<meta http-equiv="Content-Type" content="text/html; charset=utf-8"><div dir="ltr"><div>William,</div><div><br></div><div>&nbsp;&nbsp;&nbsp;&nbsp; I agree that AC coupled input power can't be &quot;directly&quot; regulated by the battery inverter, but it *can* be indirectly regulated using techniques such as telling the downstream PV inverter(s) to back off via a frequency-watt change, or turning on a diversion load, or worst case simply shutting off the battery inverter AC output connected to the PV inverters (so-called bang-bang control).&nbsp; However, I thought the battery charging parameters were part of the equation when the inverter is making the decision about what to do if the batteries are nearly full?</div><div><br></div><div>&nbsp;&nbsp;&nbsp; And in my case, with the SI master set to EXT-BMS (most recent firmware), the battery parameters *could* be set and appeared to make a difference in operation.&nbsp; My (possibly incorrect!), assumption was that the closed loop communication was primarily for SOC and fault conditions.&nbsp; If there is any documentation for what the closed loop communication consists of that would be really interesting!</div><div><br></div><div>Cheers,</div><div><br></div><div>Kirk Bailey</div><div><a href="mailto:kirk@abundantsolar.com">kirk@abundantsolar.com</a></div><div>541-231-8072 x1</div><div><br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sun, Nov 12, 2023 at 4:38\u202fPM William Miller &lt;<a href="mailto:william@millersolar.com">william@millersolar.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div class="msg-7508858173050669440"><div lang="EN-US"><div class="m_-7508858173050669440WordSection1"><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">Kirk:</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">There are a lot of misconceptions about AC Coupling in the industry.&nbsp; I think you may have fallen victim to one:</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">When you are feeding AC power backwards through a battery inverter, that inverter cannot exert any control over the charging parameters.&nbsp; You can set bulk, absorption, float, EQ, any charge setting you can find, but if your power source is AC-coupled (coming in through the out door), those settings do not affect the charging at all.</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">Someone please slap me if I am wrong on this.</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">Those settings do apply if you have an AC source like a generator or grid that is connected to an AC <u>input</u>.&nbsp;&nbsp; We cannot connect grid-tied inverters to any input because AC inputs do not create a mini-grid.</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">Furthermore, if you set a Sunny Island for battery type \u201cExt BMS\u201d, you cannot adjust those settings.&nbsp; Pressing the buttons elicits wonky responses. Pressing up arrow jumps to zeros\u2026&nbsp; Pressing the down arrow can reduce settings but they will not be saved.&nbsp; I have seen this and while Fortress cannot replicate this in the lab, they have heard this reported.&nbsp; (This Ext-BMS setting is only available with the latest firmware and by initiating New battery or New system in the quick programming function.)</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">Until this moment I did not realize that this is another reason Closed loop on a </span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">Sunny Island is a non-starter:&nbsp; If you can\u2019t set charge parameters for generator or grid battery charging then you have a system that cannot be set to charge batteries from AC sources with precision.&nbsp; If closed loop does not work for this reason, and open loop does not track the critical SOC values, then we may be out of options.&nbsp; Maybe this is why SMA will not talk to anyone with lithium batteries.</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">Hmmmmm\u2026</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">William</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">Miller Solar</span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">17395 Oak Road, Atascadero, CA 93422</span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">805-438-5600</span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)"><a href="http://www.millersolar.com/" target="_blank"><span style="color:blue">www.millersolar.com</span></a></span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">CA Lic. 773985</span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;;color:rgb(31,73,125)">&nbsp;</span></p><p class="MsoNormal"><b><span style="font-size:10pt;font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;">From:</span></b><span style="font-size:10pt;font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;"> Kirk Bailey [mailto:<a href="mailto:kirk@abundantsolar.com" target="_blank">kirk@abundantsolar.com</a>] <br><b>Sent:</b> Sunday, November 12, 2023 3:05 PM<br><b>To:</b> <a href="mailto:william@millersolar.com" target="_blank">william@millersolar.com</a>; RE-wrenches<br><b>Subject:</b> Re: [RE-wrenches] Integrating Fortress E-vault maxes into an SI AC-coupled system</span></p><p class="MsoNormal">&nbsp;</p><div><div><p class="MsoNormal">I went back and looked at my notes on my recent adventure with closed loop SI to eFlex Fortress, and one thing I had noted at the time is that Fortress recommends 2.2V, 2.26V, and 2.3V for the setting for ChrgVtgFlo (220-10), depending on which of three Fortress docs I read.&nbsp; I think I ended up setting it to 2.26V after some experimentation.</p></div><div><p class="MsoNormal">&nbsp;</p></div><div><p class="MsoNormal">I can imagine a scenario where the voltage gets *slightly* too high, activating the most trigger-happy of the battery's BMS's, and the resulting sudden partial loss in load then causes a transitory voltage surge from the SI, which then...</p></div><div><p class="MsoNormal">&nbsp;</p></div><div><p class="MsoNormal">Cheers,</p></div><div><p class="MsoNormal">&nbsp;</p></div><div><p class="MsoNormal">Kirk Bailey</p></div><div><p class="MsoNormal"><a href="mailto:kirk@abundantsolar.com" target="_blank">kirk@abundantsolar.com</a></p></div><div><p class="MsoNormal">&nbsp;</p></div></div><p class="MsoNormal">&nbsp;</p><div><div><p class="MsoNormal">On Sun, Nov 12, 2023 at 2:36\u202fPM William Miller via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:</p></div><blockquote style="border-color:currentcolor currentcolor currentcolor rgb(204,204,204);border-style:none none none solid;border-width:medium medium medium 1pt;padding:0in 0in 0in 6pt;margin-left:4.8pt;margin-right:0in"><div><p class="MsoNormal">Jay:</p></div><div><p class="MsoNormal">&nbsp;</p></div><div><p class="MsoNormal">Good question. I assumed some kind of FET circuit but that is only my assumption.&nbsp;</p></div><div><p class="MsoNormal">&nbsp;</p></div><div><p class="MsoNormal">However an open relay exhibits some fairly high impedance.&nbsp;</p></div><div><p class="MsoNormal">&nbsp;</p></div><div><p class="MsoNormal">The symptoms indicate the SI shuts down but the batteries remain connected. Something allows 69 volts on the battery terminals\u2026<br clear="all"></p><div><div><p class="MsoNormal"><br>William Miller<br>Miller Solar.com<br>805-438-5600<br><a href="http://www.millersolar.com" target="_blank">www.millersolar.com</a></p></div></div></div><div><p class="MsoNormal">&nbsp;</p></div><div><p class="MsoNormal">&nbsp;</p><div><div><p class="MsoNormal">On Sun, Nov 12, 2023 at 2:22 PM Jay via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:</p></div><blockquote style="border-color:currentcolor currentcolor currentcolor rgb(204,204,204);border-style:none none none solid;border-width:medium medium medium 1pt;padding:0in 0in 0in 6pt;margin-left:4.8pt;margin-right:0in"><div><div><p class="MsoNormal">Maybe someone else knows differently but it was explained to me that the fortress batteries have a relay that disconnects the battery if the voltage gets to high or low. There isn\u2019t any electronic &nbsp;device to change battery impedance besides what the actual cells are doing.&nbsp;</p></div><div><p class="MsoNormal">&nbsp;</p></div><div><p class="MsoNormal">Jay</p></div><div><p class="MsoNormal"><br><br></p><p class="MsoNormal" style="margin-bottom:12pt">On Nov 12, 2023, at 12:50\u202fPM, Jerry Shafer via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:</p></div><blockquote style="margin-top:5pt;margin-bottom:5pt"><div><p class="MsoNormal"><span style="font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;">\ufeff</span></p><div><p class="MsoNormal">Regarding the SI Inverters,for me it works best to eliminate the bat temp sensor and put in a resister set to be 75 degrees, this will prevent the charger over under charge issue.</p><div><p class="MsoNormal">Fun times&nbsp;</p></div></div><p class="MsoNormal">&nbsp;</p><div><div><p class="MsoNormal">On Sun, Nov 12, 2023, 12:36 PM William Miller via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:</p></div><blockquote style="border-color:currentcolor currentcolor currentcolor rgb(204,204,204);border-style:none none none solid;border-width:medium medium medium 1pt;padding:0in 0in 0in 6pt;margin-left:4.8pt;margin-right:0in"><div><div><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">Friends:</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">I am still working on getting the E-vaults to play nice with the Sunny Islands and Sunny Boys.</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">With Open loop I was getting significant discrepancies in the reporting of SOC in the e-vaults versus that reported by the SI inverters.&nbsp; This discrepancy did not diminish over time.&nbsp; The discrepancy caused unacceptable charging and generator operations.</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">I got Closed loop hooked up, but I found that every few days the SI inverters would shut down due to a battery over-voltage condition.&nbsp; I believe that when the e-vaults are near 100% SOC the BMS units increase the battery impedance which means any charging current applied will cause the voltage spike I have been seeing.&nbsp;&nbsp; I was able to measure these conditions myself on site, although they were very fleeting and required recording with the Fluke87 Min-Max function (love this meter!).</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">I was able to extract log files from the Sunny Island primary inverter and perform some analysis.&nbsp; It appears when I turned on remote BMS on the SI (as part of the Closed loop protocol) it disabled the Frequency-Shift Power Control.&nbsp; This means the SI inverters have gone from having poor control over battery charging to having no control over battery charging.</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">I have documented my research <a href="https://millersolar.com/MillerSolar/case_studies/36_SIFortress/36_SunnyIslandFortressIntegration.html#Inhibit" target="_blank">here</a>.&nbsp; There is a table of contents to take you to the latest information.&nbsp; I appreciate pertinent comments any of you might have.</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">By the way, if anyone has called SMA tech support for help on a Sunny Island system, you have likely been asked to extract log files, zip them up and send them off for review (and waited a long time for a reply).&nbsp; I am the kind of guy who does not like to wait for solutions and who likes to figure out things for himself.&nbsp; I have taught myself how to evaluate those log files. I will be posting a web page on the subject.&nbsp; In the meantime, if you are interested, two of my analysis Excel sheets are linked in the case study.&nbsp; I will be expanding on this and providing resources to any integrator that wants that knowledge.</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">Thanks in advance for any insight.&nbsp; I hope I am wrong about this and I am just missing something.&nbsp; I also hope revealing my headaches will help someone someday\u2026</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">William</span></p><p class="MsoNormal"><span style="font-family:&quot;Verdana&quot;,&quot;sans-serif&quot;">&nbsp;</span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">Miller Solar</span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">17395 Oak Road, Atascadero, CA 93422</span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">805-438-5600</span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"><a href="http://www.millersolar.com/" target="_blank">www.millersolar.com</a></span></p><p class="MsoNormal"><span style="font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">CA Lic. 773985</span></p><p class="MsoNormal">&nbsp;</p><p class="MsoNormal">&nbsp;</p></div></div><p class="MsoNormal" style="margin-bottom:12pt">_______________________________________________<br>List sponsored by Redwood Alliance<br><br>Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a><br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There are two list archives for searching. When one doesn't work, try the other:<br><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a></p></blockquote></div><p class="MsoNormal" style="margin-bottom:12pt">_______________________________________________<br>List sponsored by Redwood Alliance<br><br>Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a><br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There are two list archives for searching. When one doesn't work, try the other:<br><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a></p></div></blockquote></div><p class="MsoNormal" style="margin-bottom:12pt">_______________________________________________<br>List sponsored by Redwood Alliance<br><br>Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a><br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There are two list archives for searching. When one doesn't work, try the other:<br><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a></p></blockquote></div></div><p class="MsoNormal" style="margin-bottom:12pt">_______________________________________________<br>List sponsored by Redwood Alliance<br><br>Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a><br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There are two list archives for searching. When one doesn't work, try the other:<br><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a></p></blockquote></div></div></div>
</div></blockquote></div>