<div dir="ltr"><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">I&#39;m not following the wiring diagrams for this new inverter. It has 200A pass-through capability with an integrated 200A load disconnect. But then it says the wire gauge for the load out wiring can be #4 to 2/0. </div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">In an off-grid scenario where there is no generator, the max continuous output is 62.5A, so I assume 80A circuit protection could be used with 80A rated wire (#4), but how is that circuit protection implemented if the 200A breaker is integrated? Do you have to run a short piece of 2/0 to an external 80A rated OCPD and then step down to #4?</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Jason Szumlanski</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><b><div style="text-align:center"><br></div></b></div></div></div></div></div></div></div></div><img width="0" height="0" class="mailtrack-img" alt="" style="display:flex" src="https://mailtrack.io/trace/mail/f378a393a291dc013800d77613c31f347da26cd4.png?u=1613865"></div>