And then the power cycle would reboot the BMS.</div>
      <div class=""><br class="">
      </div>
      <div class="">I am presuming its open loop, and the fact you
        mentioned that there was more PV and then the shut down sure
        might be connected.  </div>
      <div class="">You might check the charge voltages/time to make
        sure they are correct and I can\u2019t remember if the classic has
        battery sense wire connections. </div>
      <div class=""><br class="">
      </div>
      <div class="">jay</div>
      <div class=""><br class="">
      </div>
      <div class=""><br class="">
      </div>
      <div class=""><br class="">
      </div>
      <div class=""><br class="">
      </div>
      <div class=""><br class="">
      </div>
      <div class=""><br class="">
        <div><br class="">
          <blockquote type="cite" class="">
            <div class="">On Aug 27, 2024, at 2:51 PM, Ray Walters via
              RE-wrenches &lt;<a
                href="mailto:re-wrenches@lists.re-wrenches.org"
                class="moz-txt-link-freetext" moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>&gt;
              wrote:</div>
            <br class="Apple-interchange-newline">
            <div class="">
              <meta http-equiv="Content-Type"
                content="text/html; charset=UTF-8" class="">
              <div class="">
                <p class="">The SPD was on one of the PV inputs before
                  it came into the house.  There were two Classics, each
                  fed with its own PV input and SPD.  It actually caused
                  an underground splice to fail (high resistance) which
                  I replaced the splice and restored full voltage, and
                  both Classics were working fine.  Just seems unlikely
                  ( but not impossible) that the surge would make it
                  past the Classic without damage, but then damage the
                  Fortress BMS in an otherwise imperceptible manner.  
                  That is our current best theory at the moment though.
                    I added an SPD on the 48 v buss, before this latest
                  total shutdown.    <br class="">
                </p>
                <p class="">Ray Walters<br class="">
                </p>
                <div class="moz-cite-prefix">On 8/27/2024 2:35 PM, Dave
                  Angelini Offgrid Solar via RE-wrenches wrote:<br
                    class="">
                </div>
                <blockquote type="cite"
                  cite="mid:73b67fe1b3d521cc295be424ab132127@sti.net"
                  class="">
                  <meta http-equiv="Content-Type"
                    content="text/html; charset=UTF-8" class="">
                  <div id="signature" class="">When I have had someone
                    lose an SPD (I assume it was on DC buss) there is
                    often latent damage (shows up later) to many of the
                    devices.  In a Hi Rel mode, it is recommended to
                    replace it all. Most offgrid is not that critical
                    but try telling that to someone with rotten food.</div>
                  <div class=""> </div>
                  <div class="">The freezers and reefers are often full
                    of spoils that smells never go away. YUK !<br
                      class="">
                    <pre class=""> </pre>
                    <pre class=""><strong class=""><span
                    style="font-size: small;" class="">Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" rel="noopener"
                    moz-do-not-send="true" class="">  </a><a
style="color: blue; font-size: 11px; font-family: 'Lucida Grande', Verdana, Arial, Helvetica, sans-serif; font-weight: 400; background-color: #ffffff;"
                    href="https://offgridsolar1.com/"
                    rel="noopener noreferrer" moz-do-not-send="true"
                    class=""><span style="font-size: 12pt;" class="">https://offgridsolar1.com/</span></a><a
                    href="http://members.sti.net/offgridsolar/"
                    rel="noopener" moz-do-not-send="true" class=""> </a>
e-mail  <a href="mailto:offgridsolar@sti.net" moz-do-not-send="true"
                    class="moz-txt-link-freetext">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
                  </div>
                  <p class=""><br class="">
                  </p>
                  <p id="reply-intro" class="">On 2024-08-27 1:02 pm,
                    Ray Walters via RE-wrenches wrote:</p>
                  <blockquote type="cite"
style="padding: 0 0.4em; border-left: #1010ff 2px solid; margin: 0"
                    class="">
                    <div class="pre"
style="margin: 0; padding: 0; font-family: monospace">Greetings All;<br
                        class="">
                      <br class="">
                      I have Fortress Battery installation with a pair
                      of E Vault batteries set up in a Master/ Slave
                      arrangement.  Its been working fine for over a
                      year, but the customer just had a complete
                      shutdown of the batteries which left multiple
                      freezers, and refrigerator with rotting food.  
                      When he rebooted the batteries by turning on/off
                      the main breaker on each, they both come up and
                      showed 100% SOC on the Master, and 98% on the
                      other.    There were no fault codes.   I just
                      recently installed a larger PV array, and so the
                      system has been reaching full charge every
                      morning.<br class="">
                      <br class="">
                      I have multiple calls in to Fortress, but not
                      hearing anything back from them at all.  We did
                      have a lightning surge event a few months ago,
                      that damaged a Midnite SPD (first ever for me),
                      and took out the control board on the generator. 
                      One VFX inverter has an LED out, but we only use
                      two inverters of the Quad stack, so I just
                      switched to another inverter.  All other equipment
                      appeared fine: Midnite controllers, rest of the
                      Outback VFX quad stack, and never any issues seen
                      with the Fortress batteries.<br class="">
                      <br class="">
                      The other odd thing, is since he rebooted the
                      batteries, the system is working fine, and
                      recharging to 100%  by 9:30 am as before.    Is it
                      possible the Fortress BMS were damaged and are now
                      having an intermittent shutdown issue?  I did ask
                      him to temporarily disconnect the comms between
                      batteries, in case it is a bad BMS on one, it will
                      isolate it from the other.<br class="">
                      <br class="">
                      This is a tough one to figure out, since it hasn't
                      happened again, and there are no fault codes.  The
                      Mate 3 shows a low frequency AC code, but that's
                      usually just from the generator shutting down.   
                      Any help, ideas, experiences, would be greatly
                      appreciated.<br class="">
                      <br class="">
                      Thanks,<br class="">
                      <br class="">
                      Ray Walters<br class="">
                      Remote Solar<br class="">
                      <br class="">
                      _______________________________________________<br
                        class="">
                      List sponsored by Redwood Alliance<br class="">
                      <br class="">
                      Pay optional member dues here: <a
                        href="http://re-wrenches.org/" target="_blank"
                        rel="noopener noreferrer" moz-do-not-send="true"
                        class="moz-txt-link-freetext">http://re-wrenches.org</a><br
                        class="">
                      <br class="">
                      List Address: <a
                        href="mailto:RE-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true"
                        class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br
                        class="">
                      <br class="">
                      Change listserver email address &amp; settings:<br
                        class="">
                      <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                        target="_blank" rel="noopener noreferrer"
                        moz-do-not-send="true"
                        class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br
                        class="">
                      <br class="">
                      There are two list archives for searching. When
                      one doesn't work, try the other:<br class="">
                      <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                        target="_blank" rel="noopener noreferrer"
                        moz-do-not-send="true"
                        class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br
                        class="">
                      <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                        target="_blank" rel="noopener noreferrer"
                        moz-do-not-send="true"
                        class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br
                        class="">
                      <br class="">
                      List rules &amp; etiquette:<br class="">
                      <a href="http://www.re-wrenches.org/etiquette.htm"
                        target="_blank" rel="noopener noreferrer"
                        moz-do-not-send="true"
                        class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br
                        class="">
                      <br class="">
                      Check out or update participant bios:<br class="">
                      <a href="http://www.members.re-wrenches.org/"
                        target="_blank" rel="noopener noreferrer"
                        moz-do-not-send="true"
                        class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br
                        class="">
                      <br class="">
                    </div>
                  </blockquote>
                  <br class="">
                  <fieldset class="moz-mime-attachment-header"></fieldset>
                  <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext"
                  href="http://re-wrenches.org/" moz-do-not-send="true">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated moz-txt-link-freetext"
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext"
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                  moz-do-not-send="true">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                  moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext"
                  href="http://www.re-wrenches.org/etiquette.htm"
                  moz-do-not-send="true">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext"
                  href="http://www.members.re-wrenches.org/"
                  moz-do-not-send="true">http://www.members.re-wrenches.org</a>

</pre>
                </blockquote>
              </div>
              _______________________________________________<br
                class="">
              List sponsored by Redwood Alliance<br class="">
              <br class="">
              Pay optional member dues here: <a
                href="http://re-wrenches.org"
                class="moz-txt-link-freetext" moz-do-not-send="true">http://re-wrenches.org</a><br
                class="">
              <br class="">
              List Address: <a
                href="mailto:RE-wrenches@lists.re-wrenches.org"
                class="moz-txt-link-freetext" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br
                class="">
              <br class="">
              Change listserver email address &amp; settings:<br
                class="">
              <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                class="moz-txt-link-freetext" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br
                class="">
              <br class="">
              There are two list archives for searching. When one
              doesn't work, try the other:<br class="">
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br
                class="">
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br
                class="">
              <br class="">
              List rules &amp; etiquette:<br class="">
              <a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a><br class="">
              <br class="">
              Check out or update participant bios:<br class="">
              <a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a><br class="">
              <br class="">
            </div>
          </blockquote>
        </div>
        <br class="">
      </div>
    </blockquote>
  </body>
</html>