<div dir="auto">Does the utility allow line side tie in and then you should not need to be concerned about the 100 amp main as long as you have the wire size correct. Many utilities are not allowing line side tap however.<div dir="auto">Fun times<br><div dir="auto"><br></div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Aug 8, 2023, 8:11 AM Dana Orzel via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  

    
  
  <div text="#000000" bgcolor="#FFFFFF">
    <p><font size="5">Oh Wise folks!</font></p>
    <p><font size="5">Attached is a wire schematic please review. &amp;
        feel free to possibly use for yourself in the future.<br>
      </font></p>
    <p><font size="5">I am in a bind with an interconnection where I
        have an apartment 6 pack meter  box with all 120-240v/100 amp
        breakers &amp; assumed 100 amp busbars. The apts. were a mid
        1970&#39;s original build.  There are 4 apartment with 1
        circuit/meter each &amp; 1 house circuit/ meter for owners
        use.The breaker boxes are Sylvania (yuck). Originally I assumed
        a larger busbar due to 6 - 100 amp breakers &amp; this was not
        the case. We all know about assuming...</font></p>
    <p><font size="5">I consulted with W-2 who had assisted my lead
        installer in in the past from UT. He sent the following &amp;
        though it makes sense to me, the utility is asking how I can
        have a 225 amp panel behind a 100 amp breaker. My response was
        that all we are doing is  achieving a properly sized bus bar to
        accommodate the back feed.</font></p>
    <p><font size="5">My Utility Idaho Power requires  interconnection
        with a meter that has a load on it. Solar only meters are not
        allowed. This is for the owners loads only &amp; he has 1 meter
        per apt complex at 100amps each.<br>
      </font></p>
    <p><font size="5">I am wondering if any of you have used this
        connection adaption to achieve a larger array connection &amp;
        how it went?</font></p>
    <div>-- <br>
      Dana Orzel Great Solar Works, Inc. C - 208.721.7003
      <a href="mailto:dana@solarwork.com" target="_blank" rel="noreferrer">dana@solarwork.com</a> Idaho Contractor - # 028765 Idaho PV # 028374
      &quot;Responsible Technologies for Responsible People since 1988&quot;</div>
  </div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn&#39;t work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>