<div dir="auto">It seems best not to have a temp sensor installed and use the default of 75 degrees. SMA needs a resister to hold the temp.<div dir="auto">Fun times</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Nov 16, 2022, 5:48 PM Maverick Brown via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="auto">Ray<div><br></div><div>I\u2019ve installed eFlex and eVault MAX on Outback and Schnieder. Rock solid so far. I\u2019ve noticed the lower charge voltages cause or amplify a variability in the SOC and bring up the Absorb a bit solves the issue. </div><div><br></div><div>The fortress / Outback integration guide has values for charge controllers and has Absorb at 55.2 for two hours. Some of the integration guides have a lower Absorb setting. I\u2019m not sure why. I\u2019ve had to measure actual inverter voltages and adjust the charger settings to over come any minor calibration issues. The Classic can be calibrated quite easily from the tweaks menu. Also, if using an FNDC, make sure that is calibrated to bus bar voltage that batteries are producing. </div><div><br></div><div><div style="display:block"><div style="display:inline-block" role="link"><a style="border-radius:10px;font-family:-apple-system,Helvetica,Arial,sans-serif;display:block;width:228px;overflow:hidden;text-decoration:none" rel="nofollow noreferrer" href="https://www.fortresspower.com/wp-content/uploads/2022/01/Fortress-Power-Outback-Inverter-Guide-Rev1.6_1.21.2022.pdf" dir="ltr" role="button" width="228" target="_blank"><table style="table-layout:fixed;border-collapse:collapse;width:228px;background-color:#e9e9eb;font-family:-apple-system,Helvetica,Arial,sans-serif" cellpadding="0" cellspacing="0" border="0" width="228"><tbody><tr><td align="center"><img style="width:228px;height:295px" width="228" height="295" alt="preview.png" src="cid:D901FEFE-D83F-4B63-9B7A-3E0CDD779BF5"></td></tr><tr><td><table bgcolor="#E9E9EB" cellpadding="0" cellspacing="0" width="228" style="font-family:-apple-system,Helvetica,Arial,sans-serif;table-layout:fixed;background-color:rgba(233,233,235,1)"><tbody><tr><td style="padding:8px 0px 8px 0px"><div style="max-width:100%;margin:0px 16px 0px 16px;overflow:hidden"><div style="word-wrap:break-word;font-weight:500;font-size:12px;overflow:hidden;text-overflow:ellipsis;text-align:left"><a rel="nofollow noreferrer" href="https://www.fortresspower.com/wp-content/uploads/2022/01/Fortress-Power-Outback-Inverter-Guide-Rev1.6_1.21.2022.pdf" style="text-decoration:none" target="_blank"><font color="#000000" style="color:rgba(0,0,0,1)">Fortress-Power-Outback-Inverter-Guide-Rev1.6_1.21.2022</font></a></div><div style="word-wrap:break-word;font-weight:400;font-size:11px;overflow:hidden;text-overflow:ellipsis;text-align:left"><a rel="nofollow noreferrer" href="https://www.fortresspower.com/wp-content/uploads/2022/01/Fortress-Power-Outback-Inverter-Guide-Rev1.6_1.21.2022.pdf" style="text-decoration:none" target="_blank"><font color="#A2A2A9" style="color:rgba(60,60,67,0.6)">PDF Document · 595 KB</font></a></div></div></td></tr></tbody></table></td></tr></tbody></table></a></div></div><div><br></div><a href="https://www.outbackpower.com/downloads/documents/appnotes/fndc_field_cal_app_note.pdf" target="_blank" rel="noreferrer">https://www.outbackpower.com/downloads/documents/appnotes/fndc_field_cal_app_note.pdf</a></div><div><br><br><div dir="ltr"><div style="color:rgb(0,0,0);font-family:Helvetica;font-size:12px"><div>Maverick Brown<br>Off-Grid Solar Commander since 2006<br><b>Maverick Solar Enterprises, Inc.</b></div><div><b> \u2022 Solar Commander Remote Power</b></div><div><b> \u2022 SunFlow Systems Cathodic Protection <br></b><a href="mailto:maverick@mavericksolar.com" target="_blank" rel="noreferrer">maverick@mavericksolar.com</a><br>512-460-9825</div><div><br></div></div></div><div dir="ltr"><br><blockquote type="cite">On Nov 16, 2022, at 2:15 PM, Ray Walters via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">re-wrenches@lists.re-wrenches.org</a>&gt; wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff
  
    
  
  
    <p>I finally heard back from Fortress, I&#39;m going to try their
      suggestion of &quot;equalizing&quot; the batteries at 55.5 v, and adjust
      some settings.  I&#39;ll report back to the list on what I come up
      with.  This is an interesting application: quad stack of VFX
      inverters with Midnite CCs.   Using the aux out on the Classic to
      control a relay to turn on/off the inverters for LVD, since
      Outback programming (like Schneider) won&#39;t allow LVD settings
      above 48v.<br>
    </p>
    <p>Ray<br>
    </p>
    <div>On 11/16/2022 12:40 PM, Chris Sparadeo
      via RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="auto">Hi Ray,</div>
      <div dir="auto"><br>
      </div>
      <div dir="auto">I would suggest pushing the latest firmware update
        to both units. 
        <div dir="auto"><br>
        </div>
        <div><a href="https://www.fortresspower.com/firmware/" target="_blank" rel="noreferrer">https://www.fortresspower.com/firmware/</a></div>
      </div>
      <div dir="auto"><br>
      </div>
      <div dir="auto">re: tech support\u2026</div>
      <div dir="auto"><br>
      </div>
      <div dir="auto">I have had good luck speaking directly to Tom:<br>
      </div>
      <div dir="auto"><br>
      </div>
      <div dir="auto">
        <div dir="auto">Thomas Honey</div>
        <div dir="auto">Fortress Power</div>
        <div dir="auto">Applications Engineering </div>
        <div dir="auto">(215) 613-4318 x4318</div>
        <div dir="auto"><a href="mailto:tomh@fortresspower.com" target="_blank" rel="noreferrer">tomh@fortresspower.com</a></div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">I agree that Fortress\u2019 Discord, online
          ticketing system and phone support are subpar. Call me old
          school, but an answered phone call when on-site is a must have
          feature of any manufacturer.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">Hope this helps,</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">-Chris  </div>
        <div dir="auto"><br>
        </div>
      </div>
      <div>
        <div class="gmail_quote">
          <div dir="ltr" class="gmail_attr">On Wed, Nov 16, 2022 at 2:20
            PM Howie Michaelson via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">re-wrenches@lists.re-wrenches.org</a>&gt;
            wrote:<br>
          </div>
          <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-style:solid;padding-left:1ex;border-left-color:rgb(204,204,204)">
            <div dir="ltr">
              <div class="gmail_default" style="font-family:verdana,sans-serif">Hi Ray,</div>
              <div class="gmail_default" style="font-family:verdana,sans-serif">I have been
                having a difficult time communicating with Fortress as
                well.  I filed a support ticket several times and only
                got a response a couple of days later asking another
                question that was easily answered, but then do not
                receive any reply to that without filing another support
                ticket, which again takes days for them to respond to. 
                Very unsatisfactory and frustrating after having
                invested in 7 eVault Max for a long time client. Don&#39;t
                have any suggestions for you.<br clear="all">
              </div>
              <div>
                <div dir="ltr" data-smartmail="gmail_signature">
                  <div dir="ltr">
                    <div>
                      <div dir="ltr">
                        <div>
                          <div dir="ltr">
                            <div>
                              <div dir="ltr">
                                <div>
                                  <div dir="ltr">
                                    <div>
                                      <div dir="ltr">
                                        <div>
                                          <div dir="ltr"><span><span><font style="color:rgb(136,136,136)"><span style="color:rgb(120,63,4)"><b>Howie
                                                      Michaelson<br>
                                                    </b></span><span style="color:rgb(0,0,255)"></span></font></span></span><span><span><span><span><font style="color:rgb(136,136,136)"><span style="color:rgb(106,168,79)"><b>Sun
                                                          Catcher</b></span><br>
                                                      <span style="color:rgb(68,68,68)"><span style="background-color:rgb(255,255,255)"><font style="color:rgb(68,68,68)" size="2">
                                                          <span style="color:rgb(32,18,77)"><b><span></span></b></span></font></span></span></font></span><span><font style="color:rgb(136,136,136)"><span style="color:rgb(68,68,68)"><span style="background-color:rgb(255,255,255)"><font style="color:rgb(68,68,68)" size="2"><span style="color:rgb(32,18,77)"><b><span><span><span style="color:rgb(68,68,68)"><span style="background-color:rgb(255,255,255)"></span></span></span></span></b></span></font></span></span></font></span></span></span></span><span><span><font style="color:rgb(136,136,136)"><span style="color:rgb(0,0,255)"><b><font style="color:rgb(0,0,255)" size="1"><i>NABCEP Certified Solar PV
                                                          Installer\u2122<br>
                                                        </i></font></b></span></font></span><span><span><font style="color:rgb(136,136,136)"><span style="color:rgb(120,63,4)"></span></font></span></span></span><span><span><span><font style="color:rgb(136,136,136)"><span style="color:rgb(120,63,4)"><b><img src="https://drive.google.com/uc?id=1MQF8aTcFNnBR59ia5JAm1DsPHCxzNkPx&amp;export=download"><br>
                                                      </b></span></font></span></span><span><font style="color:rgb(136,136,136)"><span style="color:rgb(0,0,255)"></span></font></span><span><font style="color:rgb(136,136,136)"><span style="color:rgb(68,68,68)"><span style="background-color:rgb(255,255,255)"><font style="color:rgb(68,68,68)" size="2"><span style="color:rgb(32,18,77)"><b><span><span><span style="color:rgb(68,68,68)"><span style="background-color:rgb(255,255,255)"><font style="color:rgb(68,68,68)" size="2">Solar Electric Systems Sales &amp;
                                                          Service<br>
                                                          </font></span></span><span style="color:rgb(180,95,6)">802-272-0004</span></span></span></b></span></font></span></span></font></span></span></div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
              <br>
            </div>
            <br>
            <div class="gmail_quote">
              <div dir="ltr" class="gmail_attr">On Wed, Nov 16, 2022 at
                2:02 PM Ray Walters via RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">re-wrenches@lists.re-wrenches.org</a>&gt;
                wrote:<br>
              </div>
              <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-style:solid;padding-left:1ex;border-left-color:rgb(204,204,204)">Greetings
                Fellow Wrenches;<br>
                <br>
                Based on glowing reports from the RE list, I finally
                used Fortress for a <br>
                battery replacement for a long time customer. Overall,
                it seems to be a <br>
                better solution than others I&#39;ve seen. However, we are
                having issues.  <br>
                First the two batteries are supposed to be linked
                together in a master/ <br>
                slave configuration, but they charge and discharge
                unevenly, and have <br>
                SOC often 20% different.   Batteries are connected to a
                common buss with <br>
                equal length 4/0 cables.<br>
                <br>
                I&#39;ve been truly disappointed with Fortress customer
                support. First, I&#39;ve <br>
                called multiple times over the past two weeks, and never
                got through to <br>
                anyone.  Their online support system is quite flawed as
                well, and I had <br>
                a very difficult time even setting up a support ticket. 
                Now I can&#39;t <br>
                even log in to view the support ticket, and I&#39;ve only
                received one email <br>
                back asking if I had properly paralleled the batteries.<br>
                <br>
                Has anyone else had a hard time with Fortress support? 
                Does anyone have <br>
                a direct contact?  Customer is beyond pissed now, after
                almost 2 weeks <br>
                hearing nothing, and having spent tens of thousands.<br>
                <br>
                Thanks;<br>
                <br>
                Ray Walters<br>
                Remote Solar<br>
                <br>
                _______________________________________________<br>
                List sponsored by Redwood Alliance<br>
                <br>
                Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
                <br>
                List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Change listserver email address &amp; settings:<br>
                <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                <br>
                There are two list archives for searching. When one
                doesn&#39;t work, try the other:<br>
                <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                <br>
                List rules &amp; etiquette:<br>
                <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
                <br>
                Check out or update participant bios:<br>
                <a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
                <br>
              </blockquote>
            </div>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
            <br>
            List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address &amp; settings:<br>
            <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            There are two list archives for searching. When one doesn&#39;t
            work, try the other:<br>
            <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
            <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
      </div>
      -- <br>
      <div dir="ltr" data-smartmail="gmail_signature">
        <div dir="ltr">
          <div>
            <div dir="ltr">
              <div dir="ltr">
                <div>Chris Sparadeo</div>
                <div><br>
                </div>
                <div><br>
                </div>
                <div>C_802-369-4458</div>
                <div>H_802-728-3059</div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset></fieldset>
      <pre>_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank" rel="noreferrer">http://re-wrenches.org</a>

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn&#39;t work, try the other:
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  

<span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank" rel="noreferrer">http://re-wrenches.org</a></span><br><span></span><br><span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a></span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>There are two list archives for searching. When one doesn&#39;t work, try the other:</span><br><span><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a></span><br><span><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a></span><br><span></span><br><span>Check out or update participant bios:</span><br><span><a href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a></span><br><span></span><br></div></blockquote></div></div>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn&#39;t work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>