<div dir="ltr">Hi Jeff<div>Here&#39;s the skinny on your questions. </div><div><br></div><div><span style="color:rgb(0,0,0)">1)  you are using the Radian only as an AC Grid-Tie inverter - no batteries on it?</span></div><div><span style="color:rgb(0,0,0)"><i>The Radian inverter has a bank of AGM Lead Acid Batteries on it. </i></span></div><div><span style="color:rgb(0,0,0)">2) that you are aware that the AC Coupled wattage plus the DC wattage on the Sol-Ark&#39;s MPPTs must be within the total allowed for solar generation</span></div><div><span style="color:rgb(0,0,0)"><i>Yes, we are aware of the limits of the inverters. </i></span></div><div><span style="color:rgb(0,0,0)">3) that you have the AC Coupled output of the Radian connected to the GEN breaker of the Sol-Ark</span></div><div><i>This is the weird  part of this system. Because of the client&#39;s needs/wants we are treating the Radian inverter as the grid and it is tied into the grid breaker on the Sol-Arks. Lesson learned here is never let the client drive the design. </i><br style="color:rgb(0,0,0)"><span style="color:rgb(0,0,0)">4) that you have the software set for the GEN breaker to be AC Coupled and have checked all other software items with Sol-Ark needed for AC coupling</span></div><div><span style="color:rgb(0,0,0)"><i>We have the Sol-Arks set as AC coupled, but on the</i> grid breaker. <i>We cleared this design with Sol-Ark tech support by sending them the schematic before moving ahead with the design. They didn&#39;t see any issue with the design before we built it. </i></span></div><div><span style="color:rgb(0,0,0)"><i><br></i></span></div><div><font color="#000000"><i>Please see the as-built schematic attached to the previous email. </i></font></div><div><font color="#000000"><i><br></i></font></div><div><font color="#000000"><i><br></i></font></div><div><font color="#000000"><i>Thanks for looking this over. I feel like there must be something that we and Sol-Ark are missing. </i></font></div><div><font color="#000000"><br></font></div><div><font color="#000000"><br></font></div><div><font color="#000000"><br clear="all"></font><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div style="font-size:small;color:rgb(80,0,80)"><div><font face="georgia, serif">Vince McClellan</font></div><div><font face="georgia, serif">Energy Design</font></div><div><font face="georgia, serif">NABCEP PV Installation Professional</font></div><div><font face="georgia, serif">p. <a href="tel:(541)%20485-8122" value="+15414858122" style="color:rgb(17,85,204)" target="_blank">(541) 485-8122</a>  f. <a href="tel:(541)%20338-8202" value="+15413388202" style="color:rgb(17,85,204)" target="_blank">(541) 338-8202</a></font></div></div><div style="font-size:small;color:rgb(80,0,80)"><img src="https://docs.google.com/uc?export=download&amp;id=1HcXK0FTsJsEFDvKv-POVulmqJD3Ikpz4&amp;revid=0B2VUQDDTFCz_aVNUUUNDRkNRUCtjc1oyZ3JFY2NvNWlJVGpvPQ" width="420" height="79"><br></div><div style="font-size:small;color:rgb(80,0,80)"><span style="font-family:&quot;arial narrow&quot;,sans-serif">If you have received this email and are not the intended recipient please delete this email. Copying, or using any part, content, or attachment of this email is strictly prohibited. </span></div></div></div></div><br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Jan 19, 2022 at 7:05 PM Jeff Clearwater &lt;<a href="mailto:jeffc@villagepowerdesign.com">jeffc@villagepowerdesign.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">


<div style="color:rgb(0,0,0)">Yes what Jay 
said - need a block diagram 
with available power flows on this one.  If you&#39;ve been working with 
Sol-Ark you probably covered the basics but just for the rest of us to 
be assured:<br>

<br>

I assume:<br>

<br>

1)  you are using the Radian only as an AC Grid-Tie inverter - no 
batteries on it?<br>

2) that you are aware that the AC Coupled wattage plus the DC wattage on
 the Sol-Ark&#39;s MPPTs must be within the total allowed for solar 
generation<br>

3) that you have the AC Coupled output of the Radian connected to the 
GEN breaker of the Sol-Ark <br>

4) that you have the software set for the GEN breaker to be AC Coupled 
and have checked all other software items with Sol-Ark needed for AC 
coupling<br>

<br>


just as a starting base for us to understand what may be happening.<br>

<br>

And some of the techs at Sol-Ark are in training - have you talked to 
the tech lead,  Dustin Douglas?  He&#39;s the official Sol-Ark rep on this 
list but I just saw him at InterSolar and he said he has been just too 
busy to chime in here much.  I&#39;m scheduled to speak with him soon - I&#39;ll
 see if he can find the time if he hasn&#39;t already talked to you.<br>

<br>

<br>

Best,<br>

<br>

Jeff<br>

<br>

<br>

<span></span>
<blockquote type="cite" style="border:0px none"><div style="margin:30px 25px 10px"><div style="width:100%;border-top:2px solid rgba(146,154,163,0.7);padding-top:10px">   <div style="display:inline-block;white-space:nowrap;vertical-align:middle;width:49%">
        <a style="padding-right:6px;font-weight:500;color:rgb(72,86,100);text-decoration:none" href="mailto:vince@solarenergydesign.com" target="_blank">Vince McClellan</a></div>   <div style="display:inline-block;white-space:nowrap;vertical-align:middle;width:48%;text-align:right">     <font color="#909AA4"><span style="padding-left:6px">January
 19, 2022 at 3:15 PM</span></font></div>    </div></div>
  <div style="color:rgb(144,154,164);margin-left:24px;margin-right:24px">
<div dir="ltr"><div>Is anyone on the list familiar with AC coupling Sol-Ark 
inverters?</div><div> </div><div>We haven&#39;t been able to AC couple an 
existing Outback Radian system to a new system that we built with 3, 
Sol-Ark 12K inverters and 3, Blue Ion batteries. Each time we have 
tested the system the Sol-Ark inverters accept the power from the Radian
 inverter until we turn on the DC power from the new solar array to the 
Sol-Ark inverters. As soon as there is significant DC power coming from 
the solar array the Sol-Ark inverters freq-watt turns on for a 
brief second and disconnects the Radian inverter even when the Blue Ion 
batteries are below the programmed state of charge threshold. If we 
don&#39;t turn on the DC power from the new solar array the Radian will 
connect and stay connected. </div><div><br></div><div>We have been 
working with Sol-Ark for several months now to get this system to accept
 the incoming power from the Radian without freq-watt kicking in on the 
Sol-Ark inverters and disconnecting the Radian inverter. Sol-Ark has 
sent two software revisions to the Sol-Ark inverters and we are still 
experiencing the same problem. </div><div><br></div><div>Can anyone 
think of what we might be missing and where to direct our 
troubleshooting efforts next? </div><div><br></div><div>Thanks, </div><br clear="all"><div><div dir="ltr"><div dir="ltr"><div style="font-size:small;color:rgb(80,0,80)"><div><font face="georgia, 
serif">Vince McClellan</font></div><div><font face="georgia, serif">Energy
 Design</font></div><div><font face="georgia, serif">NABCEP PV 
Installation Professional</font></div><div><font face="georgia, serif">p. <a href="tel:%28541%29%20485-8122" value="+15414858122" style="color:rgb(17,85,204)" target="_blank">(541)
 485-8122</a>  f. <a href="tel:%28541%29%20338-8202" value="+15413388202" style="color:rgb(17,85,204)" target="_blank">(541) 338-8202</a></font></div></div><div style="font-size:small;color:rgb(80,0,80)"><img src="https://docs.google.com/uc?export=download&amp;id=1HcXK0FTsJsEFDvKv-POVulmqJD3Ikpz4&amp;revid=0B2VUQDDTFCz_aVNUUUNDRkNRUCtjc1oyZ3JFY2NvNWlJVGpvPQ" height="79" width="420"><br></div><div style="font-size:small;color:rgb(80,0,80)"><span style="font-family:&quot;arial narrow&quot;,sans-serif">If you have 
received this email and are not the intended recipient please delete 
this email. Copying, or using any part, content, or attachment of this 
email is strictly prohibited. </span></div></div></div></div></div>

<br><fieldset></fieldset><br><div>_______________________________________________<br>List
 sponsored by Redwood Alliance<br><br>Pay optional member dues here: 
<a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a><br><br>List
 Address: 
<a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change
 listserver email address
 &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There
 are two list archives for searching. When one doesn&#39;t work, try the 
other:<br><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List
 rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check
 out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a><br><br></div>

  </div></blockquote>

<br>



</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn&#39;t work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>