<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div dir="ltr"></div><div dir="ltr">Brad,</div><div dir="ltr">For hand installation, especially with lower flow rates, my go-to solution, mentored to me by Windy Dankoff, was SDR9 high-pressure (140 psi max if I\u2019m remembering correctly) flexible polyethylene pipe with bronze SDR9 compression couplers and connectors to MPT. They all used a stainless steel inner sleeve that fit inside the poly pipe. I carried the fittings in 3/4\u201d and 1\u201d sizes.&nbsp;</div><div dir="ltr">Contact me off list if you\u2019d like some of these fittings as I described. I\u2019m retired and no longer need them.&nbsp;</div><div dir="ltr">Allan</div><div dir="ltr">Allan@sindelarsolar.com</div><div dir="ltr"><br></div><div dir="ltr"><br><blockquote type="cite">On May 26, 2024, at 12:39\u202fPM, Bradley Bassett via RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt; wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff<div dir="ltr">Ray,<div><br></div><div>Do you have&nbsp;a US supplier for either of these fittings? The Jentro fitting looks great, the Blueseal16 does not look like it would have much of a pressure rating. I did not find a specification.</div><div><br></div><div>What do you all use for drop pipes for well pumps?&nbsp; I have a 260ft deep well with galv, but the&nbsp;first batch corroded through, must have been a really bad batch. The second batch has been fine for many years. I can't bring myself to use PVC which is most common, I just have seen too many issues with it. Stainless is really expensive and hard to find threaded lengths, so I used very high pressure Poly. When it's rated for 300psi it has a very thick wall and is hard to get onto fittings, but is light weight and moderately flexible.&nbsp;</div><div><br></div><div>Brad</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sun, May 26, 2024 at 11:17\u202fAM Ray Walters via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><u></u>

  
    
  
  <div>
    <p>Hi Brad;</p>
    <p>I've seen a lot of leaks with barb fittings on poly pipe. I just
      replace most of the poly plumbing at my place, because I just
      couldn't get it to stop leaking. Black poly pipe is the lowest
      cost per foot, but not quite bomb proof.&nbsp;&nbsp; Barb fittings are
      really more suited for irrigation under 40 psi, where leaks are
      just part of the irrigation system.&nbsp; Also, if the pipe is exposed
      to sunlight, it can degrade and split open. Your described setup
      would have sections above 100 psi, and that will really drive
      leaks.&nbsp; There are compression fittings for the poly pipe, which
      are better.&nbsp; Here are some examples:<br>
    </p>
    <p><img src="https://external-content.duckduckgo.com/iu/?u=https%3A%2F%2Fwww.sabspa.com%2Fwp-content%2Fuploads%2F2021%2F03%2F2-2.jpg&amp;f=1&amp;nofb=1&amp;ipt=5778bf3f16bb7ee6a852dee3ec93ea930661f7ad9bdca992df067de647a3f899&amp;ipo=images" alt="PE pipe compression fitting for drinking water? Choose Blueseal16 - SAB spa" width="358" height="184" data-unique-identifier=""><img src="https://www.jentrofittings.com/sites/jentro/files/styles/product_detail/public/products/klem_draadstuk_sdr11_lowres_0.jpg?itok=6bInZMD5" alt="Jentro Fittings sdr11 klem draadstuk" width="225" height="225" data-unique-identifier=""></p>
    <p>Barb fittings would probably be fine towards the top at the
      storage tanks, where the pressure is much lower, but at the pump,
      and top of the well, where the pressure is over 100 psi, I'd be
      using something better.</p>
    <p>Good Luck,&nbsp; <br>
    </p>
    <p>Ray Walters<br>
      Remote Solar<br>
    </p>
    <div>On 5/26/2024 10:12 AM, Bradley Bassett
      via RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="ltr">Yes, lots of possibilities for leaks. I will be
        exploring them today. Thanks for the tips for&nbsp;finding the
        location. This setup uses 300psi 1" black poly pipe on a 25 ft
        drop, and then about 1200 ft run of the same pipe up 220ft
        elevation to the tanks up the hill with the house about 36ft
        below the tanks with only gravity feed (16 psi). All connections
        on the poly pipe are made with long stainless barb fittings with
        T-bolt clamps, pretty bomb proof stuff. There is a pitless
        adapter into the well casing, I will check that for sure under
        pressure. I'll also fix the check valve in the pump house. I
        seem to have a lot of issues with check valves,&nbsp;do they really
        fail so often? We do<u> not</u> have high mineral&nbsp;water. I've
        especially had issues with spring check valves and no longer use
        them. The one in my pump house is a swing check valve
        which&nbsp;I&nbsp;thought&nbsp;was pretty reliable. If I remember correctly,
        the check valve in these pumps is not replaceable. Fortunately,
        we actually have two wells, each with a 3SQF-2&nbsp;pump that we can
        alternate for supply.&nbsp; I'll let you know what I find.
        <div>
          <div><br>
          </div>
          <div>Way back in the '90's we had a customer&nbsp;with a solar pump
            that just would not perform. Even with a new pump, new
            control, check this and that, it just would not pump much
            water. It pumped fine when out of the well. The drop pipe
            did not have any obstruction. They finally&nbsp;ran the pump
            while it was out of the well with the drop pipe connected
            and under pressure, and discovered a&nbsp;crack in the PVC pipe
            that did not show up except under pressure. So leaks can
            indeed be hard to find.</div>
          <div><br>
          </div>
          <div>Brad&nbsp;
            <div><br>
            </div>
            <div><br>
            </div>
          </div>
        </div>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Sun, May 26, 2024 at
          8:17\u202fAM Jay via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;
          wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div dir="auto">
            <div dir="ltr">Hi all</div>
            <div dir="ltr"><br>
            </div>
            <div dir="ltr">Yes the pump won\u2019t go backwards but it\u2019s
              possible there could be some leakage through the helical
              coil.&nbsp;</div>
            <div dir="ltr"><br>
            </div>
            <div dir="ltr">But both check valves have to fail which is a
              low probability.&nbsp;</div>
            <div dir="ltr"><br>
            </div>
            <div dir="ltr">I\u2019ve seen pipe broken due to someone closing
              a valve and not having a pressure relief valve. Not
              knowing what kind of pipe/fittings &nbsp;are being used it
              could be corrosion has made a hole.&nbsp;</div>
            <div dir="ltr"><br>
            </div>
            <div dir="ltr">Not knowing the layout it might be possible
              to split the plumbing and see if the leakage is above or
              in the well.&nbsp;</div>
            <div dir="ltr"><br>
            </div>
            <div dir="ltr">Lots of fun possibilities&nbsp;</div>
            <div dir="ltr"><br>
            </div>
            <div dir="ltr">Jay</div>
            <div dir="ltr"><br>
            </div>
            <div dir="ltr"><br>
              <blockquote type="cite">On May 26, 2024, at 9:03\u202fAM, Roy
                Butler via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;
                wrote:<br>
                <br>
              </blockquote>
            </div>
            <blockquote type="cite">
              <div dir="ltr">\ufeff <font size="2">Brad,<br>
                  <br>
                  Windy might chime in at some point to back me up on
                  this but I see no way for that pump to turn backwards.<br>
                  Reverse flow is likely a leak at the pump, the down
                  well piping or at the pitless adapter if there is one.<br>
                  <br>
                  Roy....<br>
                  <br>
                  Another old time solar and wind guy, hoping to be
                  retired someday :-).<br>
                </font>
                <pre cols="72">Roy Butler
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807


Education is when you read the fine print; experience is what you get when you don\u2019t.

\u201cThe less people know, the more stubbornly they know it.\u201d

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.

                
</pre>
                <div>On 5/26/2024 10:10 AM, Dave Angelini Offgrid Solar
                  via RE-wrenches wrote:<br>
                </div>
                <blockquote type="cite">
                  <div id="m_-1372981223384826363m_283153019252473897signature">Hey Brad,</div>
                  <div>&nbsp;</div>
                  <div>Sometimes shooting is best if you tell more on
                    what you have done so far like using the SQF
                    shooting guide, especially on a holiday weekend\U0001f609</div>
                  <div>Assume there is a CU200 controller and pump is in
                    ground still, must be with 100ft head, sorry</div>
                  <div>No high amps? It runs, How old?&nbsp;&nbsp;</div>
                  <div>&nbsp;</div>
                  <div>--Dave</div>
                  <div><br>
                    <pre>&nbsp;</pre>
                    <pre><strong><span style="font-size:small">Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" rel="noopener" target="_blank">  </a><a style="color:blue;font-size:11px;font-family:&quot;Lucida Grande&quot;,Verdana,Arial,Helvetica,sans-serif;font-weight:400;background-color:rgb(255,255,255)" href="https://offgridsolar1.com/" rel="noopener noreferrer" target="_blank"><span style="font-size:12pt">https://offgridsolar1.com/</span></a><a href="http://members.sti.net/offgridsolar/" rel="noopener" target="_blank"> </a>
e-mail  <a href="mailto:offgridsolar@sti.net" target="_blank">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
                  </div>
                  <p><br>
                  </p>
                  <p id="m_-1372981223384826363m_283153019252473897reply-intro">On 2024-05-26
                    4:26 am, Jay via RE-wrenches wrote:</p>
                  <blockquote type="cite" style="padding:0px 0.4em;border-left:2px solid rgb(16,16,255);margin:0px">
                    <div style="margin:0px;padding:0px;font-family:monospace">Hi Brad<br>
                      <br>
                      With 2 check valves leaking I\u2019d look for a broken
                      pipe or a corroded fitting. <br>
                      <br>
                      If there is anyway to isolate between the 2 check
                      valves then you could measure the pressure drop on
                      both sides which should point to the direction of
                      the leak. <br>
                      <br>
                      Jay<br>
                      <br>
                      <blockquote type="cite" style="padding:0px 0.4em;border-left:2px solid rgb(16,16,255);margin:0px">On
                        May 25, 2024, at 7:41\u202fPM, Bradley Bassett via
                        RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;
                        wrote:<br>
                        <br>
                        <br>
                        I have a water system with a Grundfos SQFlex
                        SQF3-2 pump. I'm getting water flow in reverse
                        either through the pump or a leak up to the
                        pump. My question is if the check valve on the
                        top of the pump is not sealing, will the
                        progressive cavity pump allow water to flow
                        through the pump in reverse? I'd think that with
                        a positive displacement pump it would not,
                        except very slowly or if it turned the motor
                        backwards which I think would be very unlikely.
                        There is about 100 psi head on &nbsp;the pump. <br>
                        <br>
                        I think it's most likely I have a leak somewhere
                        in the plumbing, and of course another failed
                        check valve farther up in the plumbing. It's
                        possible to get failures even with redundant
                        protection if you have two concurrent failures,
                        which I must have here. <br>
                        <br>
                        Brad Bassett <br>
                        Old time solar guy who used to do solar pumping
                        back in the '80's and '90's. Mostly retired now.<br>
                        <br>
                        <br>
                        _______________________________________________<br>
                        List sponsored by Redwood Alliance<br>
                        <br>
                        Pay optional member dues here: <a href="http://re-wrenches.org" rel="noopener noreferrer" target="_blank">http://re-wrenches.org</a><br>
                        <br>
                        List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                        <br>
                        Change listserver email address &amp; settings:<br>
                        <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noopener noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                        <br>
                        There are two list archives for searching. When
                        one doesn't work, try the other:<br>
                        <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noopener noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                        <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noopener noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                        <br>
                        List rules &amp; etiquette:<br>
                        <a href="http://www.re-wrenches.org/etiquette.htm" rel="noopener noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
                        <br>
                        Check out or update participant bios:<br>
                        <a href="http://www.members.re-wrenches.org" rel="noopener noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
                        <br>
                      </blockquote>
                      _______________________________________________<br>
                      List sponsored by Redwood Alliance<br>
                      <br>
                      Pay optional member dues here: <a href="http://re-wrenches.org" rel="noopener noreferrer" target="_blank">http://re-wrenches.org</a><br>
                      <br>
                      List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                      <br>
                      Change listserver email address &amp; settings:<br>
                      <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noopener noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      There are two list archives for searching. When
                      one doesn't work, try the other:<br>
                      <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noopener noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                      <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noopener noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      List rules &amp; etiquette:<br>
                      <a href="http://www.re-wrenches.org/etiquette.htm" rel="noopener noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
                      <br>
                      Check out or update participant bios:<br>
                      <a href="http://www.members.re-wrenches.org" rel="noopener noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
                      <br>
                    </div>
                  </blockquote>
                  <br>
                  <fieldset></fieldset>
                  <pre>_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a>

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a>

</pre>
                </blockquote>
                <br>
                <span>_______________________________________________</span><br>
                <span>List sponsored by Redwood Alliance</span><br>
                <span></span><br>
                <span>Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a></span><br>
                <span></span><br>
                <span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a></span><br>
                <span></span><br>
                <span>Change listserver email address &amp; settings:</span><br>
                <span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
                <span></span><br>
                <span>There are two list archives for searching. When
                  one doesn't work, try the other:</span><br>
                <span><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a></span><br>
                <span><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br>
                <span></span><br>
                <span>List rules &amp; etiquette:</span><br>
                <span><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a></span><br>
                <span></span><br>
                <span>Check out or update participant bios:</span><br>
                <span><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a></span><br>
                <span></span><br>
              </div>
            </blockquote>
          </div>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
          <br>
          List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address &amp; settings:<br>
          <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          There are two list archives for searching. When one doesn't
          work, try the other:<br>
          <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
          <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
          <br>
          List rules &amp; etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <fieldset></fieldset>
      <pre>_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a>

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
<span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: http://re-wrenches.org</span><br><span></span><br><span>List Address: RE-wrenches@lists.re-wrenches.org</span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span>https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</span><br><span>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span>http://www.re-wrenches.org/etiquette.htm</span><br><span></span><br><span>Check out or update participant bios:</span><br><span>http://www.members.re-wrenches.org</span><br><span></span><br></div></blockquote></body></html>