</head><body text="#000000">Hi Jay and All,<br>
<br>
So I jumped the gun a bit on the auto-former - My experience thus far is
 mostly with multiple inverter systems (3 systems of 2 &amp; 3 units) 
and so I have not had any single leg issues on those systems.  And the 
few single inverter systems I do have out there (2 systems) I haven't 
had any problem - so I was just suggesting that could be a way to deal 
with it if you were having  that issue - I should be more careful to 
speak only from experience!<br>
<br>
As for field repair I do know that some early Sol-Arks had issues with 
sharing the load while paralleling and there is an MC board ("Master 
Control" I assume)  that they offer for those instances that is field 
installable.  I have not had that problem.<br>
<br>
I've had customer calls twice on those 5 systems in a years time - both 
times a simple reboot solved the problem and other issues I've had were 
simply my learning curve with settings as they are a lot of options 
-especially if using the Time-of-use interface.   The one system I have 
that is a single inverter that is in GTBB mode (on grid as sell-back 99%
 of time with battery there for outages) has not burped once in a year's
 time so that's simple.  The Off-Grid systems work like a charm though 
high loads did cause a reboot once. <br>
<br>
It's true what  Eric says that there are settings on the PowerView 
interface that are not covered in the Manual - the control software is 
more powerful than most inverters but it does take some time to get to 
the bottom of all of them and it seams even Sol-Ark tech support is 
learning.  The control is highly customizable and that has come in super
 handy with a customer that is on-grid but really likes to be off grid 
as much as possible - so during the seasons in New England she changes 
her Time-of-Use settings to match the seasons and that has worked out 
super well (it's just changing the SOC levels that we let the batteries 
come to at different times of day)  - can't imagine doing what she's 
doing with any other inverter.<br>
<br>
In talking with tech support one tech did mention that sometimes some 
data gets into the "wrong ledger" or some such and that's why a simple 
reboot works and they say they are refining that in subsequent 
firmware.  A deeper level reboot is sometimes required he says by doing a
 factory reset rather than just a restart but then you have to reset 
settings but he says that is a rare need.  They have had multiple (like 4
 or 5?) firmware upgrades over the year but none seemed to be that 
critical.<br>
<br>
So that's my fuller report.  I consider the Sol-Ark my replacement for 
the Sunny Island (that sadly simply isn't evolving with the times except
 perhaps the European model)  - Robust - stackable and much easier to 
install with DC coupling option and included switchgear.  Yes you do 
need to learn the software interface but I find it clearly no more 
complicated than say the Outback or Schneider XW interface once you are 
use to it and once you do you have much more control and easy remote 
programming both on laptops and phones and the customer has the same 
access if you want to programmables.<br>
<br>
I've never been put on hold for Sol Ark tech support and they spend as 
much time as it needs while looking at the same data you are looking at 
through PowerView - super helpful.<br>
<br>
Hope that helps!<br>
<br>
Best,<br>
<br>
Jeff<br>
<br>
<br>
<br>
<br>
<span>

</span><br>
<blockquote type="cite" 
cite="mid:967F9A1D-817A-42A8-BB97-A007E33275B0@gmail.com" style="border:
 0px none ! important;">
  <div xmlns="http://www.w3.org/1999/xhtml" class="__pbConvHr" 
style="margin:30px 25px 10px 25px;"><div 
style="width:100%;border-top:2px solid 
rgba(146,154,163,0.7);padding-top:10px;">   <div 
style="display:inline-block;white-space:nowrap;vertical-align:middle;width:49%;">
        <a style="color:#485664 
!important;padding-right:6px;font-weight:500;text-decoration:none 
!important;" href="mailto:jay.peltz@gmail.com" moz-do-not-send="true">Jay</a></div>
   <div 
style="display:inline-block;white-space:nowrap;vertical-align:middle;width:48%;text-align:
 right;">     <font color="#909AA4"><span style="padding-left:6px">January
 7, 2022 at 5:55 AM</span></font></div>    </div></div>
  <div xmlns="http://www.w3.org/1999/xhtml" class="__pbConvBody" 
__pbrmquotes="true" 
style="color:#909AA4;margin-left:24px;margin-right:24px;"><meta 
http-equiv="content-type" content="text/html; charset=utf-8"><div 
dir="ltr">Hi Jeff</div><div dir="ltr"><br></div><div dir="ltr">Thanks 
for the info. </div><div dir="ltr"><br></div><div dir="ltr">As to out of
 balance 120v.</div><div dir="ltr"><br></div><div dir="ltr">How are you 
configuring for that?  Just putting potential problem loads on the 
xformer or ?</div><div dir="ltr"><br></div><div dir="ltr">Which 
transformer are you using with a 9kw inverter?  Most I\u2019ve seen are only 
5-6kw. </div><div dir="ltr"><br></div><div dir="ltr">And as many people 
are using the sol ark, a question about repairing. Is it possible to 
repair in the field?  Has anyone actually done it?  If not field 
repairable, how quickly/easily is the repair/warranty process working</div><div
 dir="ltr"><br></div><div dir="ltr">Thanks</div><div dir="ltr">Jay</div><div
 dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br></div>


  </div>
  <div xmlns="http://www.w3.org/1999/xhtml" class="__pbConvHr" 
style="margin:30px 25px 10px 25px;"><div 
style="width:100%;border-top:2px solid 
rgba(146,154,163,0.7);padding-top:10px;">   <div 
style="display:inline-block;white-space:nowrap;vertical-align:middle;width:49%;">
        <a style="color:#485664 
!important;padding-right:6px;font-weight:500;text-decoration:none 
!important;" href="mailto:jeffc@villagepowerdesign.com" 
moz-do-not-send="true">Jeff Clearwater</a></div>   <div 
style="display:inline-block;white-space:nowrap;vertical-align:middle;width:48%;text-align:
 right;">     <font color="#909AA4"><span style="padding-left:6px">January
 6, 2022 at 8:04 PM</span></font></div>    </div></div>
  <div xmlns="http://www.w3.org/1999/xhtml" class="__pbConvBody" 
__pbrmquotes="true" 
style="color:#909AA4;margin-left:24px;margin-right:24px;">
<meta http-equiv="Content-Type" content="text/html; charset=utf-8">

We just ordered
 a 3 Sol-Ark system with 16 
Storz Power batteries I'll let you know this Spring once I have it up 
and running.  Yes they are closed loop will be UL9540 soon.<br>

<br>

We have several Sol-Arks in the field - all working great - yes a few 
minor issues that have required software updates - but tech support is 
great and they push the updates for me.  I love the monitoring and 
ability to remote program every parameter.  Conversion efficiency in all
 modes is high (though slightly under what they claim but still great)<br>

<br>

Surge is fine per leg with multiple inverters or a balancing 
transformer.  Gen support could use an upgrade  for sure but they are 
working on it.<br>

<br>

The  Time-of -use  features and interface we love as you can really fine
 tune daily cycles - optimizing solar and battery and grid and generator
 inputs - Especially great for grid-tie with strong off-grid capability 
as opposed to most  lightweight GTTB systems.  In pure Off-grid I find 
them robust and reliable so far.<br>

<br>

Enjoy!<br>

<br>

Jeff Clearwater<br>

Village Power Design<br>

<br>

<br>

<span>

</span><br>



<br>





<br><fieldset class="mimeAttachmentHeader"></fieldset><br><div>_______________________________________________<br>List
 sponsored by Redwood Alliance<br><br>Pay optional member dues here: 
<a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a><br><br>List Address: 
<a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address
 &amp; settings:<br><a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There
 are two list archives for searching. When one doesn't work, try the 
other:<br><a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List
 rules &amp; etiquette:<br><a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check
 out or update participant bios:<br><a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a><br><br></div>

  </div>
</blockquote>
<br>
</body></html>