<p>I mean twice the Watts / Amp. </p>
<div id="signature">---<br />
<div class="pre" style="margin: 0; padding: 0; font-family: monospace"> </div>
</div>
<p><br /></p>
<p id="reply-intro">On 2021-08-03 10:13, drake.chamberlin@redwoodalliance.org wrote:</p>
<blockquote type="cite" style="padding: 0 0.4em; border-left: #1010ff 2px solid; margin: 0">
<div id="replybody1">
<div style="font-size: 10pt; font-family: Verdana,Geneva,sans-serif;">
<p>Hi Brad,</p>
<p>The auto transformer should work just fine. You should get 4X the efficiency with 1/2 the current and twice the Watts / Volt. I don't know how much benefit is available from paralleling wires of different sizes; it is not recommended practice of course.</p>
<p>If you find a source for those old auto transformers, I'd sure like to know.</p>
<p>Best,</p>
<p>Drake</p>
<p><br /></p>
<p>Drake Chamberlin</p>
<p>Athens Electric LLC</p>
<p>Ohio Electrical Contractor’s License 44810</p>
<p>CO Master Electrician’s License 4526</p>
<p>NABCEP Certified PV Installation Professional</p>
<div id="v1signature">---<br />
<div class="v1pre" style="margin: 0; padding: 0; font-family: monospace;"> </div>
</div>
<p><br /></p>
<p id="v1reply-intro">On 2021-08-02 15:16, Bradley Bassett wrote:</p>
<blockquote style="padding: 0 0.4em; border-left: #1010ff 2px solid; margin: 0;">
<div id="v1replybody1">
<div dir="ltr">
<p class="v1v1MsoNormal" style="margin: 0in 0in 8pt; line-height: 107%; font-size: 11pt; font-family: 'Calibri',sans-serif;">The system currently has a 600 foot run of 2-2-4 aluminum from the service to the house loads. The load is often only 120VAC which gives a large voltage drop using only the #2 and #4 conductors. My thought was to install an autotransformer at the load end so that the current runs through the #2 conductors at 240VAC for much less voltage drop. Are there any issues I should be looking at doing this? I'm thinking that to balance the legs a 4kVA autoformer would be adequate. The circuit is protected by 30A breakers both ends.<span></span></p>
<p class="v1v1MsoNormal" style="margin: 0in 0in 8pt; line-height: 107%; font-size: 11pt; font-family: 'Calibri',sans-serif;">Second question is if I could reduce the voltage drop even more by taking the #4 and paralleling it to one of the #2 conductors. This would eliminate the neutral on the long run. I'm thinking that the autoformer could generate a new neutral for the load circuits. This is an older install so the neutral is already grounded to earth at both ends, there is no ground wire between the two such as would be required by code now. I know that code does not allow paralleling conductors smaller than 1/0 but I will disregard that in this case since it's my own system. <span></span></p>
<p class="v1v1MsoNormal" style="margin: 0in 0in 8pt; line-height: 107%; font-size: 11pt; font-family: 'Calibri',sans-serif;">If anyone has one of the old AEE toroid autoformers you'd like to sell, or if you want one yourself we can do a bulk buy. Let me know off list.</p>
<p class="v1v1MsoNormal" style="margin: 0in 0in 8pt; line-height: 107%; font-size: 11pt; font-family: 'Calibri',sans-serif;"> </p>
<p class="v1v1MsoNormal" style="margin: 0in 0in 8pt; line-height: 107%; font-size: 11pt; font-family: 'Calibri',sans-serif;">Thanks,</p>
<p class="v1v1MsoNormal" style="margin: 0in 0in 8pt; line-height: 107%; font-size: 11pt; font-family: 'Calibri',sans-serif;">Brad Bassett</p>
<p class="v1v1MsoNormal" style="margin: 0in 0in 8pt; line-height: 107%; font-size: 11pt; font-family: 'Calibri',sans-serif;">AEE Solar</p>
<p class="v1v1MsoNormal" style="margin: 0in 0in 8pt; line-height: 107%; font-size: 11pt; font-family: 'Calibri',sans-serif;"> </p>
</div>
</div>
<br />
<div class="v1pre" style="margin: 0; padding: 0; font-family: monospace;">_______________________________________________<br />List sponsored by Redwood Alliance<br /><br />Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank" rel="noopener noreferrer">http://re-wrenches.org</a><br /><br />List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br /><br />Change listserver email address & settings:<br /><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noopener noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br /><br />There are two list archives for searching. When one doesn't work, try the other:<br /><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank" rel="noopener noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br /><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank" rel="noopener noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br /><br />List rules & etiquette:<br /><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noopener noreferrer">http://www.re-wrenches.org/etiquette.htm</a><br /><br />Check out or update participant bios:<br /><a href="http://www.members.re-wrenches.org" target="_blank" rel="noopener noreferrer">http://www.members.re-wrenches.org</a><br /><br /></div>
</blockquote>
</div>
</div>
<br />
<div class="pre" style="margin: 0; padding: 0; font-family: monospace">_______________________________________________<br />List sponsored by Redwood Alliance<br /><br />Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank" rel="noopener noreferrer">http://re-wrenches.org</a><br /><br />List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br /><br />Change listserver email address & settings:<br /><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noopener noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br /><br />There are two list archives for searching. When one doesn't work, try the other:<br /><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank" rel="noopener noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br /><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank" rel="noopener noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br /><br />List rules & etiquette:<br /><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noopener noreferrer">http://www.re-wrenches.org/etiquette.htm</a><br /><br />Check out or update participant bios:<br /><a href="http://www.members.re-wrenches.org" target="_blank" rel="noopener noreferrer">http://www.members.re-wrenches.org</a><br /><br /></div>
</blockquote>