William,</div>
<div style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
I'm sorry, I was assuming that people posting here simply hadn't found these integration instructions. If you have tried these and they didn't work, then I stand corrected. I have no personal experience paring this with SMA... I have some really bad experience
 trying to pair other LiFePO4 batteries with SMA open loop... I basically try to avoid The SMA Sunny Island products any more, but that's not always an option...&nbsp;</div>
<div style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
I'm curious if you know which tech support agent told you they've been having problems... I was actually giving someone a price to use Fortress with an existing SMA and if they want to go forward, I might contact my friends at Fortress and see if they would
 want to work with my client's system as a pilot to try to iron out the kinks...&nbsp;</div>
<div style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
Thanks,</div>
<div style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);" class="elementToProof">
<br>
</div>
<div class="elementToProof">
<div style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div id="Signature">
<div id="divtagdefaultwrapper" style="font-size: 12pt; font-family: Calibri, Arial, Helvetica, sans-serif; color: rgb(0, 0, 0);">
<br>
<div><strong style="font-family:'Comic Sans MS'"><font face="Calibri" size="4"></font></strong>
<div dir="auto" style="font-weight:400;text-decoration:none"><span style="font-size:large" class="ContentPasted0">Kienan Maxfield</span><span style="font-size:large"><br class="ContentPasted0">
</span><span style="font-size:large" class="ContentPasted0">Technical sales, Technical Support</span><span style="font-size:large"><br class="ContentPasted0">
</span><span style="font-size:large"><br class="ContentPasted0">
</span></div>
<div dir="auto" style="font-weight:400;text-decoration:none"><strong style="font-size:large" class="ContentPasted0">Green-Go Solar Wholesale Distribution</strong><span style="font-size:large"><br class="ContentPasted0">
</span></div>
<div dir="auto" style="font-weight:400;text-decoration:none"><a href="https://kienan@dist.solar/" target="_blank" style="font-family:&quot;Comic Sans MS&quot;;font-size:large" id="OWA41c0b4fb-1ef7-7041-1423-f58224f30eb6" class="OWAAutoLink ContentPasted0"><strong>kienan@dist.solar</strong></a><span style="font-size:large"><br class="ContentPasted0">
</span><strong style="font-family:&quot;Comic Sans MS&quot;;font-size:large" class="ContentPasted0">(801) 631-5584 (Cell)</strong><span style="font-size:large"><br class="ContentPasted0">
</span></div>
<div dir="auto" style="font-weight:400;text-decoration:none"><strong style="font-family: &quot;Comic Sans MS&quot;; font-size: large;"><a href="https://www.distribution.solar/" target="_blank" style="font-family:&quot;Comic Sans MS&quot;;font-size:large" id="OWA592ae429-3f3e-ee5d-e5f3-025f688f09a5" class="OWAAutoLink ContentPasted0">www.distribution.solar</a></strong></div>
</div>
<div>
<div><font face="Comic Sans MS" size="4"><strong><font face="Calibri"><span></span></font></strong></font></div>
</div>
</div>
</div>
</div>
<div id="appendonsend"></div>
<hr style="display:inline-block;width:98%" tabindex="-1">
<div id="divRplyFwdMsg" dir="ltr"><font face="Calibri, sans-serif" style="font-size:11pt" color="#000000"><b>From:</b> RE-wrenches &lt;re-wrenches-bounces@lists.re-wrenches.org&gt; on behalf of William Miller via RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt;<br>
<b>Sent:</b> Tuesday, September 19, 2023 1:39 PM<br>
<b>To:</b> RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt;<br>
<b>Cc:</b> William Miller &lt;william@millersolar.com&gt;<br>
<b>Subject:</b> Re: [RE-wrenches] Sunny Island/Fortress E-vault</font>
<div>&nbsp;</div>
</div>
<div>
<div dir="auto">Kieran:</div>
<div dir="auto"><br>
</div>
<div dir="auto">I have read the documentation. Fortress tech support said there have been problems and recommended open loop.&nbsp;</div>
<div dir="auto"><br>
</div>
<div dir="auto">Do you know what parameters are passed with closed loop?<br clear="all">
<div dir="auto">
<div dir="ltr" class="x_gmail_signature" data-smartmail="gmail_signature"><br>
William Miller<br>
Miller Solar.com<br>
805-438-5600<br>
<a href="http://www.millersolar.com">www.millersolar.com</a><br>
</div>
</div>
</div>
<div><br>
</div>
<div><br>
<div class="x_gmail_quote">
<div dir="ltr" class="x_gmail_attr">On Tue, Sep 19, 2023 at 12:18 PM Kienan Maxfield via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br>
</div>
<blockquote class="x_gmail_quote" style="margin:0 0 0 .8ex; border-left:1px #ccc solid; padding-left:1ex">
<div dir="ltr">
<div style="font-family:Calibri,Helvetica,sans-serif; font-size:12pt; color:rgb(0,0,0)">
That's actually incorrect, Fortress totally does support closed-loop with the SMA Sunny Island inverters. Here is their integration guide. This has all of the instructions and coms wiring, etc. -&nbsp;<a href="https://learn.fortresspower.com/external/manual/sma/article/introduction-useful-links?p=dc8b9a9c1b3f410556835193e66f2257c662403dfb3da4056e618e954e8381d2" id="x_m_-2265844953036468018LPlnk209221" target="_blank">https://learn.fortresspower.com/external/manual/sma/article/introduction-useful-links?p=dc8b9a9c1b3f410556835193e66f2257c662403dfb3da4056e618e954e8381d2</a></div>
<div>
<div style="font-family:Calibri,Helvetica,sans-serif; font-size:12pt; color:rgb(0,0,0)">
<br>
</div>
<div id="x_m_-2265844953036468018Signature">
<div id="x_m_-2265844953036468018divtagdefaultwrapper" style="font-size:12pt; font-family:Calibri,Arial,Helvetica,sans-serif; color:rgb(0,0,0)">
Thanks,</div>
<div id="x_m_-2265844953036468018divtagdefaultwrapper" style="font-size:12pt; font-family:Calibri,Arial,Helvetica,sans-serif; color:rgb(0,0,0)">
<br>
<div><strong style="font-family:'Comic Sans MS'"><font face="Calibri" size="4"></font></strong>
<div dir="auto" style="font-weight:400; text-decoration:none"><span style="font-size:large">Kienan Maxfield</span><span style="font-size:large"><br>
</span><span style="font-size:large">Technical sales, Technical Support</span><span style="font-size:large"><br>
</span><span style="font-size:large"><br>
</span></div>
<div dir="auto" style="font-weight:400; text-decoration:none"><strong style="font-size:large">Green-Go Solar Distribution</strong><span style="font-size:large"><br>
</span></div>
<div dir="auto" style="font-weight:400; text-decoration:none"><a href="https://kienan@dist.solar/" id="x_m_-2265844953036468018OWA1b215a34-1d85-5032-22ce-97dac168f12d" target="_blank" style="font-family:&quot;Comic Sans MS&quot;; font-size:large"><strong>kienan@dist.solar</strong></a><span style="font-size:large"><br>
</span></div>
<div dir="auto" style="font-weight:400; text-decoration:none"><strong style="font-family:&quot;Comic Sans MS&quot;; font-size:large">(801) 631-5584 (Cell)</strong><span style="font-size:large"><br>
</span></div>
<div dir="auto" style="font-weight:400; text-decoration:none"><strong style="font-family:&quot;Comic Sans MS&quot;; font-size:large"><a href="https://www.distribution.solar/" id="x_m_-2265844953036468018OWA931e73fc-a7f3-5c4a-44a3-47c4a38a664a" target="_blank" style="font-family:&quot;Comic Sans MS&quot;; font-size:large">www.distribution.solar</a></strong></div>
<div dir="auto" style="font-weight:400; text-decoration:none"><br>
</div>
<div dir="auto" style="font-weight:400; text-decoration:none"><br>
</div>
<div dir="auto" style="font-weight:400; text-decoration:none"><br>
</div>
<div><font face="Comic Sans MS" size="4"><strong><font face="Calibri">
<div style="font-family:Calibri,Arial,Helvetica,sans-serif,&quot;Apple Color Emoji&quot;,&quot;Segoe UI Emoji&quot;,NotoColorEmoji,&quot;Segoe UI Symbol&quot;,&quot;Android Emoji&quot;,EmojiSymbols; font-size:16px">
<font face="Comic Sans MS" size="4"><strong><font face="Calibri"><strong style="font-family:&quot;Comic Sans MS&quot;"><font face="Calibri"></font></strong></font></strong></font></div>
<span></span></font></strong></font></div>
</div>
</div>
</div>
</div>
<div id="x_m_-2265844953036468018appendonsend"></div>
<hr style="display:inline-block; width:98%">
<div id="x_m_-2265844953036468018divRplyFwdMsg" dir="ltr"><font face="Calibri, sans-serif" color="#000000" style="font-size:11pt"><b>From:</b> RE-wrenches &lt;<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>&gt;
 on behalf of Kirk Herander via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
<b>Sent:</b> Saturday, September 16, 2023 8:33 AM<br>
<b>To:</b> RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
<b>Cc:</b> Kirk Herander &lt;kirkh@vermont.solar&gt;<br>
<b>Subject:</b> Re: [RE-wrenches] Sunny Island/Fortress E-vault</font>
<div>&nbsp;</div>
</div>
<div>
<div dir="auto">Jerry,&nbsp;</div>
<div dir="auto"><br>
</div>
<div dir="auto">Who is the maker of the Blue Planet/Outback SOC box interface you mention?</div>
<div><br>
<div>
<div dir="ltr">On Sat, Sep 16, 2023 at 9:30 AM Jerry Shafer via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br>
</div>
<blockquote style="margin:0px 0px 0px 0.8ex; border-left-width:1px; border-left-style:solid; padding-left:1ex; border-left-color:rgb(204,204,204)">
<div dir="auto">Mac, wrenches&nbsp;
<div dir="auto">SMA and fortress can only open loop and with a fixed temp sender its fine. Now on the blue planet and open loop with outback, you need a SOC box that they can make for you, it will interface with the blue planet and command the genny.</div>
<div dir="auto">Fun times</div>
</div>
<br>
<div>
<div dir="ltr">On Sat, Sep 16, 2023, 6:04 AM Mac Lewis &lt;<a href="mailto:maclewis1@gmail.com" target="_blank">maclewis1@gmail.com</a>&gt; wrote:<br>
</div>
<blockquote style="margin:0px 0px 0px 0.8ex; border-left-width:1px; border-left-style:solid; padding-left:1ex; border-left-color:rgb(204,204,204)">
<div dir="ltr">Hi William,
<div><br>
</div>
<div>Are you doing open loop or closed loop communication?&nbsp; I'm not sure if Fortress can do a closed loop with SMA or not.</div>
<div><br>
</div>
<div>We struggled to get the open loop to work well with some Blue Ion batteries, not from a charging sense but from a sense of getting the auto gen start to trigger correctly.&nbsp; Basically, the SOC algorithm was always way off.&nbsp; For a while we were using an
 external voltage trigger and we could get the generator to start OK before BMS shutdown.&nbsp; We have since added a Namaka box and are using the &quot;Ext BMS&quot; setting for battery type in the Sunny Island and it has been working very well.</div>
<div><br>
</div>
<div>I think the difficulty arises because the Sunny Island is so State-of-Charge centric and you can't manipulate the SOC algorithm without that Ext-BMS setting (and solid communication).&nbsp; One weakness of the ext&nbsp;BMS setting is that it won't fall back on Voltage
 settings if battery communication goes down, but this is a weakness throughout closed loop communication for many manufacturers.</div>
<div><br>
</div>
<div>Let us know if there is a Fortress to SMA communication solution.</div>
<div><br>
</div>
<div><br>
</div>
<div><br>
</div>
<div><br>
</div>
</div>
<br>
<div>
<div dir="ltr">On Fri, Sep 15, 2023 at 11:11\u202fPM Jerry Shafer via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br>
</div>
<blockquote style="margin:0px 0px 0px 0.8ex; border-left-width:1px; border-left-style:solid; padding-left:1ex; border-left-color:rgb(204,204,204)">
<div dir="ltr">William, Wrenches
<div>Yes I do and it does require some basic electronics&nbsp;to make it work correctly, you will need to remove the ttemp sender and make a resistor&nbsp;pack to simulate the 77 degree reading otherwise&nbsp;it will not charge properly, for the first one I used a breadboard
 to set the temp for what I wanted to see then build a more solid state shrink wrap resistor. Doing this will prevent undercharge by the SMA and your customer will be happy to see the full state of charge at the batteries.</div>
<div>OldSchool fun times</div>
<div><br>
<div><br>
</div>
</div>
</div>
<br>
<div>
<div dir="ltr">On Thu, Sep 14, 2023 at 2:12\u202fPM William Miller via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br>
</div>
<blockquote style="margin:0px 0px 0px 0.8ex; border-left-width:1px; border-left-style:solid; padding-left:1ex; border-left-color:rgb(204,204,204)">
<div>
<div lang="EN-US">
<div>
<p><span style="font-size:12pt; font-family:Verdana,sans-serif">Friends:</span></p>
<p><span style="font-size:12pt; font-family:Verdana,sans-serif">&nbsp;</span></p>
<p><span style="font-size:12pt; font-family:Verdana,sans-serif">I am commissioning an E-vault battery array to an existing SMA Sunny Island System.&nbsp; Does anyone have any experience with this they could share?</span></p>
<p><span style="font-size:12pt; font-family:Verdana,sans-serif">&nbsp;</span></p>
<p><span style="font-size:12pt; font-family:Verdana,sans-serif">Thanks.</span></p>
<p><span style="font-size:12pt; font-family:Verdana,sans-serif">&nbsp;</span></p>
<p><span style="font-size:12pt; font-family:Verdana,sans-serif">William</span></p>
<p><span style="font-size:12pt; font-family:Verdana,sans-serif">&nbsp;</span></p>
<p><span style="font-size:12pt; font-family:Arial,sans-serif">Miller Solar</span></p>
<p><span style="font-size:12pt; font-family:Arial,sans-serif">17395 Oak Road, Atascadero, CA 93422</span></p>
<p><span style="font-size:12pt; font-family:Arial,sans-serif">805-438-5600</span></p>
<p><span style="font-size:12pt; font-family:Arial,sans-serif"><a href="http://www.millersolar.com/" rel="noreferrer" target="_blank" style="font-family:Arial,sans-serif">www.millersolar.com</a></span></p>
<p><span style="font-size:12pt; font-family:Arial,sans-serif">CA Lic. 773985</span></p>
<p>&nbsp;</p>
<p>&nbsp;</p>
</div>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">
http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">
RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</div>
</blockquote>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">
http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">
RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote>
</div>
<br clear="all">
<div><br>
</div>
<span>-- </span><br>
<div dir="ltr">
<div><br>
</div>
<div><font face="'times new roman', serif" style="font-family:&quot;times new roman&quot;,serif; color:rgb(48,90,120)"><br>
</font></div>
<div><br>
</div>
Mac Lewis<br>
<br>
<span style="font-family:&quot;Times New Roman&quot;; font-size:medium; color:rgb(255,153,0)"><b style="font-family:&quot;Times New Roman&quot;"><font face="Arial, Helvetica, sans-serif" size="3" style="font-family:Arial,Helvetica,sans-serif; color:rgb(255,153,0)">
<p align="left" style="font-family:Arial,Helvetica,sans-serif"><font face="Verdana, Arial, Helvetica, sans-serif" style="font-family:Verdana,Arial,Helvetica,sans-serif; color:rgb(0,0,0)"><span style="font-size:small; font-family:Verdana,Arial,Helvetica,sans-serif"><span style="font-family:arial; font-weight:normal; color:rgb(48,90,120)"><font face="'times new roman', serif" style="font-family:&quot;times new roman&quot;,serif; color:rgb(48,90,120)">&quot;Yo
 solo sé que no sé nada.&quot;&nbsp;</font><span style="font-weight:700; font-family:arial; color:rgb(104,104,104)"><font face="'times new roman', serif" style="font-family:&quot;times new roman&quot;,serif; color:rgb(104,104,104)">-Sócrates</font></span></span></span></font></p>
</font></b></span></div>
</blockquote>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">
http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">
RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote>
</div>
</div>
</div>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">
http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">
RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote>
</div>
</div>
</div>
</body>
</html>